DIY Home Improvement, Remodeling & Repair Forum > Appliances > HVAC > Hot water heat: zone doesn't run unless another zone is also calling for heat




Reply
 
LinkBack Thread Tools Search this Thread Display Modes
Old 11-09-2011, 08:42 AM  
operagost
Junior Member
 
Join Date: Nov 2011
Posts: 5
Liked 1 Times on 1 Posts
Likes Given: 1

Default Hot water heat: zone doesn't run unless another zone is also calling for heat

I have a hydronic baseboard system in which the zone relay built into the aquastat stopped working. Instead of replacing the aquastat, I decided to add another Honeywell R845A and move the thermostat and circulator to that. The new relay is at the end of the "chain" of relays. I am using the provided diagram for a multizone system, which matches the way the existing relays were wired.

Each zone has its own circulator. The problem zone's circulator is hooked up to terminals 2 and 6. Terminal 2 is also hooked up to the common of the line power. The line hot is connected to terminal 3, which is jumpered over to 5. Terminals 1 and 4 are hooked up to 1 and 4, respectively, from the last relay in the line (which ultimately ends up at ZC and ZP on the aquastat, of course). The thermostat is hooked up to the thermostat terminals.

When the thermostat in the problem zone calls for heat alone, nothing happens. When another zone calls for heat while the problem zone is also calling for heat, the problem zone starts working as expected. When another zone calls for heat while the problem zone is not, only the other zone runs just as expected.

I use a Honeywell digital setback thermostat, but I tried changing its batteries and also testing with the old Honeywell round one that it replaced with no change.

I measured 120V between terminals 2 and 5 (and 2 and 3), but measured 24V across the thermostat terminals only when another zone is calling for heat. When no other zone is calling for heat, there is no power on this relay. So this appears to be the cause of the problem, but I don't know how to fix it.



__________________
operagost is offline  
 
Reply With Quote Quick reply to this message
Old 11-09-2011, 03:46 PM  
Blue Jay
Senior Member
 
Blue Jay's Avatar
 
Join Date: Jun 2008
Location: La Rue, Ohio
Posts: 250
Liked 10 Times on 10 Posts
Likes Given: 16

Default

Sounds like your zone control on the problem zone is NOT powered all the time but thru another zone control, you need to have it powered all the time instead of daisy chaned.



__________________
Blue Jay is offline  
 
Reply With Quote Quick reply to this message
Old 11-10-2011, 11:56 AM  
operagost
Junior Member
 
Join Date: Nov 2011
Posts: 5
Liked 1 Times on 1 Posts
Likes Given: 1

Default

It's not really "daisy chained"; I have terminal 1 on the previous relay jumped to terminal 1 on this relay. The same is true for terminal 4, so I thought I should have an unbroken link from the ZC and ZR.

__________________
operagost is offline  
 
Reply With Quote Quick reply to this message
Old 11-10-2011, 06:23 PM  
Blue Jay
Senior Member
 
Blue Jay's Avatar
 
Join Date: Jun 2008
Location: La Rue, Ohio
Posts: 250
Liked 10 Times on 10 Posts
Likes Given: 16

Default

Quote:
Originally Posted by operagost View Post
I measured 120V between terminals 2 and 5 (and 2 and 3), but measured 24V across the thermostat terminals only when another zone is calling for heat. When no other zone is calling for heat, there is no power on this relay. So this appears to be the cause of the problem, but I don't know how to fix it.
This is the key to your problem, not passing 24V to thermostat when this zone alone is calling for heat. Need to recheck the wiring.
__________________

Last edited by Blue Jay; 11-10-2011 at 06:26 PM.
Blue Jay is offline  
 
Reply With Quote Quick reply to this message
Old 11-11-2011, 11:41 AM  
operagost
Junior Member
 
Join Date: Nov 2011
Posts: 5
Liked 1 Times on 1 Posts
Likes Given: 1

Default

There appears to have been a break in one of the wires on terminals 1/4, which come from the ZC/ZR on the aquastat. I replaced the wires and all is well. Thanks.



__________________
operagost is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
An Old Taco Zone Valve rmmagow HVAC 1 01-07-2013 12:00 PM
Zone valve wiring Taco milbry18 Plumbing Forum 11 11-15-2011 11:49 AM
My hoover dishwasher wont heat the water? kaytav General Appliance Discussion 0 04-20-2011 07:45 AM
Exhaust Fan/Heater/Light: Panasonic vs NuTone vs. Air Zone? Abba_ General Home Improvement Discussion 2 05-07-2008 06:43 AM
zone valve stopped working marie38 Plumbing Forum 2 07-28-2007 05:43 AM