Default Thermostat clicks but nothing happens

Hello all!

A/C has been running fine until last night. The thermostat clicks but nothing happens; neither the outside fan nor inside fan turn on. Fans will also not turn on, if switched to "On", instead of "Auto". I checked breaker, still on...I turned it off, waited 30 seconds, turned it back on, which did not help. FWIW, I also put fresh batteries in and cleaned connections about one month ago.

Your thoughts are greatly appreciated, thanks!


__________________
I'm tackling projects and making progress with your help, thank you!
If I don't reply in a timely manner, I apologize!
o2284200 is offline  
 
Reply With Quote
Old 09-16-2016, 10:47 AM  
doechsli
Join Date: May 2012
Location: , Kentucky
Posts: 68
Liked 23 Times on 11 Posts
Likes Given: 6

Default

I would say a starter cap, but I believe the furnace/air handler fan would run regardless of a cap failure. I just had one of these failures this year.

Another question is the "light switch" to control power to the furnace/air handler. My three year old grandson turned that off once unknown to my son. Typically around here they are mounted on the furnace/air handler.

Just guesses......good luck.


__________________
Dennis
doechsli is offline  
nealtw Likes This 
Reply With Quote
Old 09-16-2016, 11:09 AM  
o2284200
Member
Join Date: Oct 2012
Location: , South Florida
Posts: 221
Liked 11 Times on 10 Posts
Likes Given: 2

Default

What is a "starter cap"? How does one troubleshoot it?

The only "light switch", other than the breaker is behind the unit and not accessible. I checked the breaker, it was still on...I turned it off, waited 30 seconds, turned it back on, which did not help.
__________________
I'm tackling projects and making progress with your help, thank you!
If I don't reply in a timely manner, I apologize!
o2284200 is offline  
 
Reply With Quote
Old 09-16-2016, 11:20 AM  
doechsli
Join Date: May 2012
Location: , Kentucky
Posts: 68
Liked 23 Times on 11 Posts
Likes Given: 6

Default

The cap is located on the outside unit. Troubleshooting is problematic unless you have the correct meter however the caps are fairly inexpensive (20-40 bucks) and not too difficult to change. That said, if you don't know your way around electricity either find a competent friend or hire a pro.

Google AC starter cap and I bet a video pops up.....

Again, I have some doubt that is your issue since the inside fan is not working.

I'd start at the thermostat.......

Someone with more knowledge than I will jump in here soon.....

edit----I see you are in south Florida and may not have the combo of furnace/AC that I am used to seeing.....so my answers are subject to being totally off base.
__________________
Dennis

Last edited by doechsli; 09-16-2016 at 11:22 AM.
doechsli is offline  
 
Reply With Quote
Old 09-16-2016, 07:57 PM  
kok328
Senior Member
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,724
Liked 241 Times on 204 Posts
Likes Given: 113

Default

Problem is not the cap, symptoms don't lead to that.
You have to trouble shoot your way through but I'm putting my money on a blown control board fuse.
Check that first. If it is good then post pics and find your volt meter.
kok328 is offline  
 
Reply With Quote
Old 09-17-2016, 08:10 AM  
o2284200
Member
Join Date: Oct 2012
Location: , South Florida
Posts: 221
Liked 11 Times on 10 Posts
Likes Given: 2

Default

Thanks!
How do I check for a blown control board fuse?
Here are some pics:

Air handler wiring




Click image for larger version

Name:	thermostat3.jpg
Views:	272
Size:	82.8 KB
ID:	12878  
__________________
I'm tackling projects and making progress with your help, thank you!
If I don't reply in a timely manner, I apologize!

Last edited by slownsteady; 11-17-2016 at 08:33 PM. Reason: image mgmt
o2284200 is offline  
 
Reply With Quote
Old 09-17-2016, 03:01 PM  
o2284200
Member
Join Date: Oct 2012
Location: , South Florida
Posts: 221
Liked 11 Times on 10 Posts
Likes Given: 2

Default

I found one large purple fuse, inside air handler, which looks OK
FWIW... I have one of those cheap 7 function digital multimeter from HF as well as a Milwaukee pen style digital multimeter.

__________________
I'm tackling projects and making progress with your help, thank you!
If I don't reply in a timely manner, I apologize!
o2284200 is offline  
 
Reply With Quote
Old 09-17-2016, 03:17 PM  
overkill
Junior Member
Join Date: May 2013
Posts: 6
Likes Given: 2

Default

First ,check and see if its a bad thermostat,by bypassing it.
Take the thermostat cover off, then take the red,and yellow wire and connect the two. no need to turn the power off,its only 24volts and will not harm you.. did the system start ? if yes, then replace your Tstat. If not,then connect the wires back as they were,then procede with the following.

3 things you can do yourself , and for your situation, I would turn off your power to the outside unit. Open the panel and look at the capacitor. Is it swollen on top ? if yes,its a bad cap. ,if not swollen, I would take a multimeter and check voltage to the contactor, on the terminals L1 and L2 ( that's the power coming from the outside units power panel) from the house . Check L1 L2 and make sure you have 240 V. ,next you could take an insulated screwdriver and wear heavy rubber gloves,and press down on the contacts for a second and see if it all starts up.. If it does then its a bad coil not pulling the contacts down on its own.. Be carefull around the electrical part,get someone to do this if your not comfortable.. A capacitor and a contactor both cost about $25-35.. you'll save a ton if you can do this

Last edited by overkill; 09-17-2016 at 03:27 PM.
overkill is offline  
 
Reply With Quote
Old 09-17-2016, 03:41 PM  
overkill
Junior Member
Join Date: May 2013
Posts: 6
Likes Given: 2

Default

Here is my capacitor I just changed last week. The new one is on the left, and bad one on the right.. You see how the top is swollen ? That's a sure sign you can look for... If you find it bad. Note,your wiring.. Brown = Fan .. Yellow = C (common) and Blue = Herm (that's the compressor) ..
Power off on the outside unit, drain the capacitor by touching a screwdriver across the terminals on the cap . They can hold enough power to shock you even when disconnected,so play it safe and drain the cap before handling..
Click image for larger version

Name:	goodbad capacitor.jpg
Views:	284
Size:	43.4 KB
ID:	12518  

Last edited by overkill; 09-17-2016 at 03:47 PM.
overkill is offline  
 
Reply With Quote
Old 09-18-2016, 02:28 PM  
kok328
Senior Member
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,724
Liked 241 Times on 204 Posts
Likes Given: 113

Default

Fuse is good.
Start with line power to the unit.
Check the control board for flashing light code & reference code the legend on back of cover panel.
Check for 24volts on the secondary side of the transformer.
Check for 24vokts at the tstat.
Post back findings.


kok328 is offline  
 
Reply With Quote
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Another thermostat Question. house92 HVAC 2 01-21-2013 07:29 PM
Looking for a new thermostat! BritKnee HVAC 2 06-30-2011 03:03 PM
Thermostat Help Please!!! kittycutie2007 Electrical and Wiring 6 10-17-2009 08:47 PM
Help me rig my thermostat! aces11 Electrical and Wiring 9 11-13-2006 08:46 AM
Need a new thermostat? buckethead HVAC 2 10-12-2005 06:03 AM



Newest Threads