230v welder, 240v compresser - breaker & wire size?
Hi:
I have a Lincoln Arc welder 230V 1 phase 60Hz. Came with a 50 amp plug and also a 50 amp recepticle. Wondering proper breaker and wire size to use. 50 amp breaker and #6 wire? Or does the breaker need to be more amps? The compressor is 11 peak HP, 7.5 run HP. 240 votls at 30 amps. Would I use #8 wire and a 40 amp breaker? ** Thanks ** |
Hi:
Also wondering if 35 to 40 feet away from breaker panel is ok. They say the closer the better for less voltage drop. Thanks ! |
For your welder #6 is fine. In a residence 6/2NM is what I would use. You do NOT need 6/3 for this.
A two-pole 50 amp breaker is correct. Is 30 amps the exact spec (running amps) for the compressor? If so then yes, #8 is good. Again, 8/2NM is what I would use on a 40 amp breaker. At 35-40 feet voltage drop is not at all an issue. |
Hi Mr. Petey:
Thanks so much. Yes, the compressor is 30 amps - running. |