Default Lennox headoffice contact?

I installed a new Lennox G61MPV furnace and a new Honeywell HE225 humidifier. Found the humidifier is SOLELY controlled by the furnace's heating time, which I suppose it should control by the Humidistat and Fan. My local installer just stopped their service after installation and dragging on my problem without any solution.

How should we wire the Furnace to the Humidifier, so that the Humidifier ONLY control by the FAN and HUMIDISTAT. Not SOLELY control by the furnace, which now the humidifier only work when the furnace heat is kicking in.

Or someone can tell me Lennox headoffice's email address for me to contact them on this problem and correct wiring.

Now I put pots of water everywhere in my house to protect my rose wood furniture and piano. At nigh, I have to have a portable humidifier in my bedroom in order to sleep well. Now is dry.

Thank you.



__________________
ccpyue is offline  
 
Reply With Quote Quick reply to this message
Old 03-26-2011, 12:24 PM  
hvactechfw
Professional
 
Join Date: Mar 2011
Location: Fort Wayne, IN
Posts: 66
Default

was this ever resolved? If no, how is the Humidifier currently wired and what humidistat are you using?



__________________
hvactechfw is offline  
 
Reply With Quote Quick reply to this message
Old 03-27-2011, 10:39 AM  
joecaption
Senior Member
 
Join Date: Jan 2011
Location: Hartfield VA, VA
Posts: 1,397
Liked 51 Times on 42 Posts
Likes Given: 2

Default

Sounds like you have a problum with the installer not Lenox. I'm sure they would like to know if one of there installers is messing up, but I'd be calling someone else to do the future work.

__________________
joecaption is offline  
 
Reply With Quote Quick reply to this message
Old 11-24-2014, 02:48 PM  
ccpyue
Member
 
ccpyue's Avatar
 
Join Date: Feb 2011
Location: Toronto, Ontario
Posts: 45
Likes Given: 1

Default

Quote:
Originally Posted by joecaption View Post
Sounds like you have a problum with the installer not Lenox. I'm sure they would like to know if one of there installers is messing up, but I'd be calling someone else to do the future work.



You are very correct. I won't call this company any more.
__________________
ccpyue is offline  
 
Reply With Quote Quick reply to this message
Old 11-24-2014, 04:32 PM  
kok328
Supporting Member
HRT_SUPPORTER.png
 
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,230
Liked 116 Times on 101 Posts
Likes Given: 65

Default

You can also purchase a piano humidifier.

__________________
kok328 is offline  
 
Reply With Quote Quick reply to this message
Old 11-24-2014, 04:35 PM  
kok328
Supporting Member
HRT_SUPPORTER.png
 
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,230
Liked 116 Times on 101 Posts
Likes Given: 65

Default

Wire the humidistat in parallel with the fan circuit so when both the fan comes on & the stat calls for humidity , it will humidify. Just make sure your transformer is capable of the extra current.

__________________
kok328 is offline  
 
Reply With Quote Quick reply to this message
Old 11-24-2014, 08:46 PM  
slownsteady
Supporting Member
HRT_SUPPORTER.png
 
slownsteady's Avatar
 
Join Date: Jun 2009
Location: Newton, NJ
Posts: 1,430
Liked 226 Times on 189 Posts
Likes Given: 279

Default

If the humidifier in question doesn't have it's own blower, then it is useless to run it without the furnace. The furnace supplies the airflow that the humidifier needs.

__________________
slownsteady is offline  
 
Reply With Quote Quick reply to this message
Old 11-25-2014, 07:51 AM  
kok328
Supporting Member
HRT_SUPPORTER.png
 
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,230
Liked 116 Times on 101 Posts
Likes Given: 65

Default

It would have to be wired into the fan circuit of the furnace so you can set the fan to "On" versus "Auto" and would open the solenoid valve for the water supply when the fan is running.



__________________
kok328 is offline  
slownsteady Likes This 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Lennox A/C Problem HardcoreNinja69 HVAC 1 05-29-2010 06:41 AM
Lennox Condensor BWonsch HVAC 1 07-01-2009 11:29 AM
Lennox capacitor Betty HVAC 4 06-02-2008 05:56 PM
1994 lennox fan o0o_ddt_o0o HVAC 1 11-26-2007 09:05 PM
help needed/condenser coil contact et30525 HVAC 2 07-20-2006 08:11 PM

Newest Threads

LATEST SPONSOR DEALS