The length of wire needed to wire my cooktop is approx. 20 feet. I have 2 questions:
1.) What size wire should I use ? 2.) What size (amps) circuit breaker should I use ? Thanks again. John from NC |
Need to know how many amps the cook top requires. Would be stated on an information plate on the cook top.
|
It is a new Frigidaire unit and the only specs I found on it were as follows: "All electric cooktops run off a single phase, 3-wire or 4-wire cable, 240/208volt, 60 hertz, AC only electrical supply with ground."
|
There will be a wattage or kW rating somewhere. Typically there is a sticker or plate right on the unit.
Without that we cannot give an answer. :help: |
208 - 5.0 kW
240 - 6.7 kW Hope this helps. Thanks again. |
A 30A circuit would be legal, but a 40A circuit would afford some cushion and allow for a larger unit to be installed in the future.
A 30A circuit would require #10cu or #8al A 40A circuit would require #8cu or #6al (possibly #8al depending on installation/application and code cycle followed). Do the instructions mention a "4-wire" feed, or anything about requiring a neutral? |
The instructions include wiring illustrations for both 3-wire and 4-wire installation.
|
In the 4-wire illustration, the white feed wire is capped.
|
OK, so this is a straight 240v appliance. The 4-wire illustration is only there for installations where this unit is replacing a unit with a 4-wire feed.
For your new circuit you would use 10/2 or 8/2 cable. IMO for what you are installing 10/2 is fine. Especially considering the short distance and that this is brand new unit. Any future upgrade, while unlikely any time soon, will not be very hard. |
Thank you Speedy Petey !
|