Quote:
Originally Posted by speedy petey
You must mean after the 2005 NEC. I can't comment as I do not have a copy of 2008 yet.
|
From the 2005 AND 2008 NEC: (there are no changes in 2008 for this section)
250.118. Types of Equipment Grounding Conductors. The equipment grounding conductor run with
or enclosing the circuit conductors shall be one or a combination of the following:
(1) A copper, aluminum, or copper-clad aluminum conductor.....
(2) Rigid metal conduit.
(3) Intermediate metal conduit.
(4) Electrical Meallic tubing.
(5) Listed flexible metal conduit......
(6) Listed liquidtight flexable metal conduit....
(7) Flexible metallic tubing......
(8) Armor of Type AC cable......
(9) The copper sheath of mineral-insulated, metal-sheathed cable.
(10) Type MC cable where listed and identified for grounding.....
(11) Cable trays....
(12) Cablebus framework....
(13) Other listed electrically continuous metal raceways and listed auxilliary gutters.
(14) Surface metal raceways listed for grounding.
(portions edited because I didn't want to type all the little details)
So yes, you can still use the raceway as a ground.