10-14-2012, 04:36 PM
|
|
|
Junior Member
Join Date: Oct 2012
Posts: 4
|
GFI outdoor outlet won't reset
Hi there,
I have a GFI outdoor outlet on my deck that won't reset. Push the button, it pops right back out. I have also reset the dedicated circuit breaker for this outlet several times but it doesn't fix it, the outlet still won't reset. Any idea how I can troubleshoot this? This is a brand new home with new everything. All other exterior GFI outlets reset normally (usually needs to be done after it rains). This one also used to work fine but suddenly stopped.
Thanks.
|
|
|
10-14-2012, 05:10 PM
|
|
|
Obnoxious Knowitalll
Join Date: Sep 2012
Posts: 249
Liked 24 Times on 23 Posts Likes Given: 12
|
if a GFI won't reset it usually means you have a ground fault.
I especially don't like the "(usually needs to be done after it rains)" part. You have a major problem somewhere.
If you have to ask for advice on trouble shooting it may be beyond your experience level and could be quite dangerous. The simplest check would be to replace the GFI with a new one, making sure and doubly sure that the breaker for that outlet is off. You need to check the leads to outlet since outlet itself is off.
Some of the tests are going to be in main breaker box, and some with power on, so without knowing your experience, I can't make any suggestions.
I repeat that the need to reset GFI's after rain is extremly troubling, and indicates problems that add to danger in trouble shooting.
__________________
[CENTER][FONT=Comic Sans MS]Measure twice, cut once.[/FONT][/CENTER]
[CENTER][FONT=Comic Sans MS]Look at the nail, not the hammer. Watch the fence, not the blade.[/FONT][/CENTER]
[CENTER][FONT=Comic Sans MS]If you hook your thumb over your belt you won't hit it with the hammer or leave it layin on the saw table.[/FONT][/CENTER]
|
|
|
10-14-2012, 05:15 PM
|
|
|
Senior Member
Join Date: Jan 2010
Posts: 1,429
Liked 57 Times on 53 Posts Likes Given: 31
|
You can check the insulation resistance of your wet cabling up to several hundred megohms with almost any DVM and one or more 9v batteries.
You're looking for 20 to 100 Kilo-ohms between the hot lead and the ground lead of the cable downstream of the GFCI if this is the reason your GFCI is tripping.
No cable downstream? Sometimes no power or incorrect wiring to the GFCI has it refusing to stay latched.
It is insensitive to leaky cables upstream of it.
Last edited by Wuzzat?; 10-14-2012 at 06:24 PM.
|
|
|
10-15-2012, 06:38 AM
|
|
|
Senior Member
Join Date: Mar 2006
Location: Welland, Ontario
Posts: 724
Liked 33 Times on 29 Posts
|
Turn off the breaker for this receptacle and remove and inspect it. I have seen them full off bugs. Even if they are dead a bit of water will be enough to cause the GFCI to trip.
|
|
|
10-15-2012, 08:42 AM
|
|
|
Obnoxious Knowitalll
Join Date: Sep 2012
Posts: 249
Liked 24 Times on 23 Posts Likes Given: 12
|
With breakers off swap the non-resetting GFI with one that is working on another circuit. If the swap resets, and first one does not work in new spot the original GFI is bad . If both now work original was improperly wired.
If original works in new spot but swap out does not, there is wiring problem in that circuit.
Once you get that GFI sorted out, find out why rain trips them. They or other outdoor outlets on circuits may not be protected from rain, they should all be in outdoor rated boxes with covers on unused outlets. They may just be too close to ground level, getting splashed on or receiving direct rain fall. If there is something you leave permanently plugged in, consider hardwiring it inside a weather proof box.
__________________
[CENTER][FONT=Comic Sans MS]Measure twice, cut once.[/FONT][/CENTER]
[CENTER][FONT=Comic Sans MS]Look at the nail, not the hammer. Watch the fence, not the blade.[/FONT][/CENTER]
[CENTER][FONT=Comic Sans MS]If you hook your thumb over your belt you won't hit it with the hammer or leave it layin on the saw table.[/FONT][/CENTER]
|
|
|
10-15-2012, 08:57 AM
|
|
|
Senior Member
Join Date: Jan 2010
Posts: 1,429
Liked 57 Times on 53 Posts Likes Given: 31
|
Yes, there should be a gasket in the box that keeps out rain. Maybe it was left out of this one box.
And with notmrjohn's swap method you don't have to gamble $15 for a new GFCI.
|
|
|
10-17-2012, 07:20 AM
|
|
|
Junior Member
Join Date: Mar 2010
Posts: 26
Liked 2 Times on 2 Posts
|
If you still have the issue, turn the breaker off, disconnect the LOAD wires if they are present, these wires lead to any downstream connections. Turn power back on and try to reset the GFIC. If it resets the problem is not the GFIC normally (95%). The problem is with the circuit downstream (LOAD). If you have no LOAD wires connected and just the wires to the LINE you have a bad GFIC.
|
|
|
10-17-2012, 09:42 AM
|
|
|
Junior Member
Join Date: Oct 2012
Posts: 4
|
Excellent, thanks so much for your responses!
|
|
|
10-23-2012, 05:20 AM
|
|
|
Junior Member
Join Date: Sep 2012
Posts: 2
|
I've had this problem before, new houses go up very quickly these days. Go into your service panel and check all your grounds and neutrals are all TIGHT! , good time to even check all wire to each breaker. GFCI will not work without a gnd.
|
|
|
10-23-2012, 08:50 AM
|
|
|
Senior Member
Join Date: Nov 2010
Location: vancouver, b.c.
Posts: 4,770
Liked 214 Times on 200 Posts Likes Given: 328
|
Bjstottler: Hey welcome to the site. GFCI do work with out ground.
|
|
|
| Thread Tools |
Search this Thread |
|
|
|
| Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
|
|