Heating unit
I have an outside propane Honeywell HVAC unit. The ignitor lights the flame but the gas valves aren't opening nor is the fan coming on. Help please!
|
Welcome Honeydo:
Your unit probably also has a draft inducer fan that is not comming on and the unit will not work until it is working. There should be a pressure switch on the exhaust and, if it doesn't feel the fan blowing, it locks out the gas valve. Look on the inside of the inspection panel for a wiring diagram which will tell you if there is a pressure switch and where to find it. That diagram also tells the route of power through the unit; it is possible to follow that checking the power at each point until you find the failure. Please let us know how it turns out. Glenn |
If you have proper voltage to the inducer fan but, the fan isn't blowing, then you've verified the problem.
|