Old 08-27-2013, 05:54 AM  
toofast
Member
 
Join Date: Feb 2011
Location: columbia station, OH
Posts: 36
Default Generator install - unique home wiring or not

I was not sure what to call this thread....so here we go.

I bought a Generator that would power 10 - 20 amp circuits in my house. We live in the country and often lose power, especially in the dead of night in the winter...plus I travel. So wife does not love getting up in the middle of the night in a snow storm to stay in a hotel with our 3 year old.

OK....now the problem.

The Generator Installer got everything set, then went to wire the 10 circuits and said OPPPS, you are in trouble. I can only use "5" of the circuits you wanted, because the electricians when they built the house "cheated" and you don't really have dedicated circuits. For example...my hot water tank is gas, but on its OWN 20 AMP circuit, however coming into the main panel is a 12 - 3 line, one of the hots feeding the hot water tank, and another hot feeding the foyer lights, sharing a neutral.

So the way the generator is setup, he says I have to move BOTH circuits because the generator circuit takes control and I can't "split" the neutral.

Hopefully that made sense ?

With that in mind, what options do I have. My neighbor who is a EE told me that I could CHEAT YET again, and it might not be CODE, but the way your house is wired you would never have an issue. What he means is that I have 200 amp service with "dedicated" circuits in every room. In the example above he said I could combine the hot water line and the foyer line (runs a single light with 4 40 watt bulbs) together and I would NEVER come close to overloading that circuit.

He said I could do this with MOST of the circuits that are setup with this 12-3 shared neutral and I should be ok.

That does not feel right, but it might be my only option. I can't afford to re-wire my entire house. Is there any other way to perhaps put in a junction box and somehow split that back out...meaning move the 12-3 into a box, then take two 12-2 and run one to the main (aka foyer) and then run the other 12-2 into the genny panel for hot water. Or will this cause an issue with the neutral and when the genny kicks in all heck will break loose.

Ok...hopefully this is enough to get some guidance and of course if you need more details just yell.



__________________
toofast is offline  
 
Reply With Quote Quick reply to this message
Old 08-27-2013, 06:19 AM  
toofast
Member
 
Join Date: Feb 2011
Location: columbia station, OH
Posts: 36
Default

Ok, I did a bit more research and I THINK this is called multi-wire branch circuit (MWBC).

Hope this helps.



__________________
toofast is offline  
 
Reply With Quote Quick reply to this message
Old 08-27-2013, 07:24 AM  
JoeD
Contractor
 
Join Date: Mar 2006
Location: Welland, Ontario
Posts: 966
Liked 102 Times on 84 Posts
Likes Given: 4

Default

You are correct. They are called multi wire branch circuits. They are legal and not cheating. It saves cable and expense when wiring a house.
He is correct that both of them must be moved.
I would not be following your neighbour's directions.

__________________
JoeD is offline  
 
Reply With Quote Quick reply to this message
Old 08-28-2013, 02:28 PM  
toofast
Member
 
Join Date: Feb 2011
Location: columbia station, OH
Posts: 36
Default

Quote:
Originally Posted by JoeD View Post
You are correct. They are called multi wire branch circuits. They are legal and not cheating. It saves cable and expense when wiring a house.
He is correct that both of them must be moved.
I would not be following your neighbour's directions.
Yeah I agree with not listening to the neighbor.

As a side note...is there ANY WAY to split out these circuits...without rewiring the whole house ?
__________________
toofast is offline  
 
Reply With Quote Quick reply to this message
Old 08-28-2013, 03:42 PM  
kok328
Supporting Member
HRT_SUPPORTER.png
 
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,195
Liked 109 Times on 95 Posts
Likes Given: 64

Default

It is my understanding that in order to utilize a MWBC you have to share the neutral between the two phases of hot.

__________________
kok328 is offline  
 
Reply With Quote Quick reply to this message
Old 08-28-2013, 05:48 PM  
JoeD
Contractor
 
Join Date: Mar 2006
Location: Welland, Ontario
Posts: 966
Liked 102 Times on 84 Posts
Likes Given: 4

Default

The only way to separate them is replace the 12/3 line from the panel to the point where it separates into two circuits With two separate 12/2 cables. The new cables do not need to follow the same route as the 12/3, as long as you get them from the panel the separation point. The old 12/3 can be abandoned in the wall.

EDIT.
Actually you only need one 12/2 cable. The 12/3 can remain as one of the circuits with one of the hots simply being left unused.

__________________
JoeD is offline  
 
Reply With Quote Quick reply to this message
Old 08-29-2013, 05:52 AM  
bud16415
Fixer Upper
 
bud16415's Avatar
 
Join Date: Feb 2013
Location: Erie Pa, Pa
Posts: 1,227
Liked 352 Times on 282 Posts
Likes Given: 115

Default

I don’t know much about backup generators but have a few questions based around what the OP said he had.

If he has a generator capable of (10) 20 amp circuits the unit then should be large enough to power his whole house assuming he has a 200 amp service. Why would they isolate the power of individual circuits in this manner rather than one large switch that isolates the whole house?

I understand the rational of doing that with a small unit sized to supply only emergency needs heat, water pump, fridge, and a few lights etc. Around here many people have a small gasoline unit sitting in the garage and will hook up some extension cords even if needed in the winter to keep the necessities going, and others have whole house natural gas rig outside with automatic transfer. I assumed the big units took the house off line and then fired up replacing the power.

__________________
bud16415 is offline  
 
Reply With Quote Quick reply to this message
Old 08-29-2013, 06:55 AM  
JoeD
Contractor
 
Join Date: Mar 2006
Location: Welland, Ontario
Posts: 966
Liked 102 Times on 84 Posts
Likes Given: 4

Default

20 circuits does not mean it is large enough to support the whole house.
Also a 200 amp whole house transfer switch is much more expensive.

__________________
JoeD is offline  
 
Reply With Quote Quick reply to this message
Old 08-29-2013, 10:11 AM  
toofast
Member
 
Join Date: Feb 2011
Location: columbia station, OH
Posts: 36
Default

Correct...my main panel has 42 20 amp breakers. My Genny (if I ever get it going) will power most of the critical circuits but not all.

Keep in mind (although I am no expert) the total amps of the breakers installed nearly always exceed the service as these are not directly related. Although it seems like it should be. Perhaps an expert will explain this better.

As for my problem...I think I will try to FIX the circuits that I can get to - without tearing into the walls. Hopefully it will give me enough to power the critical areas.

__________________
toofast is offline  
 
Reply With Quote Quick reply to this message
Old 08-29-2013, 11:09 AM  
bud16415
Fixer Upper
 
bud16415's Avatar
 
Join Date: Feb 2013
Location: Erie Pa, Pa
Posts: 1,227
Liked 352 Times on 282 Posts
Likes Given: 115

Default

How big is your gen, KVA rating?

A auto disconnect for a whole 200 amp house is about $700 and a manual one is about $350 so ya pretty pricy.

The reason the sum of the parts is greater than the whole I believe is that’s a max rating. No one would ever have every circuit maxed out at the same time. That’s kind of what your neighbor was suggesting. You said one of the items was your gas water heater? How much current could that draw?

Do you have a well and pump? That would and should be a dedicated line now what other combinations and items do you want to break out?

If you do like JoeD said and use the 12 / 3 as a 12 / 2 for the lighting then it might not be as hard to run a new wire to your water heater. Other things might just work out the same.



__________________
bud16415 is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
natural gas-powered generator inside home? ilyaz Electrical and Wiring 8 04-05-2013 02:17 PM
Wiring a furnace for a generator..... doechsli Electrical and Wiring 3 12-24-2012 12:49 AM
I need to know how to install a wireless home security alarm. donaldjerry Electrical and Wiring 3 11-17-2010 10:14 AM
Wiring my home for Cable (Dish) & Cat 5 cheesefood Electrical and Wiring 9 01-28-2008 07:49 PM
Unique Business? MTCquality Roofing and Siding 5 07-28-2006 08:13 PM