Default Feed to Separate Building

I'm sure this can't be right, but I've discovered that the feed to my detached garage comes from a 220v 50amp breaker in the main panel in the house. The current is carried by a 10-3 NM cable across the 33 feet to the garage and terminates at an old fuse box in the garage. This box contains 3 of those tubular black fuses and the entire garage is fed directly from this box.

Am I off the mark or is the 10-3 wiring woefully inadequate to carry anything near 50 amps? In other words, wouldn't the wiring fail before the breaker would ever trip? I haven't had any problems of any kind to date, but I'd like to avoid them in the future as well. I'm thinking that an upgrade of feed wiring, a breaker box install, and some garage interior re-wiring is in order.

Any thoughts appreciated!



__________________
handy is offline  
 
Reply With Quote Quick reply to this message
Old 02-28-2011, 07:14 PM  
nealtw
Contractor
 
Join Date: Nov 2010
Location: vancouver, b.c.
Posts: 10,753
Liked 927 Times on 827 Posts
Likes Given: 1596

Default

30 amp breakers tied together would be the most you would want, the fuses in the garage should be 15 amp. or less, I think.



__________________
nealtw is offline  
 
Reply With Quote Quick reply to this message
Old 03-01-2011, 05:44 AM  
speedy petey
Lic.Electrical Contractor
 
Join Date: Mar 2006
Posts: 447
Liked 39 Times on 27 Posts
Likes Given: 17

Default

Quote:
Originally Posted by nealtw View Post
..., the fuses in the garage should be 15 amp. or less, I think.
What do you base this on?
__________________
speedy petey is offline  
 
Reply With Quote Quick reply to this message
Old 03-01-2011, 07:01 PM  
kok328
Supporting Member
HRT_SUPPORTER.png
 
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,220
Liked 116 Times on 101 Posts
Likes Given: 65

Default

Yes, 10 AWG is incorrect wire size for a 50-amp breaker. Either increase the wire size or decrease the breaker size.

__________________
kok328 is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Master Bath or Separate Bath? kmb383 General Home Improvement Discussion 8 11-01-2010 12:11 PM
Convert 220v cooktop feed to 110v sub-panel? Dave928 Electrical and Wiring 2 08-06-2010 08:14 AM
Weed and Feed is illegal here. Now what do I use? codytaylor Garden and Lawncare 2 08-27-2009 08:19 PM
meter reading and separate buildings? Philphine Electrical and Wiring 5 03-03-2007 02:51 PM
separate toilet??? monkeyclipper General Home Improvement Discussion 1 01-18-2007 10:28 AM

Newest Threads

LATEST SPONSOR DEALS