I am adding a breaker for a 24000 BTU AC/heat pump. What size breaker would that be?
 
The smartest choice would be what's recommended by the manufacture; which will be the "only" right answer.
 
Check the amperage rating on the nameplate of the unit your installing.
 
You also need a breaker the 'trip curve' of which handles compressor [motor] loads, otherwise you might need a 'soft start' kit.
 
On the side of every unit is a "Minimum circuit ampacity" and a "Maximum fuse or breaker size".

You size the wire to the former and the breaker to the latter.