djosephs: are you sure these baseboard heater are 110. They make them both 110 and 220. If you are not getting a voltage reading at the baseboard heater but you feel a tingle you need a different type of voltage meter,one that will read a low voltage situation. And that is what it sound like. A all your base board on the same circuit breaker? They should be on separate breakers but you need to verify that. Are you sure you have 110 coming out of each breaker? If you have a circuit problem you may be getting feed back from another circuit. the best way to check this is to take voltage reading between the 2 phases. In most panels every other breaker is on the same phase. There is normally 2 phases in the panel and if you test voltage between the 2 phases you should read 220. Phase is just a term used for the hot wires coming in to feed the panel. It sound like you are having problems with more than 1 circuit you may have as you stated one bad leg or phase. I hope this helped
|