Old 03-26-2014, 12:45 PM  
plaza
Junior Member
 
Join Date: Mar 2014
Posts: 3
Likes Given: 3

Default Half of the lights are out downstairs

I woke up this morning and turned on the kitchen light and the living room lamp flickered and the power went out. It has since flickered a couple of times. Its only to the living room, dining room lights and the kitchen. It seems to be only on the one circuit
I reset the breakers and the main breaker and also any of the outlets that had the button.
I called an electrician and he said its very common for the outlets in our area to not be grounded and walked me through how to check them and ground them. He referred to the outlets as being push outlets and to put the grounding under all the screws. All the outlets are already grounded. The Hardware store sold me a outlet detector to tell me if its bad but since there is no power to any of them its hard to check.
Is there something else I can try before I call him back?



__________________
plaza is offline  
 
Reply With Quote Quick reply to this message
Old 03-26-2014, 01:11 PM  
JoeD
Contractor
 
Join Date: Mar 2006
Location: Welland, Ontario
Posts: 948
Liked 100 Times on 82 Posts
Likes Given: 2

Default

Sounds like a loose connection. Your problem will be finding it.
Are there only lights on the circuit or are there also receptacles? Is everything on the circuit out or only part of the items?



__________________
JoeD is offline  
plaza Likes This 
Reply With Quote Quick reply to this message
Old 03-26-2014, 01:16 PM  
plaza
Junior Member
 
Join Date: Mar 2014
Posts: 3
Likes Given: 3

Default

Quote:
Originally Posted by JoeD View Post
Sounds like a loose connection. Your problem will be finding it.
Are there only lights on the circuit or are there also receptacles? Is everything on the circuit out or only part of the items?
Well as far as I can tell its the outlets in the living room and the lights in the other rooms. Im pretty sure its the whole circuit but Im not sure what exactly is all on that circuit or even how to find out whats all on that circuit. Its four outlets total that are out
__________________
plaza is offline  
 
Reply With Quote Quick reply to this message
Old 03-26-2014, 02:01 PM  
Wuzzat?
Banned
 
Join Date: Jan 2010
Posts: 2,328
Liked 167 Times on 154 Posts
Likes Given: 94

Default

Quote:
Originally Posted by plaza View Post
the living room lamp flickered
So it may be an intermittently high resistance connection rather than a permanent open circuit. Could be a loose screw, a backstabbed outlet or a bad Wirenut.

With all of the breakers off and using an extension cord as one of the meter test leads, you may measure some resistance, more than 1/4 ohm, between the short slots on one of the bad outlets and the output terminal of one breaker.
This is the breaker that serves these outlets.

With the other breakers on, turning this breaker on and off may show what else is on this branch.
The farthest box may have only one cable coming into it whereas the others may have an entering cable and an exiting cable.
Try to figure out how this branch is laid out in your walls, from farthest to nearest. Then the bad connection will be between the last good outlet and the first dead one.

Post back how this works out.
I've never had to do this, but
in principle, on paper and in my head
it works great!
__________________

Last edited by Wuzzat?; 03-26-2014 at 02:06 PM.
Wuzzat? is offline  
plaza Likes This 
Reply With Quote Quick reply to this message
Old 03-26-2014, 02:52 PM  
kok328
Supporting Member
HRT_SUPPORTER.png
 
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,181
Liked 104 Times on 91 Posts
Likes Given: 61

Default

Start with non-working outlets and light switches.
Remove them from the junction box and look for loose or disconnected connections.
What your electrician is telling you that the outlets could be the "push" connection style where they are known for either the solid core copper breaking or the stab in coming out. If you have these, reattach them using the lugs on the side of the outlet instead of the stab in holes on the back (likewise for the light switches).

__________________
kok328 is offline  
plaza Likes This 
Reply With Quote Quick reply to this message
Old 03-26-2014, 03:47 PM  
plaza
Junior Member
 
Join Date: Mar 2014
Posts: 3
Likes Given: 3

Default

Quote:
Originally Posted by Wuzzat? View Post
So it may be an intermittently high resistance connection rather than a permanent open circuit. Could be a loose screw, a backstabbed outlet or a bad Wirenut.

With all of the breakers off and using an extension cord as one of the meter test leads, you may measure some resistance, more than 1/4 ohm, between the short slots on one of the bad outlets and the output terminal of one breaker.
This is the breaker that serves these outlets.

With the other breakers on, turning this breaker on and off may show what else is on this branch.
The farthest box may have only one cable coming into it whereas the others may have an entering cable and an exiting cable.
Try to figure out how this branch is laid out in your walls, from farthest to nearest. Then the bad connection will be between the last good outlet and the first dead one.

Post back how this works out.
I've never had to do this, but
in principle, on paper and in my head
it works great!
I understood most of what you said up to here... "With all of the breakers off and using an extension cord as one of the meter test leads, you may measure some resistance, more than 1/4 ohm, between the short slots on one of the bad outlets and the output terminal of one breaker.
This is the breaker that serves these outlets."
Can you dumb it down for me lol
__________________
plaza is offline  
 
Reply With Quote Quick reply to this message
Old 03-26-2014, 04:00 PM  
kok328
Supporting Member
HRT_SUPPORTER.png
 
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,181
Liked 104 Times on 91 Posts
Likes Given: 61

Default

You are checking for continuity between the hot side of the outlet and the breaker (using an extension cord to reach to the panel) in the panel to indicate if this outlet is on that particular breaker. You can automatically rule out any breaker over 20amps and any 2-pole breakers. If you find an outlet that doesn't go to any breaker then there is a break in that circuit somewhere. Again, start behind the outlets and/or switches for loose or broken wires. Sometimes solid core can break under the insulation within a few inches of the connection.
P.S.- Dumb is my specialty!



__________________
kok328 is offline  
2
People Like This 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Floor squeaks between upstairs and finished downstairs. nospmahm Flooring 5 07-21-2011 11:24 AM
Half Work Half Dont.....going nuts! guz168 Electrical and Wiring 4 10-14-2009 07:38 PM
Half Work Half Dont guz168 Electrical and Wiring 3 09-01-2009 07:13 AM
Toilet only half flushes theboomboomcars General Home Improvement Discussion 6 07-15-2008 06:16 PM
Half Wall Mary Jo Flooring 4 04-04-2007 12:42 PM