Old 02-07-2008, 08:32 AM  
hoarea
Junior Member
 
Join Date: Jan 2008
Posts: 11
Default quick question

how many pulg-in can u have on one 15amp breaker with 14/2 wire?



__________________
hoarea is offline  
 
Reply With Quote Quick reply to this message
Old 02-07-2008, 08:50 AM  
guyod
Senior Member
 
Join Date: Jan 2008
Location: Wind Gap, PA
Posts: 423
Liked 21 Times on 20 Posts
Likes Given: 8

Default

It really as more to do with your electrical load than the number of oulets.

a 15 amp breaker can will trip after 1800 watts. that could be 20 lamps or one space heater. it depends where the outlets are going.

If you explain what you are trying to do or your problem maybe we can be more help



__________________
guyod is offline  
 
Reply With Quote Quick reply to this message
Old 02-07-2008, 09:01 AM  
hoarea
Junior Member
 
Join Date: Jan 2008
Posts: 11
Default

i am going to run new wire to a bedroom that has knob and tubing now. it is going to have at least 6 plugins. there is only one right now. u can never have enough. so there will be a computer and just everyday bedroom stuff

__________________
hoarea is offline  
 
Reply With Quote Quick reply to this message
Old 02-07-2008, 09:12 AM  
guyod
Senior Member
 
Join Date: Jan 2008
Location: Wind Gap, PA
Posts: 423
Liked 21 Times on 20 Posts
Likes Given: 8

Default

Your putting 6 outlets in one bedroom? One breaker for one bedroom is very good. if you didnt buy your supplies you can use a 20amp 12 gage wire and be able to run that to more rooms in the future.

__________________
guyod is offline  
 
Reply With Quote Quick reply to this message
Old 02-07-2008, 02:08 PM  
speedy petey
Lic.Electrical Contractor
 
Join Date: Mar 2006
Posts: 433
Liked 31 Times on 22 Posts
Likes Given: 13

Default

To answer the original question, there is NO limit to the number of receptacles on a circuit in a residence.
We just use common sense and take into account the intended use when figuring circuits.

__________________
speedy petey is offline  
 
Reply With Quote Quick reply to this message
Old 02-07-2008, 10:41 PM  
triple D
Senior Member
 
Join Date: Jan 2008
Posts: 296
Liked 1 Times on 1 Posts

Default good luck DIY

Just make sure you run a 14-2 not a 14-3. All power in a bedroom must be on a arc-fault breaker, and you can not split circuits on arc faults. Commonly I wire 2 bedrooms, lights and plugs on one 15 amp circuit. If you think you might have a laser printer or other office type things, just do only the plugs in one room on a circuit, this will keep load down to accommodate your demand. good luck, and remember we're all pullin' fer ya

__________________
triple D is offline  
 
Reply With Quote Quick reply to this message
Old 02-08-2008, 05:09 AM  
speedy petey
Lic.Electrical Contractor
 
Join Date: Mar 2006
Posts: 433
Liked 31 Times on 22 Posts
Likes Given: 13

Default

There are several manufacturers making two-pole AFCI breakers already, and more will follow. So a multi-wire branch circuit (shared neutral) is no problem with a newer panel.
Old panels and fuse boxes are another story.

__________________
speedy petey is offline  
 
Reply With Quote Quick reply to this message
Old 02-08-2008, 08:44 AM  
maine845
Junior Member
 
Join Date: Feb 2008
Posts: 2
Default

A general rule is as follows: Figure 180 VA (watts) per outlet. Using the formula P=IxE P=watts, I=amps and E=volts P=15ampsx120volts=1800VA, now divide 180VA into 1800VA and 10 is the general number that I put on a circuit. This will work the same for a 20 amp circuit as well. I recommend you stay away from a multiwire circuit because it is wired on a double pole circuit breaker and if one side causes a short and trips, the other non affected circuit will trip and thus leaves you in the dark. I teach an Electrical Course and am an active Master Electrician.

__________________
maine845 is offline  
 
Reply With Quote Quick reply to this message
Old 02-08-2008, 07:35 PM  
speedy petey
Lic.Electrical Contractor
 
Join Date: Mar 2006
Posts: 433
Liked 31 Times on 22 Posts
Likes Given: 13

Default

Quote:
Originally Posted by maine845 View Post
I recommend you stay away from a multiwire circuit because it is wired on a double pole circuit breaker and if one side causes a short and trips, the other non affected circuit will trip and thus leaves you in the dark.
Unless you are under the 2008 NEC this is NOT a code requirement.
Also, for relatively newly wired circuit, when was the last time you tripped a breaker?
In being in my (1975) house for the last 15 years, I have NEVER tripped a breaker.
Sorry, I DO NOT buy into that whole "It will leave you in the dark" philosophy.
__________________
speedy petey is offline  
 
Reply With Quote Quick reply to this message
Old 02-09-2008, 08:01 AM  
kok328
Supporting Member
HRT_SUPPORTER.png
 
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,167
Liked 100 Times on 88 Posts
Likes Given: 61

Default

and then they invented the power strip....
Now how many outlets?



__________________
kok328 is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Vintage Stove Question ! vintagedixie66 General Appliance Discussion 2 01-29-2009 08:45 AM
Question on shared ground/neutral buss in breaker box banyan Electrical and Wiring 5 06-29-2008 01:39 AM
Split-Level Framing Question kobelleprop General Home Improvement Discussion 5 04-27-2008 11:25 AM
HVAC direct vent question Mom2bac HVAC 6 02-24-2008 07:01 PM
Grout sealing question BuckeyeDad General Home Improvement Discussion 8 10-04-2007 06:50 AM