Default Goodman CPLE24-1C a/c tripping breaker

Hello all,

As it is starting to warm up we started to run our A/C and noticed it wasn't cooling the house. The fan was blowing so I went down and checked the breaker and sure enough the two 30amp breakers for the A/C were tripped. I flipped it and it held for a second and tripped again. Multiple attempts resulted in the same outcome, it would trip within seconds. I went outside and pulled the disconnect switch, went back and flipped the breaker, and it held. So I go back outside and reinstall the disconnect switch. I hear a slight humming sound and then a little click. After returning to the basement I see that the breaker has tripped again.

One thing of interest is that all this happened with the A/C turned OFF at the thermostat. If the thermostat was set to A/C the breaker trips even faster and even sparks.

I am a first year electrical engineer student who was recently laid off from work. So needless to say I would really like to try to diagonse this issue myself for financial and knowledge reasons. Thanks in advance for any assistance guys



__________________
BraDolMag1 is offline  
 
Reply With Quote Quick reply to this message
Old 05-20-2012, 07:48 AM  
kok328
Supporting Member
HRT_SUPPORTER.png
 
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,169
Liked 100 Times on 88 Posts
Likes Given: 61

Default

Sounds like you have multiple problems here.
First; the system should not be calling for A/C with the thermostat set to OFF.
You need to see if your getting 24VAC between common and the Y terminal at the thermostat when the thermostat is shut to OFF. If so then you may have a bad thermostat and/or shorted thermostat wires.
Once you get this problem resolved, you will need to disconnect the signal wires to the contactor inside the compressor unit outside. The breaker should hold now. If not, you need to determine if it is the compressor or fan motor that is causing the problem. Obviously, to do this you will need to separate the two off the circuit. I would advise to eliminate the compressor from the circuit as you don't want to run the compressor without the fan running. If the breaker holds then you compressor is could be bad; if the breaker trips then the fan motor is could be bad. You may want to check the capacitor for the compressor and fan. This could be a dual-run capacitor or separate capacitors for each component. Replace as necessary. Before concluding that the compressor and/or fan motor is bad, you might opt to replace the breaker as it could be getting weak/touchy. Check the fan motor by spinning it by hand and see if it spins freely. This is just a preliminary check and does not rule out the fact that the motor windings could be bad. Best of Luck to You.



__________________
kok328 is offline  
 
Reply With Quote Quick reply to this message
Old 05-20-2012, 07:21 PM  
lloyd
Junior Member
 
Join Date: Jul 2010
Location: Tulsa, Ok
Posts: 28
Default

Sounds like a case ground compressor. You can test this by using a meter to check for continuity between compressor terminals (after you pull the wires off) and the compressor case. Continuity between any of the terminals and the outside of the compressor means a new compressor.

__________________
lloyd is offline  
 
Reply With Quote Quick reply to this message
Old 05-21-2012, 07:04 AM  
kok328
Supporting Member
HRT_SUPPORTER.png
 
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,169
Liked 100 Times on 88 Posts
Likes Given: 61

Default

Good point Lloyd. I suspect the contactor welded closed when the compressor fried and explains why the system trips the breaker when not in A/C mode.

__________________
kok328 is offline  
 
Reply With Quote Quick reply to this message
Old 05-21-2012, 08:39 PM  
lloyd
Junior Member
 
Join Date: Jul 2010
Location: Tulsa, Ok
Posts: 28
Default

Yep, I'll bet that's right



__________________
lloyd is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Breaker keeps tripping david542 Electrical and Wiring 10 03-09-2012 11:38 AM
Lights suddenly tripping breaker MontyP Electrical and Wiring 3 11-12-2011 09:40 AM
Dryer tripping circuit breaker rageous General Appliance Discussion 6 09-24-2009 01:04 PM
Breaker Consistantly tripping mjpogue HVAC 6 05-31-2009 03:04 PM
ICP HeatPump Tripping Outside Breaker dplusm2004 HVAC 5 04-19-2007 08:46 PM