Nestor... I agree but you forget to mention that applying "flanges" to the 2X10 beam actually strengthens it more because of the AD**2 property-- the area of the flange time the distance from the neutral axis squared -- trying to make it act like a efficient wideflange beam as much as possible. My example uses this by including the subflooring and some of the "flange" area. This way you can get the effect of adding two inches to the depth of the beam without decreasing headroom on the floor below.



__________________
CraigFL is offline  
 
Reply With Quote Quick reply to this message
Old 11-15-2009, 01:47 PM  
travelover
Senior Member
 
Join Date: Aug 2007
Posts: 693
Liked 2 Times on 2 Posts

Default

I've got a degree in mechanical engineering, too, so I understand the physics involved. I remember working out these formulas long hand pre-calculator.

But realistically, the OP only wanted to slap down another layer on the top side. Sistering is not ideal from an efficiency standpoint but if you are trying to keep the same ceiling height, it is a cheap, low tech way to reinforce the floor. Ditto with blocking or diagonal braces between joints.

And yes, the length of the joists is more important than the depth, but I didn't think the OP was gonna make the room smaller, and I didn't see a willingness to add posts underneath.



__________________
travelover is offline  
 
Reply With Quote Quick reply to this message
Old 11-15-2009, 03:10 PM  
Nestor_Kelebay
Emperor Penguin
 
Nestor_Kelebay's Avatar
 
Join Date: Mar 2009
Location: Winnipeg, Manitoba
Posts: 1,844
Liked 2 Times on 2 Posts

Default

I took engineering years ago, but I still remember and understand the basics of beam design, just as others in here do.

I just figured I'd bring out the point about strengthening the joists themselves. I always hear about people sistering joists, and there's no doubt that sistering joists will result in a stronger joist system. But, it's also true that there are other options available that may work better that haven't been presented to the homeowner.

When I have suggested these options on other Q&A forums I've posted on, I've gotten a lot of resistance. Most of the time the arguments against it went as follows "I've been doing this kinda work for 600 years, and I've never ever heard of anything so stupid in my life until you opened your mouth. Do you realize that I had to grit my teeth to stop myself from laughing out loud at what you said! That's cuz it was so mind-bogglingly stupid. Do you hear me?"

So, what do I do with criticism like that? I can explain the equations, and why adding wood should work, but I can't change prejudice, and this guy has already decided it's a stupid idea before he's even taken the time to think it through. So, I just throw the idea out there with the formulas to show why it should work, take the criticism on the chin and carry on. What else would anyone do?

I just thought I'd explain the basics so that people in here can see for themselves that there are alternatives to sistering joists that they might want to explore. If they do, then I'd recommend they proceed with the assistance of a consulting engineering firm or architectural firm to ensure that what's done is structurally sound and approved for insurance purposes. Your house is your biggest investment, and you should proceed with structural changes only with an engineering or architectural firm on side to approve the changes just to cover your A$$.

__________________

Last edited by Nestor_Kelebay; 11-15-2009 at 04:27 PM.
Nestor_Kelebay is offline  
 
Reply With Quote Quick reply to this message
Old 11-15-2009, 03:17 PM  
Adk
Junior Member
 
Join Date: Jan 2008
Posts: 19
Default

Great piece of advise!!!

__________________
Adk is offline  
 
Reply With Quote Quick reply to this message
Old 11-15-2009, 04:25 PM  
Nestor_Kelebay
Emperor Penguin
 
Nestor_Kelebay's Avatar
 
Join Date: Mar 2009
Location: Winnipeg, Manitoba
Posts: 1,844
Liked 2 Times on 2 Posts

Default

PS:

I think I still have a post I wrote up years ago that explains these beam equations in more detail. I don't want to hijack this thread, but am willing to post it here or in a new thread if anyone wants to read it.

__________________
Nestor_Kelebay is offline  
 
Reply With Quote Quick reply to this message
Old 08-04-2010, 12:23 PM  
rpineo
Junior Member
 
Join Date: Aug 2010
Posts: 3
Default

I realize that this thread is rather old, but here goes...

So, yes, I too studied engineering, and I recall the theory and equations. Everything the Nestor detailed looks correct, as I recall. In theory.

One issue that I am still struggling with is the transfer of load between the original beam (joist) and the new material.

Certainly, there are excellent bonding agents that can marry the new material to the existing material. That part should pose no problem.

But the theoretical handling of this problem seems to miss some of the realities of the situation.

Let's assume for simplicity sake that we intend to "sister" a 2x10 with a second 2x10. The typical approach would place one beside the other, effectively doubling the strength of the original beam. I agree with this.

The approach that Nestor spoke of would instead attach the second beam to the bottom of the first. Generally speaking, this would result in a 2x20. However, there is one major caveat - the added material will be by definition shorter than the original, and rather than bearing upon the fixed endpoints, the new material will be carried by the pre-existing joists.

The additional weight of material will probably be negligible as compared to the added strength. And I will assume that head room is not an issue in this example.

Even still: Nestor noted that the top most fibers of the beam would be in compression, and the bottom most fibers in tension. This is true in theory.

However, in my proposed scenario, the lower 2x10 sections do not bear upon the fixed endpoints. As such, the tension at the extreme lowest strand of the combined beam will be zero, at least at either end.

There will be some level of tension present at the same extreme lowest strand at the midpoint of the span.

How much tension will there be, and correspondingly, how much load will the new material actually pick up? Here is where my understanding begins to break down. My "gut" tells me that there is some triangular or trapezoidal load sharing pattern in the new material, as load is transferred across the glued interface and then across the material itself.

So, the 8x increase in strength that theory would suggest will be immediately diminished. Admittedly, I don't know exactly by how much, but I think we can all agree the the REAL increase will be less than 8 fold.

Also, since it is not really feasible to reduce headroom by attaching so much additional material, a realistic treatment of Nestor's idea would more likely add something modest, like 2 or maybe 3 inches of material height.

If we assume 2 inches added, at best, our 2x10s become 2x12s, which would be about 70% stronger? And as I noted, that 70% gets eaten into by the ACTUAL load sharing pattern. So, let us assume that the addition of 4 inches of new material (2x10s become 2x14s) will suffice to double the strength of the beams. Then the immediate question is: which is preferable - traditional sistering, or losing 4 inches of headroom for Nestor's approach?

Comments?

__________________
rpineo is offline  
 
Reply With Quote Quick reply to this message
Old 08-04-2010, 10:53 PM  
Nestor_Kelebay
Emperor Penguin
 
Nestor_Kelebay's Avatar
 
Join Date: Mar 2009
Location: Winnipeg, Manitoba
Posts: 1,844
Liked 2 Times on 2 Posts

Default

Rpineo:

When I did these calculations in 2nd or 3rd year mechanical, (I forget which year), using a mending plate to join two beams was a 3-part calculation:

1. First you calculated the size of the mending plate to carry the same bending stress as the original beam.

2. Then (since we never assumed a glued joing) you calculated the number of steel fasteners you needed to carry the load between the beam and the mending plate. (Assuming the shear strength of steel was 30,000 pounds per square inch, you calculated the number of square inches of steel you needed to carry the load between the first part of the beam and the mending plate, and that was also the number of square inches of steel you needed between the other end of the mending plate and the other end of the beam. Then, you divided the square inches of steel you needed by the cross sectional area of each fastener to get the number of fasteners at each end of the mending plate. Now, that'll be the minimum cross sectional area of steel we'll need to carry the load from joist to sister and back to joist; we can always use more fasteners to provide a larger safety factor.

3. Finally, you calculated the bearing strength of the holes to ensure that you weren't using too few fasteners and that the holes were going to elongate or "stretch" because of the stress applied to the side of the holes by each fastener.

Back then, we always presumed that steel beams had rivets or bolts holding them together, but the same calculation should apply to sistering a 2X8 or a 2X10. I think there's a rule of thumb somewhere for deciding how long the "mending plate" or sister joist needs to be, but you can't go wrong making it as long as practical. The weight of the sister is going to be negligible compared to the strength it's going to add.

Then, theoretically, you'd have to figure out based on the span tables how much load each joist is supposed to be supporting if the design is supposed to be 40 pounds per square foot of floor area (I seem to recall) and the joists are spaced on 16 inch centers. Of the top, that would work out to about (4/3) X 40, or about 53 pounds per lineal foot of joist span.

Now, use your beam equations to find out what the bending stress is on that joist is at the middle (or where it's broken) and divide that by 30,000 pounds per square inch shear strength of steel to find out how many square inches of steel fastener you need to carry the load between the joist and the sister, and you need that same area of steel at the other end of the sister to carry that same load back to the beam. (What we're doing here is working out how much steel we need to carry the load the original beam supported, and assuming the sister will be supporting the same amount of load, and working out based on a shear strength how many square inches of steel we need to carry that load, and then based on area, how many fasteners we need. But, in the real world, nails are cheap, and so most people would just go nutz with their nailing just to be on the safe side rather than do any calculations.)

When we did the bearing force calculations, we assumed the bolts or rivets were rigid and didn't bend, and in this calculation the equivalent assumption would be that the nails used to nail the sister to the joist are rigid and won't bend. So, you'd get the compressive strength of fir and knowing the bearing area between the nail and the wood, work out whether or not the wood will compress permanently (and therefore the holes elongate) as a result of the force applied to the wood by the nails. You know the shear force carried by each nail and you know the compressive strength of the wood, so you can determine if the wood is going to crush at each nail location... or not.

I suppose that if you treated the nail like a round beam, you could work out the force required to bend the nail, and see if that's greater or smaller than the bearing force on the holes. That'll tell you whether or not the nails will bend, and if so, ya gotta use more of them.

That's how I recall doing steel beam calculations, and I expect you'd do exactly the same thing for using a wooden mending plate to repair a wooden joist, or just to sister each of the joists in a floor. You're just working out how much steel you need to carry the load of each joist, and then ensuring that you use enough fasteners that the compressive strength of the wood isn't being exceeded. In all the calculations we ever did, we always assumed that each fastener carried the same load regardless of where it was located, and that doesn't seem reasonable to me. However, that's what we assumed in doing the calculations.

Anyhow, it's a 3 step calculation; figure out how much stress the beam or mending plate is supposed to hold, then figure out how many square inches of steel in sheer is needed to carry that load, then figure out how many fasteners you need to provide that area of steel, and check that the load on each fastener doesn't crush the hole it's in. Don't you remember doing that?

__________________

Last edited by Nestor_Kelebay; 08-04-2010 at 11:42 PM.
Nestor_Kelebay is offline  
 
Reply With Quote Quick reply to this message
Old 08-06-2010, 07:48 AM  
rpineo
Junior Member
 
Join Date: Aug 2010
Posts: 3
Default

Quote:
Originally Posted by Nestor_Kelebay View Post
Rpineo:

<snip>

Don't you remember doing that?
What I remember most about sizing and design calculations was that we would utilize a set of assumptions in order to reduce our "problem" to a nice, neat theoretical approximation. Then we would labor to produce pages and pages of meticulous, painstaking mathematics. We would then compare the results of these seemingly endless equations against some tables to determine the size of beam or plate or cable(s) that we would need.

And then we would multiply that requirement by a factor of 2 or 3 for "safety", because ultimately, nobody really knew if all the theory would actually work in practice!

But that aside...


If I read your post correctly, you are discussing the sizing math around the following configuration:


(1) Start with existing beam (joist). Assume a 2x10 wooden joist.
(2) Attach a second 2x? member (lets say a 2x6) along the bottom edge. This theoretically results in a 2x16 compound joist.
(3) Secure the beams together using mending plate(s) - as shown in attached sketch, where 'x' chars are mending plate(s).


My original post was meant to illustrate my uncertainty about how closely this practical application would match the theoretical effectiveness. I admit that it has been some time since I have had to do such math, so my misgivings are based mainly on gut feeling. Also, the notion of sistering joists has been around for a long, long time. So has physics. If "sistering" in this fashion was the superior approach, then one is left to wonder why nobody has been doing it this way. Is there some major practical drawback, or is Nestor really onto something here?

If the latter, you might want to consider a patent!
sketch.jpg  
__________________
rpineo is offline  
 
Reply With Quote Quick reply to this message
Old 08-06-2010, 10:03 AM  
Nestor_Kelebay
Emperor Penguin
 
Nestor_Kelebay's Avatar
 
Join Date: Mar 2009
Location: Winnipeg, Manitoba
Posts: 1,844
Liked 2 Times on 2 Posts

Default

Rpineo:

I think the reason why adding wood to joists isn't commonly done is because it's only recently that we've had glues that cure to form bonds that are as strong as wood. There have been other glues that form super strong bonds, like the glues used to hold laminated airplane propellers together, but these glues aren't practical to use in the field, such as in someone's basement. Now we have moisture cure polyurethane glues (like LePage's PL Premium) that are so strong that the wood they're gluing together will break before the glued joint will. And, of course, it takes time for ANY new idea to gain acceptance simply because everyone is convinced that the way they've been doing it for years is the "right" way to do it, and all other ways are either bogus or "short cuts".

Until recently, there simply haven't been wood glues that can be applied in the field that would cure to a bond stronger than the wood. So, "sistering" joists has been the fail safe alternative. But, now we have moisture cure polyurethane glues like LePage's PL Premium that WILL cure to a bond stronger than the original wood, and that's what makes the option of "adding wood to make a bigger, stronger joist" feasible. Until now, that option hasn't been available because the glues simply didn't form strong enough bonds and contractors tend to stick with "tried and true" solutions to prevent call-backs.

And, that's pretty much the definition of progress. A better product in one technology makes an alternative and advantageous method of doing something feasible in a different technology.

I've gotten a lot of flack on the internet from even suggesting that you can make a joist stronger by adding wood to it (so long as the wood and glue used are as strong or stronger than the original wood), and anyone with an engineering background will immediately see that there's no reason why that wouldn't work THEORETICALLY at least. But, (and I think) the problem is that until recently, we simply didn't have glues that were strong enough to make this a PRACTICAL alternative, and so no one did it. And, I fell into the old trap: "If what you're saying will work, why doesn't anyone do it?" Now we have much stronger glues that can be field-applied, and you're likely going to see people strengthening floors and houses by making the existing joists "taller" rather than sistering joists.

So, I'm going to keep telling people about this alternative, but I'm also going to stress that everything hinges on there not being ANY slippage at the joint between the old wood and the new wood, and therefore a super strong glue like PL Premium has to be used, and let people make up their own minds.

We all learn from each other in here.

__________________

Last edited by Nestor_Kelebay; 08-06-2010 at 10:22 AM.
Nestor_Kelebay is offline  
 
Reply With Quote Quick reply to this message
Old 08-06-2010, 10:16 AM  
rpineo
Junior Member
 
Join Date: Aug 2010
Posts: 3
Default

With regard to "obvious" patents, see: Patently Absurd (James Gleick)

In any case, I was speaking in jest.



Thanks for your thoughtful and detailed posts on this subject. This discussion has been most enlightening. I have a few joists that still require attention - I may test your approach.



__________________
rpineo is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Reinforcing subfloor in 1970s house juryduty Framing and Foundation 16 11-07-2010 10:41 PM
Advice needed for reinforcing floor for large Aquarium tempest Framing and Foundation 4 05-25-2009 12:40 AM
Floor reinforcing for Aquarium Nuuze Framing and Foundation 7 04-17-2008 10:52 AM
Replacing a subfloor bvz Flooring 4 04-08-2008 12:05 PM
Replacing a corner post, Reinforcing the wall? jlawrence42 Framing and Foundation 10 08-21-2006 07:30 PM