Default Humidifier wiring

I have a humidifier with a rotating cage and float switch for water supply. 25 year old lennox. Nothing labeled. Can I use the white and red wire coming from house thermostat to control humidifier cage motor



__________________
sgw1064 is offline  
 
Reply With Quote Quick reply to this message
Old 10-28-2010, 11:25 AM  
paul52446m
Senior Member
 
Join Date: Oct 2010
Location: Houghton Lake, Mi.
Posts: 435
Liked 1 Times on 1 Posts

Default

Quote:
Originally Posted by sgw1064 View Post
I have a humidifier with a rotating cage and float switch for water supply. 25 year old lennox. Nothing labeled. Can I use the white and red wire coming from house thermostat to control humidifier cage motor
I have been in the heating bus. for 40 years. If you are determined to wire it that way then go ahead. If you run too much amperage through the thermostat
you will burn it up. Most thermostats are made for max 1.2 amps, you might be running as much as 1/2 amp. right now, so how much amp draw is the other things you are adding. Then you have a transformer on the furnace that has a VA rating. To find out how much amperage you can run on a transformer, you take the VA rating and divide that by the voltage. 20Va divide 24volts is .8 so if you are already using 1/2 amp or .5 amp that only leaves you .3 amps left to run the rest of the things you want to add. I hate to get to tech. here, but these are the facts. Later Paul


__________________
paul52446m is offline  
 
Reply With Quote Quick reply to this message
Old 10-29-2010, 06:33 AM  
sgw1064
Junior Member
 
Join Date: Oct 2010
Location: blue springs, mo
Posts: 7
Default

Thanks paul i was just trying to find out if i could use existing 24V circuit to run humidifier motor. i decided to take your previous advice and tie into the blower circuit and add a transformer. works great and thanks again

__________________
sgw1064 is offline  
 
Reply With Quote Quick reply to this message
Old 02-01-2011, 08:31 AM  
ccpyue
Member
 
ccpyue's Avatar
 
Join Date: Feb 2011
Location: Toronto, Ontario
Posts: 40
Likes Given: 1

Default

Hello paul52446m - My humidifier cannot give me humidity over 26%. Pls help. Detail:

I newly installed a Lennox furnace and a Honeywell HE225 Flow-Thru Humidifier. I have the furnace FAN switch to ON all the time. My house humidity is as low as 26% only, can never exceed this. I need at least 35% for my skin problem. Problem I found is:

Water only supplies to the humidifier to make wet air is when the furnace is heating. Once the the furnace stopped heating (the FAN is still ON), water to the humidifier also stopped. I tried to turn the Humidistat, it "click" at around 25; but even I turn it to 40 and higher %, still on water supply to the humidifier. Therefore, my house humidity it very low.

What is the problem that cause this? How to overcome the water supplies problem, so that even the furnace is not heating, water still can supply to the humidifier to make air wet?

Thank you.

__________________
ccpyue is offline  
 
Reply With Quote Quick reply to this message
Old 02-01-2011, 11:12 AM  
paul52446m
Senior Member
 
Join Date: Oct 2010
Location: Houghton Lake, Mi.
Posts: 435
Liked 1 Times on 1 Posts

Default

Quote:
Originally Posted by ccpyue View Post
Hello paul52446m - My humidifier cannot give me humidity over 26%. Pls help. Detail:

I newly installed a Lennox furnace and a Honeywell HE225 Flow-Thru Humidifier. I have the furnace FAN switch to ON all the time. My house humidity is as low as 26% only, can never exceed this. I need at least 35% for my skin problem. Problem I found is:

Water only supplies to the humidifier to make wet air is when the furnace is heating. Once the the furnace stopped heating (the FAN is still ON), water to the humidifier also stopped. I tried to turn the Humidistat, it "click" at around 25; but even I turn it to 40 and higher %, still on water supply to the humidifier. Therefore, my house humidity it very low.

What is the problem that cause this? How to overcome the water supplies problem, so that even the furnace is not heating, water still can supply to the humidifier to make air wet?

Thank you.
how is humidifier wired into the furnace? If its wired to the HUM. post then it will only be powered when the furnace is heating.
Did you use a add on transformer to power it? If you did ,just power that
transformer from 120 volt so it will be hot all the time, then you can control it by the humidistat. Later Paul
__________________

Last edited by paul52446m; 02-01-2011 at 11:16 AM.
paul52446m is offline  
 
Reply With Quote Quick reply to this message
Old 01-02-2012, 01:56 PM  
Josty
Junior Member
 
Join Date: Jan 2012
Posts: 1
Default

I have my humidifier wired to the HUM terminals and am also having trouble getting the humidity level in the house where I want it. Going to try moving it to the EAC terminals so the cage will spin whenever the fan is on (not just when the furnace is running) and then set the fan switch on the thermostat to "ON" for a couple of days and see it that helps.

__________________
Josty is offline  
 
Reply With Quote Quick reply to this message
Old 01-02-2012, 05:38 PM  
paul52446m
Senior Member
 
Join Date: Oct 2010
Location: Houghton Lake, Mi.
Posts: 435
Liked 1 Times on 1 Posts

Default

Quote:
Originally Posted by Josty View Post
I have my humidifier wired to the HUM terminals and am also having trouble getting the humidity level in the house where I want it. Going to try moving it to the EAC terminals so the cage will spin whenever the fan is on (not just when the furnace is running) and then set the fan switch on the thermostat to "ON" for a couple of days and see it that helps.
That should do the job of letting it run through the hum. stat. Paul
__________________
paul52446m is offline  
 
Reply With Quote Quick reply to this message
Old 11-07-2012, 04:47 PM  
shake
Junior Member
 
Join Date: Nov 2012
Posts: 3
Default

sorry for highjacking this thread but it's the most relevant one I can find that is still recent. I'll make it short.

I have a furnace from the 80's so no humidifier connector.

I have a newer, dc wall-plug transformer powered, humidifier. So it basically runs all the time because there's no control.

I only want it on when heat is on.

Can I not just simply buy a 24vAC relay switch, connect one end to the furnace to toggle the switch, then connect the other end between the dc supply and the humidifier motor?

I don't know much about hvac but to me this sounds like it would work.

Where do I connect wires from the furnace / thermostat to the relay switch? To me, white = heat and black = common seems like the proper choice, but I'm uncertain.

I guess I don't know some fundamentals like is white positive or does it go to ground, does that wire switch - or + from the stat I suppose.

Thanks!

__________________
shake is offline  
 
Reply With Quote Quick reply to this message
Old 11-07-2012, 05:05 PM  
Wuzzat?
Senior Member
 
Wuzzat?'s Avatar
 
Join Date: Jan 2010
Posts: 2,135
Liked 135 Times on 123 Posts
Likes Given: 76

Default

You can put the 120vac AC input to the humidifier transformer across the 120vac blower motor "heating" winding but you have to unplug it when air conditioning is selected
because the blower motor acts like a transformer and there will be much more than 120v on this winding when the blower motor "cooling" speed is selected.

Another way to do it is with a sail switch in the duct.

You want an AND function: the humidifier comes on when
the air is too dry
AND
the heat is selected.

__________________

Last edited by Wuzzat?; 11-07-2012 at 05:12 PM.
Wuzzat? is offline  
 
Reply With Quote Quick reply to this message
Old 11-07-2012, 05:53 PM  
shake
Junior Member
 
Join Date: Nov 2012
Posts: 3
Default

Thank you. I'd rather not rig something up where the furnaces AC is literally connected to a two pronged ac to dc wallplug transformer like that one my humidifier uses. I think all I really need to do is put the relay between the power going to the humidifier motor. It seems like the simplest solution to me. I just don't want to drive that relay off the wrong wires, so I'm hoping do get that cleared up.


Thank you all the same

And yes you are exactly accurate:
what is want is so the humidifier comes on when the air is too dry AND the heat is selected.

I believe the setup should be, wall socket > wall ac to dc transformer > power wire from that to humidistat (old analog one) > line to relay switch > relay switch to humidifier motor.

Heat controls whether this relay switch is on or off. When heat is on, switch closes, circuit to humidifier is complete. When heat is of, relay switch opens, circuit to humidifier is incomplete.



__________________

Last edited by shake; 11-07-2012 at 06:03 PM.
shake is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Humidifier wiring sgw1064 Electrical and Wiring 9 10-28-2010 05:36 AM
Thermostat control of Honeywell HE365 Humidifier? skibumdc HVAC 0 09-02-2010 07:27 AM
Connecting humidifier to your furnace python01 HVAC 13 03-04-2010 07:54 AM
Whole house humidifier brasilmom HVAC 13 12-10-2009 07:19 AM
help removing humidifier on furnace smoothbore26 HVAC 0 09-12-2009 02:46 PM