Old 09-12-2011, 09:54 AM  
mmaarrkk
Junior Member
 
Join Date: Sep 2011
Location: Omaha, NE
Posts: 1
Default Electrical Panel

Thanks for all the great information. I have learned so much from everyone. One thing I learned is that my main electrical panel is a mess. I wanted to add a new breaker so I opened the panel and found numerous spots where the ground and nuetral wires are under the same screw. From what I can tell they are not part of the same circuit. I don't know if that makes a difference. My question is, should I clean these bus bars up. Should I remove all the wires and place the nuetrals under single screws and possibly triple the grounds so I have enough room for the new breaker. Can I add a new bus bar? If so, how?

I went back to look at my original home inspection to see if this was missed. The inspector passed it because none of the hots were double wired and the nuetral and grounds were not wired together in a sub panel. Is this correct.

Thanks so much!!



__________________
mmaarrkk is offline  
 
Reply With Quote Quick reply to this message
Old 09-12-2011, 01:12 PM  
kok328
Supporting Member
HRT_SUPPORTER.png
 
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,169
Liked 100 Times on 88 Posts
Likes Given: 61

Default

The main panel will have ground and neutral sharing the same bar.
The sub panle will have the ground and neutral separate.
You can double the ground or neutral in either panel as long as you observe the rules previously stated.



__________________
kok328 is offline  
 
Reply With Quote Quick reply to this message
Old 09-12-2011, 05:21 PM  
JoeD
Contractor
 
Join Date: Mar 2006
Location: Welland, Ontario
Posts: 930
Liked 91 Times on 76 Posts

Default

You can not double the neutral in main or sub panel. One neutral wire per terminal.

__________________
JoeD is offline  
 
Reply With Quote Quick reply to this message
Old 09-12-2011, 05:50 PM  
speedy petey
Lic.Electrical Contractor
 
Join Date: Mar 2006
Posts: 436
Liked 32 Times on 23 Posts
Likes Given: 13

Default

Quote:
Originally Posted by JoeD View Post
You can not double the neutral in main or sub panel. One neutral wire per terminal.
+1
__________________
speedy petey is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
hot tub sub panel help seaox Electrical and Wiring 4 10-20-2009 06:53 PM
Is this a 'proper' way to install a new electrical panel? viki412ag Electrical and Wiring 10 04-15-2009 07:54 AM
Panel or subpanel rjarrett001 Electrical and Wiring 5 02-14-2008 05:22 PM