Quote:
Originally Posted by kok328 View Post
Ok, I'm lost now (not really) but, you see my point.

DaveDIY says:
"12-3 = 2 hots & a neutral & a ground
If fed out of phase the load blances against each other on the neutral
IE 15a on one, 10a on the other - neutral carries 5a
If on the same phase the loads ADD for the neutral
IE 15a + 15A = 30a on the neutral - TOO MUCH!!"


TripleD says:
"However at no point along those circuits can the neutrals touch. I and others like me volunteer ourselves to assist people in a safe way. I am simply trying to do that for you. Are your neutrals touching?"


Also, I'm curious, DaveDIY, why would you want to nusiance trip a non-offending circuit w/a two pole breaker?

Why would you run a 240V circuit when the destination is not 240V?
"Under NEC 2008 a multi-wire circuit is required to have a double breaker so that both hots shut off. This is the preferred method as it automatically puts the 2 hots on opposite sides - "out of phase""

I'm not totally sure what you mean by a "multi-wire circuit" but, I don't believe what vdotmatrix is doing, constitutes a multi-wire circuit or were you referring to my input on sharing a neutral. This still does not constitute a "multi-wire circuit".

Again, I'm curious and would like to be enlightened because if what your saying is true, I've got a ton of wiring problems in at least 4 out of 5 plants I work in.
It s a new change in NEC 2008
When you are running a multiwire circuit you are sharing the neutral between the 2 circuits. You do not have to go back & fix pre-existing wiring. In 2005 only the connected bar was required between the breakers.
But 2 problems were identified:
#1 People were not installing the bar, or it was removed
As a result the breakers couild end up on the same phase & the power doubles on the shared neutral from the 2 circuits
#2 One breaker could be shut off, the other left live
Since this is a shared neutral power could flow on the circvuits that is shut off via the shared neutral

A 240v breaker is now required to prevent this
You are not supplying 240v, you are supplying 120v to 2 different circuits & using a shared neutral

As long as you have 2 circuits & seperate neutrals you are fine
This is only for Multi-wire circuits that share a neutral
Neutrals from 2 different circuits in the same box should not touch
All of the grounds are supposed to be tied together in the box

Hope that clears it up?

I have 3 setups using multiwire circuits
Each one is fed w/a 20a 240v breaker, power goes to a 40a dual 120v timer
After the timer there is a seperate run of 12-2 (GFCI protected) to outlets in my front garden & around the house
My multiwire circuit is only 12" long as the timers are connected to my panel
I knew of the upcoming change for 2008 so I used the 240v breakers
It makes sense, if the breaker is shut off then I know all power in the timer is off

The code is always changing - updated every 3 years
The wording can be very hard to understand
I've been in discussions with electricians, Inspectors & others on certain aspects of the code. In some cases each one has a different view of what the code actually is saying

By code you can run a 20a 120v circuit - UF wire - 12" deep without conduit. So long as it is GFCI protected befor eit goes in the trench. I wanted to run 2 circuits in the trench (6" wide), both 20a GFCI protected. Everyone I ran it by said that was perfectly acceptable
My Inspector did not fully agree, he said I needed 12" between the circuits in the trench. So I ended up running conduit


__________________
DaveyDIY is offline  
 
Reply With Quote Quick reply to this message
Old 04-15-2009, 07:58 AM  
speedy petey
Lic.Electrical Contractor
 
Join Date: Mar 2006
Posts: 445
Liked 39 Times on 27 Posts
Likes Given: 17

Default

Quote:
Originally Posted by kok328 View Post

I'm not totally sure what you mean by a "multi-wire circuit" but, I don't believe what vdotmatrix is doing, constitutes a multi-wire circuit or were you referring to my input on sharing a neutral. This still does not constitute a "multi-wire circuit".
A "multi-wire branch circuit" is the correct term for a shared neutral circuit.
This is two (or three in the case of a 3-phase MWBC) hots sharing one neutral where the line conductors are placed on different "legs" of the panel as Dave described.
__________________
speedy petey is offline  
 
Reply With Quote Quick reply to this message
Old 04-15-2009, 08:44 AM  
kok328
Supporting Member
HRT_SUPPORTER.png
 
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,196
Liked 112 Times on 97 Posts
Likes Given: 64

Default

Thanks Dave, now I understand.
So I guess the gist of it is, do not create a multi-wire circuit where you can not tolerate one circuit tripping the other.

Thanks Again.

__________________
kok328 is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Can I wire this together. Phatboy General Appliance Discussion 4 11-03-2008 10:11 PM
funny acting circuits? lartomar2002 Electrical and Wiring 6 03-11-2008 03:53 PM
What size wire? dakuda Electrical and Wiring 2 08-05-2007 02:48 PM
1 wire short wheelman HVAC 2 10-22-2006 11:09 PM
new circuits peltaz Electrical and Wiring 2 09-30-2006 10:03 PM