Old 09-26-2011, 09:31 PM  
ChollaBob
Junior Member
 
Join Date: Sep 2011
Posts: 9
Default Breaker Box Ground Wire

We recently lost power to one leg of our electrical which was caused by dual 50 amp breaker which had gone bad. On repairing the box, I noticed there was no ground wire to the neutral/ground bar. The power company meter above the pole breaker box has the ground running from a ground stake at the base of the pole to the meter. The large gauge, coiled bare ground runs into the meter. The meter connects to the breaker box with two inches of galvanized pipe. There is continuity when probing the steel between the two boxes. I measured a resistance of about 3.5 ohms between the two boxes. I read that this is legal in some states, but I am concerned that this setup is providing a proper ground. Everything is running fine now; no problems but want to confirm as the box is old.

Besides losing half our power, we had dimming, flickering, and brightening bulbs before the power died and I believe this is an open neutral condition. Does a bad ground contribute to this? Does running a second ground to the breaker box defeat ground faulting and bonding? Learning but slowly getting these concepts. Thanks for any help!

http://i1131.photobucket.com/albums/.../DSC_0168B.jpg

http://i1131.photobucket.com/albums/...llaBob/Fly.jpg



__________________

Last edited by ChollaBob; 09-27-2011 at 11:03 AM.
ChollaBob is offline  
 
Reply With Quote Quick reply to this message
Old 09-27-2011, 08:41 AM  
kok328
Supporting Member
HRT_SUPPORTER.png
 
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,196
Liked 112 Times on 97 Posts
Likes Given: 64

Default

The black wire with green tape on it is the ground wire to the neutral/ground bar.
The problem you have is that the neutral and ground bar are not separate as they should be on what appears to be a sub-panel.



__________________
kok328 is offline  
 
Reply With Quote Quick reply to this message
Old 09-27-2011, 11:03 AM  
ChollaBob
Junior Member
 
Join Date: Sep 2011
Posts: 9
Default

The green taped wire is the ground going to the house subpanel. This box serves as the main breaker box. Inside the main are the main dual 50 amp breaker, a dual 20 amp breaker for a well, and a breaker for an outdoor outlet. On main breaker boxes, I believe the ground and neutral are bonded, but will have to confirm.

Attached is a link on how the bare ground wire (tinted green) goes into the meter. The only ground connection between the meter and the main breaker box is the galvanized pipe. There is continuity between the boxes. Is this OK?
The big issue right now is grounding and ground/neutral buss bar. I want to make sure there is no more open neutrals. Replacing the bad breaker seemed to fix everything but want to safeguard all other possible problems.

Thanks for the help!

PS: This main breaker box will be replaced in the Spring.

__________________

Last edited by ChollaBob; 09-27-2011 at 11:14 AM.
ChollaBob is offline  
 
Reply With Quote Quick reply to this message
Old 09-27-2011, 12:03 PM  
kok328
Supporting Member
HRT_SUPPORTER.png
 
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,196
Liked 112 Times on 97 Posts
Likes Given: 64

Default

A 50amp main? Wow, you really do need an upgrade.
Yes, the neutral bar and the ground bar would be bonded together in the main panel but, not in a sub panel.
I'm not a big fan of using conduit as a ground conductor but, it will suffice for now.

__________________
kok328 is offline  
 
Reply With Quote Quick reply to this message
Old 09-27-2011, 12:18 PM  
ChollaBob
Junior Member
 
Join Date: Sep 2011
Posts: 9
Default

This is probably a 100 amp main as it is two ganged 50 amps, if that is how this translates. This panel supplies a single wide and the sub-panel is new and well wired. I do need an upgrade on the main panel!

I would prefer a direct ground to the main breaker box, but the meter is off-limits. Most likely, a second ground direct to the box is going to defeat the ground fault path, but have to confirm this.

So it looks like this setup is OK for the time being as I now realize the havoc this bad breaker was doing to our place as we lost some appliances.

I am thinking about replacing the well dual 20 amp breaker as there was a clay wasp nest on the buss bar, some of it fell down.

Thanks for the help!

__________________
ChollaBob is offline  
 
Reply With Quote Quick reply to this message
Old 10-20-2011, 07:53 PM  
ishiboo
Junior Member
 
Join Date: Oct 2011
Posts: 1
Default

Quote:
Originally Posted by ChollaBob View Post
This is probably a 100 amp main as it is two ganged 50 amps, if that is how this translates. This panel supplies a single wide and the sub-panel is new and well wired. I do need an upgrade on the main panel!

I would prefer a direct ground to the main breaker box, but the meter is off-limits. Most likely, a second ground direct to the box is going to defeat the ground fault path, but have to confirm this.

So it looks like this setup is OK for the time being as I now realize the havoc this bad breaker was doing to our place as we lost some appliances.

I am thinking about replacing the well dual 20 amp breaker as there was a clay wasp nest on the buss bar, some of it fell down.

Thanks for the help!
100A service has two ganged 100A breakers. That is a 50A service which is very small... a matter of opinion, of course. 200A (4 times what you have) is whats common now, though I can get by on 100A just fine as long as there's not electric heat or instant hot water. Perhaps 50A is common for mobile homes, I'm not sure?

The grounding looks correct if the neutral bar is bonded to the case, since that is where your ground is hooked up. Newer setups would have a separate ground/neutral bus, but you're fine without it until you feel like updating.


__________________
ishiboo is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Oven, How to wire a 4 wire oven to 3 wire recepticle dacrew4009 Electrical and Wiring 6 03-17-2010 09:18 PM
120v on ground wire Milwaukean Electrical and Wiring 1 12-31-2008 02:58 PM
Question on shared ground/neutral buss in breaker box banyan Electrical and Wiring 5 06-29-2008 01:39 AM
230v welder, 240v compresser - breaker & wire size? Scot Clark Electrical and Wiring 3 02-02-2007 02:50 PM
interesting ground wire hawkestone Electrical and Wiring 10 07-23-2006 02:26 PM