DIY Home Improvement, Remodeling & Repair Forum > DIY Home Improvement > Electrical and Wiring > Grounding the House




Reply
 
LinkBack Thread Tools Search this Thread Display Modes
Old 01-26-2011, 08:13 AM  
bigdave101
Junior Member
 
Join Date: Jan 2011
Location: Milan, Mi
Posts: 1
Default Grounding the House

I also have switched my copper piping to cpvc piping.
The #4 copper wire was attached to a copper pipe and now obviously cannot be attached to the cpvc... my question is can I run this braided copper to an outside ground rod and call it a day? Or is there more???



__________________
bigdave101 is offline  
 
Reply With Quote Quick reply to this message
Old 01-27-2011, 06:29 AM  
joecaption
Senior Member
 
Join Date: Jan 2011
Location: Hartfield VA, VA
Posts: 1,361
Liked 37 Times on 32 Posts
Likes Given: 2

Default

Grounding needs to be done way back at the main incoming power panel.
Grounding to pipes has not been legal for many many years.
And since no one here can see what you have and it would be a real danger to anyone living in this house with out a proper ground I'd suggest you call a real electrician.



__________________
joecaption is offline  
 
Reply With Quote Quick reply to this message
Old 01-28-2011, 05:23 AM  
ajaynejr
Junior Member
 
Join Date: Jan 2011
Location: Nashua, NH
Posts: 6
Default

Drive two ground rods at least six feet apart. (In some cases, where the ground conductivity is really good, one will suffice.)

The grounding electrode system of a house starts with this:
1. The panel ground terminal strip (ground bus)
2. A grounding electrode which may be either the main cold water pipe provided it is metal and is buried outside for at least 10 feet, or two ground rods,
3. A #6* copper wire running non-stop between the above two items.

If the main water feed entering the house has been replaced by plastic, you need to have ground rods for an alternate grounding electrode.

If you started out with ground rods, the metal parts of the plumbing system in the basement must be bonded to the grounding electrode system using #6* copper wires as needed. Using clamps, put a #6 jumper wire across the water meter inlet and outlet and across the water heater (cold) inlet and (hot) outlet.

If you have additional ground rods, say for cable TV, these must be tied (bonded) to the above. A ground rod in a detached garage or other building is bonded using the ground wire in the power feed over from the main house. Exception: No bonding needed where the wiring to the main house was grandfathered to not need a ground wire back to the house.

If A is bonded to B and B is bonded to C then A is bonded to C. So if a metal water pipe going upstairs is jumpered using a wire past a plastic section of pipe and clamped to the wire in part 3 above then that metal pipe is bonded to the panel ground.

Metal plumbing upstairs electrically isolated because of plastic pipe sections should be bonded using jumper wires more or less following the pipes down to the basement. These wires should be at least the size of the largest branch circuit wiring passing near the respective pipes (typically #12). Clamp the other end to a pipe that is bonded or to somewhere on the grounding electrode system described above.

Gas piping must be bonded to the grounding electrode system also. But if you have a gas appliance with electrical components, then the ground wire in the cable or conduit feeding that appliance and going back to the panel is a good enough bonding.

* The connection to the entering water pipe (if metal) must be within 5 feet of where it enters and before the water meter. For services greater than 100 amps those bonding wire(s) between the entering water pipe and the panel need to be #4 copper.

__________________

Last edited by ajaynejr; 01-28-2011 at 06:05 AM.
ajaynejr is offline  
 
Reply With Quote Quick reply to this message
Old 02-04-2011, 02:37 AM  
frozenstar
Senior Member
 
Join Date: Dec 2009
Posts: 253
Default

That was a very nice and detailed response ajaynejr...

__________________

[I]“You can always get someone to love you, even if you have to [B]do it yourself[/B]”[/I]
[I][SIZE="1"][/URL][/SIZE][/I]

frozenstar is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Circuit Panel Grounding Question jimmy4 Electrical and Wiring 4 06-01-2011 11:16 PM
Grounding Outlets to Conduit ISUzj Electrical and Wiring 7 10-19-2010 08:50 AM
grounding breaker panel fuzzman Electrical and Wiring 6 06-26-2010 07:10 PM
Grounding new service entrance Dan K Electrical and Wiring 3 10-17-2009 03:36 AM
Grounding Garage Imacarguytoo Electrical and Wiring 2 10-20-2008 07:38 PM