Default Furnace keeps tripping breaker

Hi. I have an Arcoaire electric furnace, model no. MF20N2600A. It runs for about a minute, maybe less, and then trips the breaker. The unit itself has a 50a breaker. Then it runs to a box on the wall with a 40a breaker. At the main fuse panel it is controlled by a 100a breaker. It is the 100a at the main panel that is tripping.

I thought it was odd that the 100a trips but the others don't. So maybe the breaker was bad. I replaced it with a spare 50a that I had lying around and it still trips at the main fuse panel.

Are there any things a DIYer with a multimeter can troubleshoot here, or is it time to call an HVAC repairman?

Thanks

Curt

Edit: Forgot to mention that I've already changed the filter.



Last edited by Raindem; 12-28-2017 at 11:26 AM.
Raindem is offline  
 
Reply With Quote
Old 12-28-2017, 10:53 AM  
nealtw
Contractor retired
 
nealtw's Avatar
Join Date: Nov 2010
Location: Upper Fraser Valley, British Columbia
Posts: 23,578
Liked 2994 Times on 2623 Posts
Likes Given: 4932

Default

So the 40 and 50 amp breakers are not tripping. there must be other breakers. so total draw of all of them is more than 100 but non are overloaded. Try turning other breakers off.


nealtw is online now  
 
Reply With Quote
Old 12-28-2017, 11:28 AM  
Wuzzat?
Banned
Join Date: Jan 2010
Location: , Western Hemisphere, N of the equator
Posts: 2,471
Liked 176 Times on 162 Posts
Likes Given: 108

Default

Go with this /\

Last edited by Wuzzat?; 12-28-2017 at 11:39 AM.
Wuzzat? is offline  
 
Reply With Quote
Old 12-28-2017, 11:30 AM  
Raindem
Member
Join Date: Jul 2008
Location: Sonoita, AZ
Posts: 99
Liked 9 Times on 9 Posts
Likes Given: 1

Default

It is the breaker at the fuse panel that is tripping. When I reset it the furnace will briefly run and trip it again after a minute.
Raindem is offline  
 
Reply With Quote
Old 12-28-2017, 11:45 AM  
Wuzzat?
Banned
Join Date: Jan 2010
Location: , Western Hemisphere, N of the equator
Posts: 2,471
Liked 176 Times on 162 Posts
Likes Given: 108

Default

Quote:
Originally Posted by Raindem View Post
I thought it was odd that the 100a trips but the others don't. So maybe the breaker was bad. I replaced it with a spare 50a that I had lying around and it still trips at the main fuse panel.
At this point no one knows if the 100a is bad or the 50A is bad or good or it is something else.
I'd replace the 100a with a similar unit (but I don't like guessing) or buy/borrow a clampon ammeter for some logical troubleshooting.
What is the nameplate current draw for your unit?

Last edited by Wuzzat?; 12-28-2017 at 11:54 AM.
Wuzzat? is offline  
 
Reply With Quote
Old 12-28-2017, 01:53 PM  
Sparky617
Member
Join Date: Nov 2014
Location: Cary (Raleigh), NC
Posts: 796
Liked 278 Times on 219 Posts
Likes Given: 171

Default

Replacing a 100A with a 50A will definitely trip unless your total load is below 50A. I suspect your 100A breaker is bad, it happens, they can become weak over time. If it just started doing this that would be my educated guess. Your electric furnace is probably the largest load in your house.

Are you running an electric range, water heater, and a dryer at the same time? Those would be your other high load appliances. Do they all go through the 100A main breaker? At my house the HVAC units and electric stove outlet have breakers in the main panel below my electric meter outside. The sub-panel for everything else is in the garage and runs off of a 100A breaker under the meter.
Sparky617 is offline  
 
Reply With Quote
Old 12-28-2017, 02:24 PM  
Wuzzat?
Banned
Join Date: Jan 2010
Location: , Western Hemisphere, N of the equator
Posts: 2,471
Liked 176 Times on 162 Posts
Likes Given: 108

Default

With the Arcoaire off, along with a clock you can use your electric meter as an ammeter and see what current is being drawn.

Your PoCo can supply you with the method, there's some number stamped on the meter that provides the conversion.

100A @ 240V gives 24 kw for an hour (24 kwh) and 0.4 kwh in one minute.
Wuzzat? is offline  
 
Reply With Quote
Old 12-28-2017, 06:42 PM  
Raindem
Member
Join Date: Jul 2008
Location: Sonoita, AZ
Posts: 99
Liked 9 Times on 9 Posts
Likes Given: 1

Default

Thanks for the follow up responses. I thought the 50a breaker would be OK temporarily because the other breakers in the circuit were equal or less. I guess I just proved I'm not an electrician.

I think what makes sense at this point is to get an exact replacement for the 100a as someone suggested. And then go from there.

I should point out that this is a small furnace in my workshop, not in the main home. There was nothing else running at the time.
Raindem is offline  
 
Reply With Quote
Old 12-29-2017, 12:36 AM  
nealtw
Contractor retired
 
nealtw's Avatar
Join Date: Nov 2010
Location: Upper Fraser Valley, British Columbia
Posts: 23,578
Liked 2994 Times on 2623 Posts
Likes Given: 4932

Default

Quote:
Originally Posted by Raindem View Post
Thanks for the follow up responses. I thought the 50a breaker would be OK temporarily because the other breakers in the circuit were equal or less. I guess I just proved I'm not an electrician.

I think what makes sense at this point is to get an exact replacement for the 100a as someone suggested. And then go from there.

I should point out that this is a small furnace in my workshop, not in the main home. There was nothing else running at the time.
Is there anything else taking power from that 100 amp breaker?
nealtw is online now  
 
Reply With Quote
Old 12-29-2017, 08:26 AM  
Raindem
Member
Join Date: Jul 2008
Location: Sonoita, AZ
Posts: 99
Liked 9 Times on 9 Posts
Likes Given: 1

Default

Not that I know of. The fuse panel was mis-labeled and had that breaker as going to a 220V outlet. But I got that sorted out. With the 100a turned off everything else in the shop appears to still be working.


Raindem is offline  
nealtw Likes This 
Reply With Quote
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Breaker keeps tripping Dennisrl Electrical and Wiring 19 02-27-2017 05:14 PM
Goodman CPLE24-1C a/c tripping breaker BraDolMag1 HVAC 4 05-21-2012 08:39 PM
Breaker keeps tripping david542 Electrical and Wiring 10 03-09-2012 12:38 PM
Breaker Consistantly tripping mjpogue HVAC 6 05-31-2009 03:04 PM
ICP HeatPump Tripping Outside Breaker dplusm2004 HVAC 5 04-19-2007 08:46 PM



Newest Threads