Default Compressor / Fan not running

Equipment: Gas Heat unit: Lennox G12 Series
Outside compressor Armstrong Concept 10

Experience: Novice at HAVC. Some electrical experience (house wiring and digital electronics)

Problem: Outside unit stopped working (both compressor and fan). Blower motor works ok. With the blue and yellow wire to the contactor coil leads disconnected and the thermostat commanding “Cool on” there is ~ 27Vac across the blue and yellow wires. Yet the contactor does not close the switch when the wires are connected to the coil leads. There is 246Vac across the input side of the contactor although I wouldn’t think this would affect whether the coil closes the switch. If the contactor switch is closed manually, the compressor and fan start and run ok.

Step 1: Replaced the contactor (which visually appeared to be in good condition). With a Furnas 45EG10AJA. Same symptoms.

Step 2: Replaced the thermostat with a used one laying around. Same symptoms.

Step 3: Shorted an 18v battery across the old contactor coil leads and the switch closed correctly.

This is the limit of my diagnostic skills. Is there a specification of the amperage the transformer must supply to the contactor coil? Is there a way to test the transformer? Any ideas how to further diagnose?

I cannot find a service or parts manual for the heat unit (Lennox site has an owners manual). Is there an online place to find these? Is there a place to find the part number for the transformer?

Any ideas or help would be greatly appreciated.



__________________
RLHdiy is offline  
 
Reply With Quote Quick reply to this message
Old 09-01-2011, 05:33 AM  
ozone
Junior Member
 
Join Date: Nov 2010
Location: Shelby Twp., Michigan
Posts: 11
Liked 1 Times on 1 Posts

Default

You have established that high and low voltage are present at the outside unit, good start. I have addressed and corrected the same problem a few times in the last month. Contactor -you replaced-. Tripped pressure switch will break low voltage -locate within cabinet and see if there is a reset, usually a red button-, this will require a later refrigerant pressure check. Low amps on the low voltage -check connections on either end of the wire as well as any splices between the two, it can be pinched and still look good so total replacement with new 18/2 is something to concider. After checking the above I would be suprised if the system doesn't work.



__________________
ozone is offline  
 
Reply With Quote Quick reply to this message
Old 09-02-2011, 09:58 PM  
RLHdiy
Junior Member
 
Join Date: Aug 2011
Location: Cincinnati, Ohio
Posts: 3
Default

OK, finally got it. Connecting the transformer directly to the contactor I found the contactor would activate correctly. At this point I suspected your suggestion about the wiring was correct. Fortunately the next step I took was to connect the transformer directly to the contactor using the 24AC wires fromt he inside unit to the outside unit. It still worked. Turns out, in the outside unit, there is a time delay relay. Once I wired this back into the circuit it failed again. From what I've read it delays the start of the compressor after shutoff to prevent restarting too soon. Anyway, this had failed. This device was in series with the 24Vac to the contactor and the net result was the 24Vac was grounded to the chassis and pulled down too much to activate the contactor. Wired around the delay relay and it works.

The thermistat in use has a compressor time delay feature also. This seems redundant. At the moment the system is working and I'm assuming the thermistat will provide the same protection. This may be a bad assumption I don't really know for sure.

__________________
RLHdiy is offline  
 
Reply With Quote Quick reply to this message
Old 09-03-2011, 04:23 PM  
hvactechfw
Professional
 
Join Date: Mar 2011
Location: Fort Wayne, IN
Posts: 66
Default

you are correct. The stat will provide the same protection as the delay on break timer.

__________________
hvactechfw is offline  
 
Reply With Quote Quick reply to this message
Old 09-03-2011, 07:57 PM  
RLHdiy
Junior Member
 
Join Date: Aug 2011
Location: Cincinnati, Ohio
Posts: 3
Default

Thanks ozone and hvactechfw for the help. Feels good to fix it myself and learn something along the way.



__________________
RLHdiy is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
no running water (on well) deadonion Plumbing Forum 2 03-28-2011 01:00 AM
Compressor not running in heat mode CD1 HVAC 3 01-06-2010 06:19 PM
Freezer fan not running Soxfann4381 Refrigerators 5 11-07-2009 06:58 PM
Wall heaters keep running Chris Klinzing Electrical and Wiring 3 04-19-2009 06:01 AM
Running Toilet Fix? SavvyCat Plumbing Forum 6 04-14-2009 09:18 PM