04-07-2010, 10:43 AM
|
|
|
Junior Member
Join Date: Apr 2010
Posts: 22
|
Carrier furnace fan won't switch on
I have a 10 year old Carrier furnace. When in heat/ac mode the fan will work, but it won't run continuously in "on" mode. When the heat/ac is "off", and the fan is "on", it won't work at all. It used to work continuously when in "on" mode. The blower motor was replaced a few months ago and the problems started then. The LED light is not showing any problems. Is there a quick fix?
|
|
|
04-07-2010, 01:19 PM
|
|
|
Moderator
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 1,856
Liked 26 Times on 25 Posts Likes Given: 12
|
Check to see if the green wire or wire from the G terminal on the thermostat is hooked up and likewise at the thermostat terminal connections inside the furnace.
|
|
|
04-07-2010, 02:09 PM
|
|
|
Junior Member
Join Date: Apr 2010
Posts: 22
|
yes, the green wire is hooked up on the thermostat and the furnace.
|
|
|
04-07-2010, 02:45 PM
|
|
|
Moderator
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 1,856
Liked 26 Times on 25 Posts Likes Given: 12
|
What happens when you jumper 24V from the red wired to the green wire?
If you remove the furnace panel door, make sure the safety switch doesn't cut power to the unit while testing.
|
|
|
04-07-2010, 02:51 PM
|
|
|
Junior Member
Join Date: Apr 2010
Posts: 22
|
I wouldn't know how to do that - please explain!
|
|
|
04-07-2010, 03:24 PM
|
|
|
Moderator
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 1,856
Liked 26 Times on 25 Posts Likes Given: 12
|
Oh sorry, sometimes I assume too much.
Take a piece of wire and strip the two ends.
Touch one end to the "R" terminal and the other end to the "G" terminal on the thermostat terminal strip inside the furnace.
As I mentioned, there may be a safety switch that will kill power to the unit when the access panel is removed. For the most part, you can just hold this in to restore power while testing.
Jumpering the R&G should run the blower motor.
|
|
|
04-07-2010, 07:26 PM
|
|
|
Junior Member
Join Date: Apr 2010
Posts: 22
|
What would I be achieving by doing this? I'm reluctant to try anything without knowing why I'm doing it. The blower motor does work if it's in heat mode, just doesn't stay on continously even tho the fan setting on the thermostat is set to "on".
|
|
|
04-07-2010, 08:43 PM
|
|
|
Moderator
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 1,856
Liked 26 Times on 25 Posts Likes Given: 12
|
I'm trying to guide you in troubleshooting the circuitry of the unit. This will basically tell us if the T-stat is bad or if there are other issues preventing the fan from working in the "On" setting. It's only 24VAC so no safety issues to be concerned about. If you prefer an alternate technique, you'll need a voltmeter. Turn your tstat to fan "On" and check for 24VAC from ground to "G" (green). This will tell me if the tstat is energizing the fan circuit or we can just energize it and see if the fan comes on which is what I was attempting in my prior post.
|
|
|
04-07-2010, 08:58 PM
|
|
|
Junior Member
Join Date: Apr 2010
Posts: 22
|
I don't have a voltmeter, but will attempt the test tomorrow. If the fan is energized this way, does it mean the tstat is bad?
|
|
|
04-08-2010, 05:43 AM
|
|
|
Moderator
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 1,856
Liked 26 Times on 25 Posts Likes Given: 12
|
If the fan turns on as a result of the test, it will either be a bad Tstat or the wiring from the Tstat to the furnace.
If you'd like, you can jumper the R & G terminals on the back of the Tstat and this will verify the wiring and result in determining a bad Tstat.
|
|
|