Default Some clarifications for kitchen outlets and GFCI

Hello,

I have removed the outlets in my kitchen to install a backsplash and having completed the installation of it, I now want to install the outlets back.

The problem is that I forgot to document or take note of how the wiring was connected to the outlets. Normally this would be no big deal since I have a general good understanding of electricity & I could simply put the outlets back the way I think they were installed but I have some concerns.

Refer to my attached picture for nomenclature...

At first, I had no idea of how the wiring was done and which breaker was controlling what.. I had done no testing (bad boy!). SO I simply installed a conventional outlet to locations A, & C, and GFCI's to D & E. I went to turn the breaker 26 & 28 and the main tripped! (not good!).

I immediately rtemoved everything and did some testing.

I have found that:

There are 3 breakers in the main panel (18/20, 26/28 & 6/8) controlling the kitchen outlets (marked by the electrician as so on the panel nomenclature sticker)
Breaker 6/8 controls Outlet B (not sure if fed directly from main since it uses 3 wires)
Breaker 18/20 controls the left wire of outlet A, right wire is dead. Again, not sure if fed directly from main because of the 3 wires.
Breaker 26/28 controls the left wire of outlet C, right wire is dead. Again, not sure if fed directly from main because of the 3 wires.

Outlets D & E are never alive so I assume they are fed from another outlet. I have marked in purple the possible path I think of..

So now to the questions:

  • Do you think my sketch is right, that is, are the purple connections correct?
  • If so, How can I install GFCI's to the outlets D & E with 3 wires? If they are feeding something else (hence the 3rd wire?) would that pose a problem?
  • Why is there a red wire in each outlet? Whats the purpose of it? As far as I know prior to stripping the kitchen, none of these outlets were controlled by a switch.
  • I have checked, all light switches and light fixtures are on a separate unrelated breaker

If all else fail, I will call an electrician.

I appreciate any answers!!

Thanks!


elec.jpg  
__________________

Last edited by condoowner; 06-25-2013 at 09:35 AM.
condoowner is offline  
 
Reply With Quote Quick reply to this message
Old 06-25-2013, 09:46 AM  
nealtw
Contractor
 
Join Date: Nov 2010
Location: vancouver, b.c.
Posts: 9,733
Liked 796 Times on 710 Posts
Likes Given: 1358

Default

On the old outlets, check to see if the little strap is removed to seperate the top and bottom plug, the strap is between the two screws on each side.



__________________
nealtw is offline  
 
Reply With Quote Quick reply to this message
Old 06-25-2013, 09:51 AM  
bud16415
Fixer Upper
 
bud16415's Avatar
 
Join Date: Feb 2013
Location: Erie Pa, Pa
Posts: 1,120
Liked 321 Times on 255 Posts
Likes Given: 106

Default

Looks like you have 3 breakers controlling 5 outlets. The power from the breaker goes first to the GFCI and connects to the LINE connection the black wire goes to the side that says HOT the white goes to COMMON. The second outlet in each of the two A & C are controlled by the GFCI and are attached to the other set of screws marked LOAD. That way E & D are just normal outlets but are GF protected by A & C. B is just a stand alone GFCI and should just have wires attached to LINE.

__________________
bud16415 is offline  
 
Reply With Quote Quick reply to this message
Old 06-25-2013, 09:55 AM  
CallMeVilla
Contractor
 
CallMeVilla's Avatar
 
Join Date: Feb 2010
Location: San Diego
Posts: 1,247
Liked 379 Times on 297 Posts
Likes Given: 154

Default

Unusual to find a red wire in a kitchen back splash outlet but it does typically have a purpose. A red wire usually indicates one of the two outlets to be operated by a switch. In this case, the strap Neal mentions would be removed, creating two separate outlet points. The black wire would supply and "always on" power to one the one outlet and the red supplies power to the other outlet point which would be switchable.

You can test this easily by locating a likely switch and flipping it to see if you get power "on" or "off."

__________________
CallMeVilla is offline  
 
Reply With Quote Quick reply to this message
Old 06-25-2013, 10:13 AM  
bud16415
Fixer Upper
 
bud16415's Avatar
 
Join Date: Feb 2013
Location: Erie Pa, Pa
Posts: 1,120
Liked 321 Times on 255 Posts
Likes Given: 106

Default

The OP has checked all the switches in the room and none of them are on any of these three circuits. I would find it rare to have counter outlets controlled by a switch or used as a split outlet. That’s mostly seen in living and bedrooms with end table lights and such. Red and black are normally hot wires. Not sure what the OP means by being fed with 3 wires though. If he can look in the boxes and see if the red is coming in with the power or maybe it’s another cable that’s going out to the remote outlets E & D.

__________________
bud16415 is offline  
 
Reply With Quote Quick reply to this message
Old 06-25-2013, 10:24 AM  
condoowner
Senior Member
 
Join Date: Dec 2009
Posts: 135
Liked 6 Times on 6 Posts
Likes Given: 10

Default

Quote:
On the old outlets, check to see if the little strap is removed to seperate the top and bottom plug, the strap is between the two screws on each side.
Unfortunately I have thrown away the old outlets a while ago...

Quote:
Looks like you have 3 breakers controlling 5 outlets.
Correct, if you assume that BOTH D & E are fed from another outlet in the kitchen.

Quote:
The power from the breaker goes first to the GFCI
Are you saying this is what I have or what I should have? Because my testing has indicated otherwise, no power to D & E whatsoever. I have once again double checked, and ALL breakers ON in the main panel, I still have no power to D & E so somehow they must be fed from another location??

Quote:
You can test this easily by locating a likely switch and flipping it to see if you get power "on" or "off."
Already done that. There is a braker in panel named "Kitchen lights" which controls both lights. When the breakers for all three backsplash outlets are off (6/8, 18/20, 56/28) I still have power to the lights and light switches. When I turn off the breaker for the lights, there is no more power to the switches and light boxes.

Otherwise, if I turn the breakers ON for the outlets but keep the kitchen light breaker OFF, I have power to A B & C.

I am pretty sure the lights are independent from the outlets in this case.

Anyways, if the red wires were supposed to be switched, wouldn't they (or at least one of them) be alive when the lights are alive? They arent right now..

The only memory I have from the original wiring is the way the outlet A was wired. If I remember correctly, it was wired something like the picture attached... Since I didnt tamper with the wire ends and left them as they originally were, at least I know which wire was attached to a terminal screw and which wire was inserted in the back holes of the outlet..
elec2.jpg  
__________________

Last edited by condoowner; 06-25-2013 at 10:35 AM.
condoowner is offline  
 
Reply With Quote Quick reply to this message
Old 06-25-2013, 10:35 AM  
condoowner
Senior Member
 
Join Date: Dec 2009
Posts: 135
Liked 6 Times on 6 Posts
Likes Given: 10

Default

Quote:
Originally Posted by bud16415 View Post
The OP has checked all the switches in the room and none of them are on any of these three circuits. I would find it rare to have counter outlets controlled by a switch or used as a split outlet. That’s mostly seen in living and bedrooms with end table lights and such. Red and black are normally hot wires. Not sure what the OP means by being fed with 3 wires though. If he can look in the boxes and see if the red is coming in with the power or maybe it’s another cable that’s going out to the remote outlets E & D.
Funny you posted just before I replied...

You are 100% right, I also find stranmge that kitchen outlet be controlled by switch? Who would turn their coffee machine or toaster on by a switch?

Yes I also would expect the switched behavior of the outlet like in my bedrooms that are exactly like that. Bottom outlet is always on (for small electronics, TV's, clock, etc) while upper one is switched for table lamp, etc..)

What I meant by "being fed by 3 wires" is that as far as I know, power from the main is achieved via 2 wire (14/2 with black & white)? Is it possible to have 3 wires (14/3) coming FROM the main panel? (red black & white)

Unless it was a 220V service, why would there be 3 wires from the main panel?
__________________
condoowner is offline  
 
Reply With Quote Quick reply to this message
Old 06-25-2013, 10:41 AM  
nealtw
Contractor
 
Join Date: Nov 2010
Location: vancouver, b.c.
Posts: 9,733
Liked 796 Times on 710 Posts
Likes Given: 1358

Default

The picture you posted could have 240 volts to that plug, the red and the black are both live 120 volts each In the old systems they split the plugs and ran red to top and black to bottom so all the tops in the kitchen were on one cercuit and the bottoms on another.
You want something like this. I'm not sure what they mean by unprotected terminal unless they are saying to use regular plugs down stream.

kitchenwiring.jpg  
__________________

Last edited by nealtw; 06-25-2013 at 10:48 AM.
nealtw is offline  
 
Reply With Quote Quick reply to this message
Old 06-25-2013, 10:45 AM  
condoowner
Senior Member
 
Join Date: Dec 2009
Posts: 135
Liked 6 Times on 6 Posts
Likes Given: 10

Default

Quote:
The picture you posted could have 240 volts to that plug
240V on a 14/3 wire??? isnt' that against code?

Why would the outlets be 240V? no kitchen appliances consume that much power?!?!


Quote:
In the old systems they split the plugs and ran red to top and black to bottom so all the tops in the kitchen were on one cercuit and the bottoms on another.
Then it would mean that all metal tabs on the live sides only were broken off so the top & bottom outlets were independent?
__________________
condoowner is offline  
 
Reply With Quote Quick reply to this message
Old 06-25-2013, 10:57 AM  
nealtw
Contractor
 
Join Date: Nov 2010
Location: vancouver, b.c.
Posts: 9,733
Liked 796 Times on 710 Posts
Likes Given: 1358

Default

If you take the cover off the breaker panel you will see that the black goes to one breaker and red goes to the one beside it.
The only reason they do that is to save wire they both are separete cercuits but use the same white and ground and if you do it wrong you could have 240 volt to one plug and yes that would not be code but using properly is not against code.



__________________
nealtw is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
How many GFCI's do I need in a kitchen? PKLehmer Electrical and Wiring 7 07-09-2009 09:09 AM
GFCI Outlets Outdoors/Garage SavvyCat Electrical and Wiring 9 05-04-2009 09:29 PM
How many electrical outlets for a new kitchen? phreaq General Home Improvement Discussion 5 09-28-2007 02:09 PM