Understanding Venting V2

House Repair Talk

Help Support House Repair Talk:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

remout

Well-Known Member
Joined
Apr 22, 2015
Messages
89
Reaction score
42
Thinking about the number of roof penetrations. Is it okay to do it as pictured below? Where the blue lines run down to the vent loops from a central header in the attic.
OHVent.png
 
I'm thinking NO due to possible back drafting but, then again I'm just an idiot with an internet connection.
I'm sure the professionals will be able to advise.
 
yes, scan0001.jpg
your sewer is 4'', that is your table 7-5



couple things you need to consider, normally, in a old house, if we need to rod the sewer,and we have no cleanout
we go on the roof and rod straight down.
if, you offset your vents to the back of the house.
which is common place on custom homes, all vents to the back
you need to add cleanouts in the house,

also need to be aware, a sewer is very humid, the inside of the pipe sweats. the vent pipe MUST pitch back twards the fixture
so that the condensation can drain
also, plastic pipe SHALL be supported every 4'
 
................

OHVent.png
 
Last edited:
Frodo,

Thank you for all the effort you put into this thread and forum!
 