Default Outside GFCI Troubleshooting

I now realize that my outside circuit should have been GFCI protected all along. I didn't pay enough attention when some landscapers wired the outside lighting. I regret not watching them more closely now.

I replaced an outside 20 Amp breaker with a GFCI breaker. The breaker immediately tripped. Checked the outlets and turned out that a few were wired wrong. Corrected all of those "reversed" wires and still had the GFCI tripping.

The condition inside the non-waterproof boxes did not look good. I cleaned up the wires and replaced all the outlets with weatherproof outlets and boxes.
I replaced two switches with weatherproof boxes, also.

I have one outlet that is before two switches that control the rest of the outlets. One of the switches controls an outlet for a fountain (I am going to use that for an above ground pool pump) and the other switch controls the rest of the outlets for outside lightning.

The outlet before the switches works fine with the GFCI switch.
But when either switch is closed, the GFCI trips. Even after I disconnects all three wires to all of the outlets.

I replaced the regular breaker and all seems to work fine with my corrected outlets. Put in the GFCI and it trips right away if either switch is closed. I disconnected the Load Neutral and it still trips.

I assume that this means that I have a Power wire somewhere underground, past the switches, that is shorting against a Ground wire.

I am not looking forward to seeing what these guys did underground... Especially since it is under a large backyard of brick pavers.

If I am wrong in my trouble shooting or if there is something else I should look for, please let me know.

Thanks,
Duane



boldt_outside_20_amp_gfci.jpg  
__________________

Last edited by Duane_Boldt; 09-27-2011 at 03:45 PM. Reason: Added image showing circuit
Duane_Boldt is offline  
 
Reply With Quote Quick reply to this message
Old 09-27-2011, 04:38 PM  
kok328
Supporting Member
HRT_SUPPORTER.png
 
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,195
Liked 109 Times on 95 Posts
Likes Given: 64

Default

Remove the black & white wire from the outlets, one at a time working your way backwards from outlet #5 all the way back to point "A" until the breaker holds.
You will now know where the problem is troubleshooting going forward.
P.S.- Landscapers are now electricians ?



__________________
kok328 is offline  
 
Reply With Quote Quick reply to this message
Old 09-27-2011, 09:27 PM  
Duane_Boldt
Junior Member
 
Join Date: Sep 2011
Location: Tucson, AZ
Posts: 7
Default

I had actually removed all three of the connections for all the outlets back to point A and it still trips if either switch is closed.

__________________
Duane_Boldt is offline  
 
Reply With Quote Quick reply to this message
Old 09-27-2011, 09:35 PM  
Duane_Boldt
Junior Member
 
Join Date: Sep 2011
Location: Tucson, AZ
Posts: 7
Default

Also the outlets are wired in parallel not series. I assume even with this that GFCI would work fine unless there is a short to ground somewhere. Which by the test removing the Load Neutral at the GFCI breker would mean the Power line is shorted somewhere??

__________________
Duane_Boldt is offline  
 
Reply With Quote Quick reply to this message
Old 09-28-2011, 10:26 AM  
kok328
Supporting Member
HRT_SUPPORTER.png
 
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,195
Liked 109 Times on 95 Posts
Likes Given: 64

Default

If the "hot" was shorted to neutral or ground then the non-gfci breaker would trip also.

I'm starting to think that you have a bad gfci breaker.

OR

you have a wiring problem between (the breaker and outlet #1) or a wiring problem between (the breaker and point A).

To test: disconnect all 3 wires from outlet #1 and see what happens.
If the breaker trips then you have a problem with the wires going to outlet #1 or you have a bad gfci breaker.
If the breaker holds then reinstall outlet #1 and disconnect all 3 wires from the output side of Point A.
Basically what you need to do is disconnect and reconnect all wires from the switches and outlets working forward from the breaker and you will eventually get to a point where the breaker will not hold. Then you have found your problem.

__________________

Last edited by kok328; 09-28-2011 at 10:32 AM.
kok328 is offline  
 
Reply With Quote Quick reply to this message
Old 09-28-2011, 01:44 PM  
Duane_Boldt
Junior Member
 
Join Date: Sep 2011
Location: Tucson, AZ
Posts: 7
Default

If I disconnect at point A, it holds with switch #1 connected and with switch #1 disconnected. Once I connect the switches just past point A, it holds until eithwr one of them are closed.

__________________
Duane_Boldt is offline  
 
Reply With Quote Quick reply to this message
Old 09-28-2011, 01:50 PM  
Duane_Boldt
Junior Member
 
Join Date: Sep 2011
Location: Tucson, AZ
Posts: 7
Default

Is it likely that the new GFCI breaker is bad even though it seems to work fine until I get past point A?
Using a GFCI tester is outlet #1 it shows that it is wired correctly and breaks properly when the test button is pushed. It breaks just as the test button on teh GFCI breaker itself.
If the small short or arc out past the switches, can't that trip the GFCI breaker and not the standard breaker?
Also, is it better to have the outlets wired in series as opposed to parallel like they are now?

__________________
Duane_Boldt is offline  
 
Reply With Quote Quick reply to this message
Old 09-28-2011, 03:10 PM  
kok328
Supporting Member
HRT_SUPPORTER.png
 
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,195
Liked 109 Times on 95 Posts
Likes Given: 64

Default

Is it likely that the new GFCI breaker is bad even though it seems to work fine until I get past point A? not likely but possible
If the small short or arc out past the switches, can't that trip the GFCI breaker and not the standard breaker? I would expect either breaker to trip but, it does not appear to be the case.
Also, is it better to have the outlets wired in series as opposed to parallel like they are now? In this case, it does not make a difference
I would test for continuity between power and ground, power and neutral, and neutral and ground with the breaker turned off, the neutral disconnect from the breaker panel and both switches closed.
If continuity is detected between any of these combinations then you have a short somewhere.

__________________

Last edited by kok328; 09-28-2011 at 03:19 PM.
kok328 is offline  
 
Reply With Quote Quick reply to this message
Old 09-28-2011, 03:43 PM  
Blue Jay
Senior Member
 
Blue Jay's Avatar
 
Join Date: Jun 2008
Location: La Rue, Ohio
Posts: 250
Liked 10 Times on 10 Posts
Likes Given: 17

Default

Do you have an ohm meter? Sounds like you are ok to point A, meter each wire past switches to ground (both white and black). Should not have ANY reading on meter (at a high ohm setting). The line with the 4 outlets on it open ALL wires at the first outlet from the switch to test that section and then move on down the line. Any reading on any wire will trip the GF breaker

__________________
Blue Jay is offline  
 
Reply With Quote Quick reply to this message
Old 09-28-2011, 05:41 PM  
edh
Junior Member
 
edh's Avatar
 
Join Date: Oct 2010
Location: Calgary, AB
Posts: 9
Default

Or did the fellow who did your wiring actually install a GFCI somewhere or has your house been protected by a GFCI in the electrical box. If you try to wire two GFCI's on the same circuit I believe you may get the trouble you are having.



__________________
edh is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Troubleshooting Bathroom Painting Problems vahomes Painting Forum 0 08-13-2011 02:29 PM
GFI Troubleshooting Joshadog Electrical and Wiring 2 05-09-2011 06:42 AM
troubleshooting indoor receptacle wlearning Electrical and Wiring 8 04-08-2011 02:53 PM
Fluorescent troubleshooting Daffypuck Electrical and Wiring 6 09-14-2009 05:31 AM
GFI Tripping and troubleshooting jwar Electrical and Wiring 4 02-08-2008 09:14 AM