Old 05-16-2014, 07:55 AM  
nealtw
Contractor
 
Join Date: Nov 2010
Location: vancouver, b.c.
Posts: 10,277
Liked 850 Times on 759 Posts
Likes Given: 1466

Default

So you have a loose connection that is connected until it warms up. Have you got pigtails in the boxes or are all the wires just stabbed into the back of the outlets?



__________________
nealtw is offline  
 
Reply With Quote Quick reply to this message
Old 05-16-2014, 07:58 AM  
JoeD
Contractor
 
Join Date: Mar 2006
Location: Welland, Ontario
Posts: 968
Liked 102 Times on 84 Posts
Likes Given: 4

Default

While you were in there did you torque the other whites? If one is loose others could be.



__________________
JoeD is offline  
 
Reply With Quote Quick reply to this message
Old 05-16-2014, 08:53 AM  
Joeb1983
Junior Member
 
Join Date: May 2014
Posts: 5
Liked 1 Times on 1 Posts

Default

^ Yes sir, " I did just that and tighten ALL my neutrals. To my surpise a few needed tightning."

^ " I replaced all the wall plates when I first bought the home and I do have the screw down connections and NOT the push-lock style." So, all my outlets and switches are the hook/pig tail, screw down type.

The problem was at my breaker panel itself in the garage. On each side of the inside of my panel there are neutral/grounding block terminal strips for all my homes circuits. (insert wire in the terminal block then screw down fastner) The neutral wire from that particular circuit was loose in that block causing the failure in that circuit.

__________________

Last edited by Joeb1983; 05-16-2014 at 09:26 AM.
Joeb1983 is offline  
 
Reply With Quote Quick reply to this message
Old 05-16-2014, 04:05 PM  
nealtw
Contractor
 
Join Date: Nov 2010
Location: vancouver, b.c.
Posts: 10,277
Liked 850 Times on 759 Posts
Likes Given: 1466

Default

Sounds good. Oldog will send you a case of beer.

__________________
nealtw is offline  
 
Reply With Quote Quick reply to this message
Old 05-16-2014, 04:54 PM  
Wuzzat?
Banned
 
Join Date: Jan 2010
Posts: 2,328
Liked 167 Times on 154 Posts
Likes Given: 94

Default

Quote:
Originally Posted by Joeb1983 View Post
burnt up about 3" back from the tip. I was able to simply/easily pull it out of the block.
High contact resistance connection due to low contact pressure. Five watts may not be enough to heat up the neutral busbar at your connection but you could have had 10x this much power, up to maybe 300w.
__________________

Last edited by Wuzzat?; 05-16-2014 at 04:57 PM.
Wuzzat? is offline  
 
Reply With Quote Quick reply to this message
Old 05-16-2014, 06:46 PM  
CallMeVilla
Contractor
 
CallMeVilla's Avatar
 
Join Date: Feb 2010
Location: San Diego
Posts: 1,277
Liked 394 Times on 307 Posts
Likes Given: 161

Default

Quote:
Originally Posted by Joeb1983 View Post
I heard the 60hz is a "slow pulse" and actually induces and slight vibration that over time will do exactly what happened... The house was built in 03. I know hospitals have a time complience/preventitive maintenance schedule to tighten them down ever so often. I did just that and tighten ALL my neutrals. To my surprise a few needed tightening!


This is an excellent practice ... Don't have to kill it by over-tightening, but firm retightening is a great preventative. Nicely done!
__________________
CallMeVilla is offline  
 
Reply With Quote Quick reply to this message
Old 05-26-2014, 10:38 AM  
WyrTwister
Junior Member
 
Join Date: May 2014
Posts: 14
Liked 4 Times on 3 Posts

Default

You are very luck to have found the problem in the loadcenter . Many time , you have to spend a lot of time and effort searching for the defect . :-(

Since you do not usually know the rout the Romex takes from the loadcenter , to device , to device , to device .....

As I think someone stated , it is often in the last non-dead receptacle . Another problem , a home owner often forgets where all the receptacles are . And it ends up being behind the heaviest piece of furniture in the house . :-(

More often than not , it is in a receptacle , than in a switch box or lighting box . Since receptacles often carry heavier current loads .

Good job !

God bless
Wyr

__________________
WyrTwister is offline  
slownsteady Likes This 
Reply With Quote Quick reply to this message
Old 05-26-2014, 12:33 PM  
Wuzzat?
Banned
 
Join Date: Jan 2010
Posts: 2,328
Liked 167 Times on 154 Posts
Likes Given: 94

Default

Quote:
Originally Posted by WyrTwister View Post
Since receptacles often carry heavier current loads .
?
The current in a series circuit, i.e.,
-receptacle-switch-breaker-
is the same.

Still, these may fail at a higher rate for other reasons, probably mechanical wear.

BTW, IMHO, I think God damns more than He or She blesses.
__________________

Last edited by Wuzzat?; 05-26-2014 at 12:36 PM.
Wuzzat? is offline  
 
Reply With Quote Quick reply to this message
Old 05-26-2014, 12:55 PM  
slownsteady
Supporting Member
HRT_SUPPORTER.png
 
slownsteady's Avatar
 
Join Date: Jun 2009
Location: Newton, NJ
Posts: 1,117
Liked 151 Times on 129 Posts
Likes Given: 206

Default

Quote:
BTW, IMHO, I think God damns more than He or She blesses.
That's why we have to ask for the better choice
__________________
slownsteady is offline  
 
Reply With Quote Quick reply to this message
Old 05-26-2014, 02:06 PM  
Wuzzat?
Banned
 
Join Date: Jan 2010
Posts: 2,328
Liked 167 Times on 154 Posts
Likes Given: 94

Default

Quote:
Originally Posted by slownsteady View Post
That's why we have to ask for the better choice
What should we ask for for this bunch
http://en.wikipedia.org/wiki/Malignant_narcissism
which includes more than a few politicians?


__________________
Wuzzat? is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Garage door won't open all the way! dekor8r2008 Windows and Doors 35 07-14-2014 03:37 PM
What to do with open circuit gottodo1 Electrical and Wiring 8 02-13-2014 10:59 AM
Converting a staircase from open on 1 side, to open on 2 sides. frozensneaker Carpentry and Woodworking 5 11-17-2013 01:53 PM
Open Ground david542 Electrical and Wiring 12 03-07-2012 11:20 AM
i have an open ground.. mundo Electrical and Wiring 3 05-15-2011 07:35 AM