Quote:
Originally Posted by tndave
To clarify post 5 has 98 volts, post 6 has 28, post 8 has 0, but if I unplug the wire and test the wire it has like 28 & post 3 has 0 volts. I tried post 3 with the wire that goes to the inducer off & it was not getting any current. Any help would be greatly appreciated.
Thanks!!
|
Ok you say that post 5 has 98 volts, If you follow the main 115 volts Hot power through the wiring diagram, it goes through door switch or interlock switch, down to 6 on fan relay, bK over to transformer and then over to your 5 post on system relay This should be 115 to 120 volts all the way. so check and see where you are losing voltage, should not be down to 98 volts.
After you get this right then on a call for heat you should get 24 to 27 volts when testing across from 7 to 8 on system relay. Check all this out first.
Paul