DIY Home Improvement, Remodeling & Repair Forum > DIY Home Improvement > Electrical and Wiring > Best Surge Setup




Help Support House Repair Talk by donating using the link above.
Reply
 
Thread Tools Search this Thread
Old 12-11-2017, 07:54 PM  
BPet
Junior Member
Join Date: Dec 2017
Posts: 2
Default Best Surge Setup

I have an outside breaker panel, located next to my meter, that contains breakers for my four outside A/C units and Pool Equipment. This panel also feeds two breaker panels located in the garage that contain all of the other breakers for the house. The garage panels are approx. 15-25ft of wire from the outside panel. Total is 400A - 200A for outside and 200A feeding garage panels. I'm considering the following Surge Protection Devices, which setup would you choose?

#1 - Install Intermatic IG2240 SPD as a Type 1 device at the outside meter. This device has its own breaker switch and removable modules that can be replaced after they die. The specs are: In(kA) 10 - SCCR(kA) 10. PLUS install an Intermatic IG1240RC3 SPD as Type 2 on the garage breaker panel that has the downstairs circuits which include all of the kitchen appliances, most of the home computers, TVs etc. The specs on this SPD are: In(kA) 20 - SCCR(kA) 50

#2 - Install 3 IG1240RC3s as Type 2 devices: The first would be on the breaker panel next to the meter on the bus that contains all of the breakers for the outside ACs etc. The top leg of this breaker panel that feeds the other garage breakers would not have very good protection at this point. Then I would install a 2nd and 3rd IG1240RC3 in the two garage breaker panels.

(I only listed the In(kA) and SCCR(kA) specs because most of the other specs were identical)

Thanks in advance for any advice you can provide


Click image for larger version

Name:	Outside Panel.JPG
Views:	43
Size:	90.4 KB
ID:	15177  
BPet is offline  
 
Reply With Quote
Old 12-19-2017, 02:37 PM  
hornetd
Member
Join Date: Nov 2005
Location: Takoma Park, Maryland
Posts: 112
Liked 70 Times on 47 Posts
Likes Given: 4

Default Read Surges Happen.

Surges Happen is a guide by the National Institute of Standards & Technology for protecting your electric and electronic devices from these electrical anomalies. It can be downloaded from https://www.nist.gov/document-18559. Once you have read it an followed the auditing process that it suggest then those with actual experience in the area of Surge and spike protection can help you with any questions that you might still have.
__________________
Tom Horne Electrician

"This alternating current stuff is just a fad. It is much too dangerous for general use." Thomas Alva Edison
hornetd is offline  
afjes_2016 Likes This 
Reply With Quote
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
House Surge Protector Boca Electrical and Wiring 21 03-19-2016 08:15 AM
Power surge freddyr24 Electrical and Wiring 8 09-22-2014 06:38 AM
Rewiring Light Fixtures..odd old Setup suboveryde Electrical and Wiring 1 10-29-2010 01:05 PM
Tandem Setup 3Dominoe3 Garage & Workshop Forum 0 09-12-2008 02:11 PM
electrical setup question imported_Hank Garage & Workshop Forum 1 07-01-2008 10:44 AM