Old 01-08-2007, 03:47 PM  
jetjaguar
Junior Member
 
Join Date: Jan 2007
Posts: 2
Default advice about new wiring for heaters

I have a small home in So. Cal. Built 1947, concrete slab. We want to install baseboard heaters. A single portable heater is already tripping the breaker.

An Electrician we had called recommended we run new wiring just for the baseboards, so they won't trip other breakers. Maybe even one breaker per heater (6).

My question is, roughly what can I expect in terms of hours to run this cabling with the work that needs to be done on the panel as well? Each heater is 1500 Watts, 240 volts, 5118 BTU. I realize each room is a different distance from the panel, but if someone can give a ballpark estimate, maybe as a function of feet from the panel, that will be very helpful.


thanks in advance,

Peter



__________________
jetjaguar is offline  
 
Reply With Quote Quick reply to this message
Old 01-10-2007, 04:25 PM  
Parrothead
Member
 
Join Date: Dec 2006
Location: , WI
Posts: 65
Likes Given: 1

Default

It is difficult to estimate the time involved without actually seeing the property and what unique little challenges present themselves. I'm used to homes with basements or at least crawl spaces, which tends to make things easier.

I agree that you should put these heaters on dedicated circuits, but I don't think it's necessary to have each one on its own. That would require 12 spaces in your breaker panel. You could easily put two heaters on a 20 amp circuit, thus reducing your needed space to six, not to mention cutting your conductor length in half.



__________________
Parrothead is offline  
 
Reply With Quote Quick reply to this message
Old 01-10-2007, 07:08 PM  
Snoonyb
Member
 
Join Date: Sep 2006
Posts: 46
Liked 1 Times on 1 Posts

Default

Just out of curiosity, why would you entertain that heating appliance for this region?

__________________

Illigitimas non-carborundum

Snoonyb is offline  
 
Reply With Quote Quick reply to this message
Old 01-11-2007, 11:46 AM  
glennjanie
Senior Member
 
Join Date: Mar 2006
Posts: 2,992
Liked 2 Times on 2 Posts

Send a message via AIM to glennjanie
Default

JetJaguar; I can see that the electric baseboard heaters would be the most economical system to install; and the utilities claim they are very efficient to operate as long as each room has a seperate thermostat and un-used rooms are turned off. Also, do you live in a rural area where other fuels would not be dependable or even available?
If you do use the system of turning off un-used rooms, make sure you are careful about freezing water in those rooms. Some heat tape might come in very handy here.
Glenn

__________________
glennjanie is offline  
 
Reply With Quote Quick reply to this message
Old 01-11-2007, 12:31 PM  
renoguy
Junior Member
 
Join Date: Dec 2006
Posts: 3
Default baseboard heat

Quote:
Originally Posted by jetjaguar View Post
I have a small home in So. Cal. Built 1947, concrete slab. We want to install baseboard heaters. A single portable heater is already tripping the breaker.

An Electrician we had called recommended we run new wiring just for the baseboards, so they won't trip other breakers. Maybe even one breaker per heater (6).

My question is, roughly what can I expect in terms of hours to run this cabling with the work that needs to be done on the panel as well? Each heater is 1500 Watts, 240 volts, 5118 BTU. I realize each room is a different distance from the panel, but if someone can give a ballpark estimate, maybe as a function of feet from the panel, that will be very helpful.


thanks in advance,

Peter
Questions to ask yourself about the baseboard installation:
How big is the AMPERAGE of the electrical service in the house?
(usually 60, or 100 in an older house like that) If the service is under 100 amps I would not recommend any baseboard heat at all.
so, then if your service is 100 amps or over, the second question is:
How many empty panel spaces are there?(spaces for more breakers in your panel)
You will need at least 4 empty spaces (for two 240volt circuts)

SO, if you have enough amperage and enough empty spaces, then the installation should be fairly reasonably priced. The only other thing that would affect price would be if there is an easy route for the wires to be run, if the walls are opened up already it's a lot easier for the electrician to do the work, if he has to "fish" wires behind finished walls, it'll be more expensive.
hope this helps you. good luck!
__________________
renoguy is offline  
 
Reply With Quote Quick reply to this message
Old 01-11-2007, 12:37 PM  
renoguy
Junior Member
 
Join Date: Dec 2006
Posts: 3
Default

PS.....If you live where it doesn't freeze outside in the winter, don't bother with 1500 watt heaters for a 10 x 10 room, it's way overkill! half that size would be okay. I live in a place where the winters can get real cold (Canada) and a 1000 watt baseboard heater in the bedroom is fine.

__________________
renoguy is offline  
 
Reply With Quote Quick reply to this message
Old 01-14-2007, 11:36 AM  
jetjaguar
Junior Member
 
Join Date: Jan 2007
Posts: 2
Default thanks everyone for your responses

It's a rental house and and the tenants want to be warm. There is no other heating available. There is a broken down hvac on the roof (no crawlspace) but it is beyond repair, had it checked by two different techs.

I realize now that we just need to get an electrician out there to look at the job and quote. That has been scheduled now.

The only thing I'm wondering about is the amperage to the whole house...based on one of the responses. I guess we'll know soon enough.

Thanks again everyone,

Peter



__________________
jetjaguar is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Need a lot of advice... LeMetsker General Home Improvement Discussion 6 01-19-2010 07:14 PM
Two questions regarding outlet wiring Pastey Electrical and Wiring 5 04-14-2007 12:00 PM
Having trouble wiring thermostat swinny Electrical and Wiring 2 11-29-2006 09:08 PM
Is existing microwave and oven wiring safe? ctraut Electrical and Wiring 6 11-15-2006 11:53 AM
knob and tube wiring info wanted. wienerwater Electrical and Wiring 3 09-30-2006 09:04 PM