Default Re-routing condensate line?

OK, I am a bit out of my depth here .... c'mon HVAC pros, help me out.

The diagram below explains the situation. The AC unit has a condensate sump actuated pump that sends the runoff in the designated direction of flow. The piping seems to go to the blower unit which does not have AC.

First, does the condensate water get used by the blower unit typically?
Second, if not, can I re-route the condensate to a closer floor drain?

The drop ceiling and presence of walls and equipment makes it almost impossible to insepct the connection point (or not) of the condensate line at the blower unit. Being 98 degrees in the ceiling does not help either!

Your thoughts???





__________________
CallMeVilla is offline  
 
Reply With Quote Quick reply to this message
Old 09-07-2013, 08:16 AM  
kok328
Supporting Member
 
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,081
Liked 71 Times on 66 Posts
Likes Given: 50

Default

First, does the condensate water get used by the blower unit typically? NO
Second, if not, can I re-route the condensate to a closer floor drain? YES

What's not making sense here is that you have to blow the air over the evaporator coils to get A/C.
Why is your blower & evaporator coils separate units and how does air get blown over the evap coils.

If this is a high efficiency furnace, then it will produce water vapor when combusting the gas to the burners. This condensate needs to be channeled to an appropriate receptacle. Perhaps instead of running two lines, they just dumped the A/C condensate into the air handler to be channeled away with the burner condensate.



__________________
kok328 is offline  
 
Reply With Quote Quick reply to this message
Old 09-07-2013, 06:27 PM  
CallMeVilla
Senior Member
 
CallMeVilla's Avatar
 
Join Date: Feb 2010
Location: San Diego
Posts: 1,054
Liked 266 Times on 216 Posts
Likes Given: 105

Default

Thanks for the input ... I went ahead and shunted overflow from the pumped condensate line to a separate (secondary) line which led water to the floor drain.

The AC unit develops condensate from the evap coils. The condensate gets pumped out (like most AC units) but the direction of the flow was toward a separate unit which I labelled as a Blower unit. That unit has no cooling, just air movement. I suspected the condensate water (being cold) could be push thru a coil to capture the energy as the blower pushed air over it. Think of it as a heat exchanger in reverse.

Absent info to the contrary, I re-piped and all seems to be working just fine.



__________________
CallMeVilla is offline  
 
Reply With Quote Quick reply to this message
Old 09-09-2013, 07:45 PM  
Caduceus
Plumber
 
Caduceus's Avatar
 
Join Date: Aug 2011
Location: Pittsburgh, Pennsylvania
Posts: 25
Liked 8 Times on 7 Posts
Likes Given: 1

Default

Just a side note...A/C condensate draining into a blower sounds like an ideal design for a legionnaires situation. It's a good thing that you found this and fixed it. The original installer should have realized this.

__________________
Caduceus is offline  
nealtw Likes This 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
re-running condensate drain beachguy005 HVAC 4 01-25-2013 09:41 AM
Condensate problem bnmb3273 Introductions 3 07-17-2012 04:14 PM
Confused on wire groupings/routing rvs0002 Electrical and Wiring 4 03-20-2011 01:32 PM
Condensate drain question Phatboy HVAC 5 10-09-2007 07:20 PM
Romex Routing in Attic 69-er Electrical and Wiring 3 02-19-2007 02:40 PM