05-27-2011, 04:21 PM
|
|
|
Junior Member
Join Date: May 2011
Location: San Antonio, Tx
Posts: 3
|
Power Pole to House underground run
I have a new power pole on my 5 acre property. I need to run a 200Amp power from the pole to the house. The electrician used 4/0 aluminum from the breaker on the pole to the WIP on the top of the power pole. He stated I need the same to go from the Pole to the house underground. That is fine, however I would prefer a copper run. I have 300 Feet from Pole to my house. I know I need to run 3 cables in a special PVC pipe, however what size should I use? Doesn't 2/0 copper = 4/0 Aluminum? That is what the internet seems to show. I know I will have a little drop over that long a run.. What is the best run for this situation?
Thanks.
XM
|
|
|
05-27-2011, 07:38 PM
|
|
|
Senior Member
Join Date: Jan 2011
Location: Hartfield VA, VA
Posts: 1,329
Liked 27 Times on 24 Posts Likes Given: 2
|
And why is the power company not running that wire for you to the panel box?
|
|
|
05-28-2011, 06:22 AM
|
|
|
Lic.Electrical Contractor
Join Date: Mar 2006
Posts: 397
Liked 8 Times on 8 Posts Likes Given: 4
|
Quote:
Originally Posted by xmlaroux
I have a new power pole on my 5 acre property. I need to run a 200Amp power from the pole to the house. The electrician used 4/0 aluminum from the breaker on the pole to the WIP on the top of the power pole. He stated I need the same to go from the Pole to the house underground.
|
Thing is now you need 4-wire from the disconnect to the house. WHY did he install a break at the pole???
Quote:
Originally Posted by xmlaroux
I know I need to run 3 cables in a special PVC pipe, however what size should I use? Doesn't 2/0 copper = 4/0 Aluminum?
|
Yes, 2/0cu is proper for a 200A residential service, and it is not "special" PVC pipe. It is plain old electrical PVC. Schedule 40 underground and Sch80 anywhere exposed where it can be damaged.
|
|
|
05-28-2011, 06:23 AM
|
|
|
Lic.Electrical Contractor
Join Date: Mar 2006
Posts: 397
Liked 8 Times on 8 Posts Likes Given: 4
|
Quote:
Originally Posted by joecaption
And why is the power company not running that wire for you to the panel box?
|
Because in most places this is not done. The customer is responsible for the underground portion to the house.
In my area the customer is even responsible for underground primary.
|
|
|
05-28-2011, 06:50 AM
|
|
|
Junior Member
Join Date: May 2011
Location: San Antonio, Tx
Posts: 3
|
Thanks for the quick response. Yes, the power pile has my meter on it with the mainbreaker. I will need to use schedule 40(Electrical) underground. If I use 2/0 copper, will I lose too much amperage over 300 feet? And why 4 wire? Ground, nutral, and hot, what is the fourth for?
Thanks in advance.
|
|
|
05-28-2011, 10:16 AM
|
|
|
Member
Join Date: Mar 2010
Location: Bradenton, FL
Posts: 56
|
Quote:
Originally Posted by xmlaroux
If I use 2/0 copper, will I lose too much amperage over 300 feet?
|
Probably, you'll drop about 5%. Depends on your AHJ if this is legal or not.
Quote:
Originally Posted by xmlaroux
And why 4 wire? Ground, nutral, and hot, what is the fourth for?
|
With all due respect, are you sure this is project you want to tackle? There are two hots in a feeder. I don't know if you'd run a ground though, since you don't normally do so for a detached structure (each should have its own ground system at both boxes).
Matt
|
|
|
05-28-2011, 01:02 PM
|
|
|
Lic.Electrical Contractor
Join Date: Mar 2006
Posts: 397
Liked 8 Times on 8 Posts Likes Given: 4
|
Quote:
Originally Posted by gatorfan
Probably, you'll drop about 5%. Depends on your AHJ if this is legal or not.
|
This is the main power feeder. It follows different rules than a sub-feed or branch circuit.
Quote:
Originally Posted by gatorfan
With all due respect, are you sure this is project you want to tackle? There are two hots in a feeder.
|
I agree.
Quote:
Originally Posted by gatorfan
I don't know if you'd run a ground though, since you don't normally do so for a detached structure (each should have its own ground system at both boxes).
|
With all due respect, this is completely wrong.
A detached or separate structure USED to be able to dual-use the neutral also as a ground. For quite a few years now this allowance has been removed. A detached structure requires a separate ground and neutral run with a feeder, even a main power feeder.
A grounding electrode is required at any detached structure fed with more than one circuit.
A grounding electrode (system) has NOTHING to do with the equipment ground run with a feeder or circuit.
|
|
|
05-29-2011, 07:46 AM
|
|
|
Member
Join Date: Mar 2010
Location: Bradenton, FL
Posts: 56
|
Quote:
Originally Posted by speedy petey
This is the main power feeder. It follows different rules than a sub-feed or branch circuit.
|
True in the NEC, but some jurisdictions have more strict rules. In Florida (where I live) FBC 13-413.ABC.1.1 requires: "Feeder and customer-owned service conductors shall be sized for a maximum voltage drop of 2 percent at design load."
Quote:
Originally Posted by speedy petey
With all due respect, this is completely wrong.
A detached or separate structure USED to be able to dual-use the neutral also as a ground. For quite a few years now this allowance has been removed. A detached structure requires a separate ground and neutral run with a feeder, even a main power feeder.
A grounding electrode is required at any detached structure fed with more than one circuit.
A grounding electrode (system) has NOTHING to do with the equipment ground run with a feeder or circuit.
|
I stand very corrected. That's what I get for trying to answer without looking it up first. As an amateur, I've learned most of the residential portions of the code working on my own place, but this is one area I have obviously not gotten to yet.... Luckily I CYAed with the "I think"
Matt
|
|
|