Default Trane XE90 Pressure switch code. Truth?

Hello all. My six year old Trane XE90 refuses to produce heat. I go to turn the unit on and nothing happens. The circuit board will blink acknowledging the call for heat, then about 5 seconds later will blink indicating a pressure switch problem (3 blinks). I took the switch off and metered acrossed the leads and physically pushed the microswitch and the switch still swithces. I have cleaned out the drain and traps. The vent tubes are clean as is the exhaust tube going through the roof. If I take the pressure switch wires and short them together will this bypass the switch so that I can see if this is the problem? I want to make sure that the pressure switch is actually bad before I buy one.



__________________
showngo2000 is offline  
 
Reply With Quote Quick reply to this message
Old 10-09-2008, 09:01 AM  
glennjanie
Senior Member
 
Join Date: Mar 2006
Posts: 2,990
Liked 2 Times on 2 Posts

Send a message via AIM to glennjanie
Default

Welcome Showngo:
Is the forced vent fan running? That is the pressure the switch is supposed to feel. If it is not evacuating the combustion products the pressure switch will not turn on.
Bypassing the switch could get you gassed if the vent fan is not running.
Glenn



__________________
glennjanie is offline  
 
Reply With Quote Quick reply to this message
Old 10-09-2008, 04:00 PM  
showngo2000
Junior Member
 
Join Date: Oct 2008
Posts: 4
Default

No, nothing is running at all. The call for heat goes in, then a few relay clicks in the unit, then the LED flashes 3 times constantly.

I'm stumped as to what is going on.....please help.

__________________
showngo2000 is offline  
 
Reply With Quote Quick reply to this message
Old 10-09-2008, 07:37 PM  
kok328
Supporting Member
HRT_SUPPORTER.png
 
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,169
Liked 100 Times on 88 Posts
Likes Given: 61

Default

DO NOT BYPASS THE PRESSURE SWITCH.
With the burn box full of gas, you will blow yourself up and burn down your home.

You mentioned that nothing is happening on a call for heat.
This may be due to a bad venter motor. Check for power at the venter motor during startup to see if the venter motor is bad. If this the first startup of the season, you may have to bump it a little with whatever you can get to reach the windings or fan blades. Nurse it with a little white oil and you should be fine.
The pressure switch is not being made, due to the venter motor not coming on but, once the venter motor satisfies the pressure switch, the system will go into ignition mode.

Check for any resets on the transformer, overloads (if applicable), roll out switches, etc....
__________________
kok328 is offline  
 
Reply With Quote Quick reply to this message
Old 10-09-2008, 07:48 PM  
showngo2000
Junior Member
 
Join Date: Oct 2008
Posts: 4
Default

Should the venter motor have 120VAC? Because it only has 8VAC. Maybe a bad control board?

__________________
showngo2000 is offline  
 
Reply With Quote Quick reply to this message
Old 10-10-2008, 09:34 AM  
glennjanie
Senior Member
 
Join Date: Mar 2006
Posts: 2,990
Liked 2 Times on 2 Posts

Send a message via AIM to glennjanie
Default

Hello Showngo:
Yes, the vent motor should show 120v. I would not say its the panel board yet unless there is a burned spot on the board. Look at it closely and see if one of the resistors or transistors has been burned; if not, I would look at the relays; they can be very tricky.
Follow the wiring diagrahm point by point checking the voltage until you loose it; that's where the repair usually needs to be done.
Glenn

__________________
glennjanie is offline  
 
Reply With Quote Quick reply to this message
Old 10-11-2008, 11:17 AM  
hvaclover
Junior Member
 
hvaclover's Avatar
 
Join Date: Oct 2008
Posts: 1
Default

Does that ventor make it's usual sound when it (ie. ventor noise).

If the switch is closing a voltage reading of 110v to gound off each side of the switch. The board lights are not always reiable and ae used more as a guide then the last word of what ia causing your no heating issue.

__________________
hvaclover is offline  
 
Reply With Quote Quick reply to this message
Old 10-13-2008, 04:26 PM  
showngo2000
Junior Member
 
Join Date: Oct 2008
Posts: 4
Default

Quote:
Originally Posted by hvaclover View Post
Does that ventor make it's usual sound when it (ie. ventor noise).

If the switch is closing a voltage reading of 110v to gound off each side of the switch. The board lights are not always reiable and ae used more as a guide then the last word of what ia causing your no heating issue.
The ventor motor makes no noise at all. It doesn't run at all.


__________________
showngo2000 is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Trane XE 90 pressure switch eddie HVAC 70 12-17-2013 05:14 PM
High limit problem on Trane XE90 Garvey HVAC 1 11-10-2011 08:33 AM
Pressure switch stuck open? 2 areas im looking @ 1001miles HVAC 6 11-02-2008 11:03 AM
Trane xe 90 led indicates pressure switch jskalic HVAC 1 11-29-2007 10:38 PM
Furnace draft pressure too low Alwaysfixinsumthin HVAC 1 10-26-2007 11:18 PM