Another Garage Subpanel Q....

House Repair Talk

Help Support House Repair Talk:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

Mach1

noob
Joined
Nov 11, 2005
Messages
6
Reaction score
0
About a year ago, I wired my attached garage with a subpanel. My sub in the garage is only 15 feet or so from the main. I used 4 AWG THHN 90C for both hots and netrual, 6 AWG bare stranded for the ground. The conductors are installed in 1.25" PVC 90C rated conduit.

The table I looked at when I bought the wire said #4 was good for 95A (w/90C insulation) My breakers are the Cutler-Hammer BR type. Since there was no 95A breaker avaliable, I used a 100A.

In hindsight, I'm wondering if using the 100 Amp BR this was the right thing to do? Should I switch it to a 90A breaker? The only reason I can think of to change it to 90A would be because of de-rating due to conduit fill. Can someone help me out?



TIA,
Mach1
 
Derating isn't an issue here, since there are only three current-carrying conductors in the pipe. However, the wire you used is only rated for 95 amps, and they are protected by a 100- amp breaker. to make it legal, you're going to either have to up-size the wire to #3 or down-size the breaker to 90 amp.

BTW, since this is a subpanel, did you make sure to remove the bonding jumper in the subpanel??? Just a thought.
 