DIY Home Improvement, Remodeling & Repair Forum

DIY Home Improvement, Remodeling & Repair Forum (http://www.houserepairtalk.com/forum.php)
-   Electrical and Wiring (http://www.houserepairtalk.com/f9/)
-   -   More wiring questions ! (http://www.houserepairtalk.com/f9/more-wiring-questions-8359/)

tiorunder 01-10-2010 11:08 AM

More wiring questions !
 
The length of wire needed to wire my cooktop is approx. 20 feet. I have 2 questions:

1.) What size wire should I use ?
2.) What size (amps) circuit breaker should I use ?

Thanks again.

John from NC

Blue Jay 01-10-2010 11:13 AM

Need to know how many amps the cook top requires. Would be stated on an information plate on the cook top.

tiorunder 01-10-2010 11:23 AM

It is a new Frigidaire unit and the only specs I found on it were as follows: "All electric cooktops run off a single phase, 3-wire or 4-wire cable, 240/208volt, 60 hertz, AC only electrical supply with ground."

speedy petey 01-10-2010 02:21 PM

There will be a wattage or kW rating somewhere. Typically there is a sticker or plate right on the unit.

Without that we cannot give an answer. :help:

tiorunder 01-10-2010 02:55 PM

208 - 5.0 kW
240 - 6.7 kW

Hope this helps. Thanks again.

speedy petey 01-10-2010 04:36 PM

A 30A circuit would be legal, but a 40A circuit would afford some cushion and allow for a larger unit to be installed in the future.

A 30A circuit would require #10cu or #8al
A 40A circuit would require #8cu or #6al (possibly #8al depending on installation/application and code cycle followed).

Do the instructions mention a "4-wire" feed, or anything about requiring a neutral?

tiorunder 01-10-2010 08:31 PM

The instructions include wiring illustrations for both 3-wire and 4-wire installation.

tiorunder 01-10-2010 08:32 PM

In the 4-wire illustration, the white feed wire is capped.

speedy petey 01-11-2010 05:08 AM

OK, so this is a straight 240v appliance. The 4-wire illustration is only there for installations where this unit is replacing a unit with a 4-wire feed.

For your new circuit you would use 10/2 or 8/2 cable. IMO for what you are installing 10/2 is fine. Especially considering the short distance and that this is brand new unit. Any future upgrade, while unlikely any time soon, will not be very hard.

tiorunder 01-11-2010 05:50 AM

Thank you Speedy Petey !


All times are GMT -6. The time now is 11:55 AM.