Scot Clark 02-02-2007 07:24 AM

230v welder, 240v compresser - breaker & wire size?
 
Hi:

I have a Lincoln Arc welder 230V 1 phase 60Hz. Came with a 50 amp
plug and also a 50 amp recepticle. Wondering proper breaker and wire
size to use. 50 amp breaker and #6 wire? Or does the breaker need
to be more amps?

The compressor is 11 peak HP, 7.5 run HP.
240 votls at 30 amps.
Would I use #8 wire and a 40 amp breaker?

** Thanks **

Scot Clark 02-02-2007 11:29 AM

Hi:

Also wondering if 35 to 40 feet away from breaker panel is ok.
They say the closer the better for less voltage drop.

Thanks !

petey_racer 02-02-2007 02:34 PM

For your welder #6 is fine. In a residence 6/2NM is what I would use. You do NOT need 6/3 for this.
A two-pole 50 amp breaker is correct.

Is 30 amps the exact spec (running amps) for the compressor? If so then yes, #8 is good. Again, 8/2NM is what I would use on a 40 amp breaker.


At 35-40 feet voltage drop is not at all an issue.

Scot Clark 02-02-2007 02:50 PM

Hi Mr. Petey:

Thanks so much.
Yes, the compressor is 30 amps - running.