Default Main to sub (main lug) panel wiring

I have a full 100 AMP main, installed a main lug fed by a 60AMP breaker on the main. Between the main and main lug I have NM 6-3 WG copper. I did not use conduit or an offset conduit, but rather 1" DIA. clamps and less than 6" length of NM 6-3 between the main and main lug. The gound wire on the 6-3 is not 6 gauge wiring of course, and I was wondering if there are NEC guidelines on appropriate gauging for the ground. There of course might be local specific codes, but I was first going to see what guidance people on this board might suggest.

I can either use the ground in the 6-3 to ground the main lug to the main panel, or optionally add a larger gauge ground dedicated between the main lug and the main. Any suggestions? Also, if I use a larger gauge ground between the two panels, should I bust a new pair of holes claimp too? I doubt it makes sense to go through the 1" dia clamps where the 6-3 NM is.

Finally, my neutral of the 6-3 doesn't fit in any of the open screw terminals on the main panel bus, and was wondering if there is a way to appropriately get it to fit. Ideas, in no particular order, include:
a. reduce the strands of the 6 gauge neutral (from the 6-3) until it fits into the terminal
b. find and buy some sort of adapter (if they exist) to accomodate the larger size
c. branch the 6 gauge neutral into two strands and fit each strand into adjacent open terminals on the neutral bus of the main panel.

I am guessing that option B is the best, if not most appropriate solution.

Your thoughts and suggestions are appreciated.



__________________
newdiyer is offline  
 
Reply With Quote Quick reply to this message
Old 03-22-2007, 10:16 AM  
newdiyer
Junior Member
 
Join Date: Mar 2007
Posts: 7
Default

Quote:
Originally Posted by newdiyer View Post
I have a full 100 AMP main, installed a main lug fed by a 60AMP breaker on the main. Between the main and main lug I have NM 6-3 WG copper. I did not use conduit or an offset conduit, but rather 1" DIA. clamps and less than 6" length of NM 6-3 between the main and main lug. The gound wire on the 6-3 is not 6 gauge wiring of course, and I was wondering if there are NEC guidelines on appropriate gauging for the ground. There of course might be local specific codes, but I was first going to see what guidance people on this board might suggest.

I can either use the ground in the 6-3 to ground the main lug to the main panel, or optionally add a larger gauge ground dedicated between the main lug and the main. Any suggestions? Also, if I use a larger gauge ground between the two panels, should I bust a new pair of holes claimp too? I doubt it makes sense to go through the 1" dia clamps where the 6-3 NM is.

Finally, my neutral of the 6-3 doesn't fit in any of the open screw terminals on the main panel bus, and was wondering if there is a way to appropriately get it to fit. Ideas, in no particular order, include:
a. reduce the strands of the 6 gauge neutral (from the 6-3) until it fits into the terminal
b. find and buy some sort of adapter (if they exist) to accomodate the larger size
c. branch the 6 gauge neutral into two strands and fit each strand into adjacent open terminals on the neutral bus of the main panel.

I am guessing that option B is the best, if not most appropriate solution.

Your thoughts and suggestions are appreciated.
I figured out the answer to the second question (answer = B), but I still have some questions about the first question in terms of ground wire gauge.

Thanks in advance.


__________________
newdiyer is offline  
 
Reply With Quote Quick reply to this message
Old 03-22-2007, 04:14 PM  
petey_racer
Licensed Electrician
 
Join Date: May 2006
Posts: 105
Default

DEFINITELY asnwer B.

As to the ground size. The cable is a factory made assembly. They would not use a ground smaller than would be code required.
A #10 ground is adequate for anything you would use #6 circuit conductors for.
If you want to look it up see NEC Table 250.122

__________________

Please post back and let us know how it turns out....

petey_racer is offline  
 
Reply With Quote Quick reply to this message
Old 03-29-2007, 08:22 PM  
AndyD5
The Cable Guy
 
Join Date: Mar 2007
Posts: 48
Send a message via Yahoo to AndyD5
Default

I agree to Answer B and for the size of ground must be equal or greater to that which you are grounding. if you use a 2/10AUG romex it should have a 10 guage ground wire in the middle my A/C unit has a heavy guage wire all wires to it are in the same romex covering one black one red one white and one green

__________________

-Andy the cable guy

I love to work on my house would love to help you with yours!

AndyD5 is offline  
 
Reply With Quote Quick reply to this message
Old 03-29-2007, 08:43 PM  
Square Eye
Senior Member
 
Square Eye's Avatar
 
Join Date: Jan 2006
Posts: 1,273
Liked 4 Times on 4 Posts

Default

Andy, buy an NEC code book.
The table that Petey Racer is talking about clearly shows that a smaller gorund wire is sufficient.

__________________

[URL="http://www.houserepairtalk.com/announcement.php?f=39&a=6"][size=3]The Ten Commandments of House Repair Talk[/size][/URL]



[URL="http://home.bellsouth.net/p/s/community.dll?ep=16&groupid=289528&ck="]Square Eye's home page[/URL]

Square Eye is offline  
 
Reply With Quote Quick reply to this message
Old 03-29-2007, 09:03 PM  
AndyD5
The Cable Guy
 
Join Date: Mar 2007
Posts: 48
Send a message via Yahoo to AndyD5
Default

Quote:
Originally Posted by Square Eye View Post
Andy, buy an NEC code book.
The table that Petey Racer is talking about clearly shows that a smaller gorund wire is sufficient.
I just go with what I was taught and what makes sence too much protection is better than not enough. It may not be required but it surely doesn't hurt anything either. So I'm over cautious!
__________________

-Andy the cable guy

I love to work on my house would love to help you with yours!

AndyD5 is offline  
 
Reply With Quote Quick reply to this message
Old 03-30-2007, 07:03 PM  
petey_racer
Licensed Electrician
 
Join Date: May 2006
Posts: 105
Default

Quote:
Originally Posted by AndyD5 View Post
I just go with what I was taught and what makes sence too much protection is better than not enough. It may not be required but it surely doesn't hurt anything either. So I'm over cautious!
That is absolutely the wrong attitude to have when it comes to electrical work.
What makes "sense" and what may seem over cautious sometimes can be counterproductive.

Square is correct. GET A CODE BOOK. Know it. Then come back and give advice.

It is not a wise man who gives advice on such things merely according to "what he was taught" or "what I've always learned".

This is how misconceptions and incorrect practices get perpetuated.


You are correct. A circuit run with #10 should have a #10 ground. Same with #12 & #14. Larger than that is DIFFERENT.
See NEC Table 250.122 and get back to us.


__________________

Please post back and let us know how it turns out....

petey_racer is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
do 150 amp service panel exist? turfgrass Electrical and Wiring 10 07-23-2011 07:36 AM
Panel or subpanel rjarrett001 Electrical and Wiring 5 02-14-2008 05:22 PM
Service panel connection. Hack Electrical and Wiring 16 01-02-2008 10:34 AM
advice about new wiring for heaters jetjaguar Electrical and Wiring 6 01-14-2007 11:36 AM
Service/breaker panel capacity question... tenderton Electrical and Wiring 1 10-13-2006 05:08 AM