As Joe D says check across both wires for 240V if you have that check across the upper element for the same. No light behind the reset button. with a cold tank the upper element comes on first until it's thermostat is meets temp then the lower element will come on. Only one element will be powered at a time.



__________________
Blue Jay is offline  
 
Reply With Quote Quick reply to this message
Old 10-07-2013, 08:23 AM  
kok328
Supporting Member
HRT_SUPPORTER.png
 
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,173
Liked 102 Times on 89 Posts
Likes Given: 61

Default

Sorry for the late response & the frustrations you are having.
Perhaps this link provides some insight:
http://waterheatertimer.org/How-to-troubleshoot-electric-problems-with-water-heater.html



__________________
kok328 is offline  
 
Reply With Quote Quick reply to this message
Old 10-07-2013, 01:37 PM  
CallMeVilla
Contractor
 
CallMeVilla's Avatar
 
Join Date: Feb 2010
Location: San Diego
Posts: 1,221
Liked 353 Times on 278 Posts
Likes Given: 141

Default

After discussing this with the Rheem Tech, and checking with a multi-meter, we have decided it is probably a faulty 2-pole breaker.

Since there is so much activity at the site, I am waiting until closing to change out the breaker (and two other I suspect are old). That is when I can power down the main ... as experienced as I am with electrical, I just never like working on a hot main.

Will let y'all know if this solves the problem ...

__________________
CallMeVilla is online now  
 
Reply With Quote Quick reply to this message
Old 10-07-2013, 01:47 PM  
JoeD
Contractor
 
Join Date: Mar 2006
Location: Welland, Ontario
Posts: 936
Liked 92 Times on 77 Posts

Default

What type of panel? What type of breaker?
Some panels if you don't put the breaker in the proper spot you get both poles on the same phase and end up with 120 volts to ground but not 240 between them.
Also make sure you have full a two pole breaker installed and not twin, mini or tandem breaker which only takes up one slot in the panel.
We still haven't heard the results of a voltage measurement between the two hots, either at the breaker or the heater.

__________________

Last edited by JoeD; 10-07-2013 at 09:12 PM.
JoeD is offline  
nealtw Likes This 
Reply With Quote Quick reply to this message
Old 10-07-2013, 05:09 PM  
kok328
Supporting Member
HRT_SUPPORTER.png
 
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,173
Liked 102 Times on 89 Posts
Likes Given: 61

Default

I thought we had already established that you were getting 120V from each leg of the 2-pole breaker?
If not, it might be that the old heater was still good.

__________________
kok328 is offline  
nealtw Likes This 
Reply With Quote Quick reply to this message
Old 10-07-2013, 11:21 PM  
CallMeVilla
Contractor
 
CallMeVilla's Avatar
 
Join Date: Feb 2010
Location: San Diego
Posts: 1,221
Liked 353 Times on 278 Posts
Likes Given: 141

Default

OK, DIY Warriors ... Here is the outcome ...

1. Checking with multimeter across the input side resulted in no voltage. However, using a tickler gave a reading of AC current present. HUH? Yes, the old induced voltage false reading!

2. Checking with a clamp meter indicated no voltage inside the WH, at the input side ... HUH?

3. Shut down the building to avoid working on a hot panel.

4. Changed out the breaker, which had been invented by Edison it was so old. Upgraded to 30A from 20A ... yes, the #10 wires would support it.

5. Powered up the building and TAH DAH! Measured 220 across the input side of the manual cut off. Engaged the entire circuit and TAH DAH! Got 220 inside the WH.

Lessons learned: (1) the AC tickler is a good tool but induced voltage can trick you. (2) believe your better diagnostic tools (multimeter and clamp meter).

Thanks for everybody kicking in on ideas ... Great team here!

Hot water for every possible need ...

shower.jpg  
__________________
CallMeVilla is online now  
nealtw Likes This 
Reply With Quote Quick reply to this message
Old 10-08-2013, 08:21 PM  
nealtw
Contractor
 
Join Date: Nov 2010
Location: vancouver, b.c.
Posts: 9,465
Liked 748 Times on 668 Posts
Likes Given: 1306

Default

A few years ago I tryed to help a friend figure out why the oven and two burners were not working. After some head scratching we figured out the breaker was at fault and changed it, but then it would not stay on, even with the stove unplugged. Then he said well the breaker did kick off a couple of weeks earlier while the stove was not in use. The pros he brought in decided the wire was faulty and dug into walls to change it and found that when he had installled the new shelf in the garage he managed to drive a screw thru the wire and tagged the red and black. You know when in doubt use 4" screws to hold up ten pounds.

__________________
nealtw is offline  
 
Reply With Quote Quick reply to this message
Old 10-14-2013, 10:16 PM  
nealtw
Contractor
 
Join Date: Nov 2010
Location: vancouver, b.c.
Posts: 9,465
Liked 748 Times on 668 Posts
Likes Given: 1306

Default

Quote:
Originally Posted by JoeD View Post
What type of panel? What type of breaker?
Some panels if you don't put the breaker in the proper spot you get both poles on the same phase and end up with 120 volts to ground but not 240 between them.
Also make sure you have full a two pole breaker installed and not twin, mini or tandem breaker which only takes up one slot in the panel.
We still haven't heard the results of a voltage measurement between the two hots, either at the breaker or the heater.
The electrition was long gone when we turned the baseboard heaters on and one set didn't work. I was about an hour into troubleshooting with just a test light when I remmembered this post and sure enough, with Stabloc you can get both breakers on one leg. Thank you very much, saved the day.


__________________
nealtw is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Heat Pump Aux. heat running too often. OIIIIIIIO HVAC 13 02-26-2012 09:13 PM
Thermostat says heat, but no heat vjf HVAC 4 01-03-2012 07:17 AM
Hot water heat: zone doesn't run unless another zone is also calling for heat operagost HVAC 4 11-11-2011 11:41 AM
Electric Heat Pump Vs. Natural Gas LifesPeachy HVAC 1 07-30-2011 07:07 AM
Electric Heat Pump & Programmable Thermostat John Greeb HVAC 2 01-09-2009 09:01 PM