Default Carrier AC Outside Fan Will Not Turn ON

Any help is appreciated. The motor fan to my outside AC unit will not turn on. I had the capacitor checked, and it is OK. What is my next step. Is the motor fan bad?

Thanks,

J Grabowski



__________________
Galaga1 is offline  
 
Reply With Quote Quick reply to this message
Old 05-15-2013, 03:43 PM  
lloyd
Junior Member
 
Join Date: Jul 2010
Location: Tulsa, Ok
Posts: 28
Default

Check the fan motor to see if it's warm/hot. If it's hot replace, it.



__________________
lloyd is offline  
 
Reply With Quote Quick reply to this message
Old 05-15-2013, 08:38 PM  
kok328
Supporting Member
HRT_SUPPORTER.png
 
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,137
Liked 92 Times on 81 Posts
Likes Given: 59

Default

Stupid question but, is the circuit breaker "on" for the outside unit?
Does the compressor come on but, not the fan?
Do you have a volt/ohm meter to perform some simple tests that will allow us to further assist you?

__________________
kok328 is offline  
 
Reply With Quote Quick reply to this message
Old 05-15-2013, 09:32 PM  
dthornton
inspector gadget
 
Join Date: Apr 2012
Location: Red Oak, IA, Iowa
Posts: 180
Liked 17 Times on 15 Posts
Likes Given: 84

Default

You can also stick (CAREFULLY!) a screwdriver down through the guard and see if the fan blade will turn. Mine didn't - it was frozen up. However, you could hear the compressor run. I had my plumber/HVAC replace the fan and the unit cools just fine. Cost me $100 (as opposed to $1500+ for a new unit.

__________________
dthornton is offline  
 
Reply With Quote Quick reply to this message
Old 05-16-2013, 04:58 AM  
Galaga1
Junior Member
 
Join Date: May 2013
Posts: 7
Default

Yes Sir the breaker is on. The fan moves freely in both directions. I do have a voltage meter. A few questions. I had a new furnace put in 4 months ago, and the burner has leaked oil from day one. A factory rep. is coming out to my house next week to access the problem. Could this have anything to do with my outside fan not turning on? Should I press in the contractor plunger to see if the fan and compressor will turn on, and should I have the safety swtich in the ON position that is located near the outside unit? The compressor was also warm to the touch, and I did not have the unit on. Is this normal? Sorry, for the long response, but I needed to give you an overview of what has been going on.

Thanks,

jay Grabowski

__________________
Galaga1 is offline  
 
Reply With Quote Quick reply to this message
Old 05-16-2013, 06:04 AM  
oldognewtrick
Moderator
HRT_MODERATOR.png
 
oldognewtrick's Avatar
 
Join Date: Jul 2009
Location: Nashville, TN
Posts: 4,343
Liked 311 Times on 262 Posts
Likes Given: 109

Default

Jay, the make, model and number on the unit will help identify what is wrong with your unit.

__________________
oldognewtrick is offline  
 
Reply With Quote Quick reply to this message
Old 05-16-2013, 06:54 AM  
kok328
Supporting Member
HRT_SUPPORTER.png
 
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,137
Liked 92 Times on 81 Posts
Likes Given: 59

Default

Yes the safety switch (service switch/disconnect) should be on.
You should have 240VAC to the L1,L2 lugs of the contactor.
You should have 24VAC to the coil lugs of the contactor.
With 24VAC to the coil, the contactor should be engaged and you should also see 240VAC on the T1,T2 lugs of the contactor.
Shut off the disconnect and check for burn wires leading to the compressor and contactor.
Also, test the capacitor. Sounds like the system if seized up or cut off on low pressure.
The fact that the compressor is not running but, yet warn is not a good sign and may be siezed up.
The fact that the fan is not running when the compressor should be is not a good sign, you will have to verify proper voltage to the fan motor to determine the problem with the fan.
Also check for burnt windings in the compressor (between leads and all leads to ground (i.e.-comrpressor housing)).

__________________
kok328 is offline  
 
Reply With Quote Quick reply to this message
Old 05-18-2013, 04:42 AM  
kok328
Supporting Member
HRT_SUPPORTER.png
 
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,137
Liked 92 Times on 81 Posts
Likes Given: 59

Default

Ricky, I would have to agree but, under a private message the OP has indicated that he had the air handler portion replaced and that when he manually engages the contactor, the fan will come on. I suspect the contactor coil wires were not hooked up or not hooked up correctly.

__________________
kok328 is offline  
 
Reply With Quote Quick reply to this message
Old 05-19-2013, 05:54 PM  
hparkinson
Junior Member
 
Join Date: May 2013
Posts: 3
Likes Given: 2

Default

If you've checked the fan for free movement; checked the cap (be careful); you have power going to the fan; excessive heat; I will run a continuity across the fan wiring to see if the motor windings are still intact and even check it to ground. The overload protector has probably kicked in because of several reasons. Check the motor when it has cooled. Checking a hot motor may give you a false reading. At this point it sounds like you need a new motor. Don't forget, find out what caused the original problem and correct that first.

__________________
hparkinson is offline  
 
Reply With Quote Quick reply to this message
Old 05-19-2013, 07:43 PM  
kok328
Supporting Member
HRT_SUPPORTER.png
 
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,137
Liked 92 Times on 81 Posts
Likes Given: 59

Default

A lot of people ask for HVAC help but, when asked to perform a few preliminary test to help us narrow down the problem, they become overwhelmed and disappear.
Based on the information we were able to obtain, I'm pretty sure the fan motor is not the problem.



__________________
kok328 is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
carrier issue richtfan HVAC 2 08-29-2011 04:06 PM
Carrier Blower Will Not Turn On beaumoi HVAC 5 08-02-2011 06:26 PM
Carrier A/C Problem dttools HVAC 0 08-02-2010 10:52 PM
Carrier Thermostat viletha HVAC 5 02-07-2010 08:57 PM
Carrier Thermidistat sailpe HVAC 1 08-17-2009 08:26 AM