Got a relay & it didn't help. Still 25 volts (big red wire) coming from "Fan & Limit Control" (pictured below & I replaced it last year, best I remember) until I plug it into relay & then it goes to 0 Volts or very close to it.


Click image for larger version

Name:	SCH01.jpg
Views:	76
Size:	63.3 KB
ID:	2583   Click image for larger version

Name:	LIMIT.jpg
Views:	85
Size:	63.7 KB
ID:	2584  
tndave is offline  
 
Reply With Quote
Old 03-10-2011, 08:41 PM  
tndave
Junior Member
Join Date: Mar 2011
Location: Cleveland, TN
Posts: 23
Default

To clarify post 5 has 98 volts, post 6 has 28, post 8 has 0, but if I unplug the wire and test the wire it has like 28 & post 3 has 0 volts. I tried post 3 with the wire that goes to the inducer off & it was not getting any current. Any help would be greatly appreciated.

Thanks!!



Last edited by tndave; 03-10-2011 at 08:51 PM.
tndave is offline  
 
Reply With Quote
Old 03-10-2011, 09:36 PM  
paul52446m
Senior Member
Join Date: Oct 2010
Location: Houghton Lake, Mi.
Posts: 435
Liked 1 Times on 1 Posts

Default

Quote:
Originally Posted by tndave View Post
To clarify post 5 has 98 volts, post 6 has 28, post 8 has 0, but if I unplug the wire and test the wire it has like 28 & post 3 has 0 volts. I tried post 3 with the wire that goes to the inducer off & it was not getting any current. Any help would be greatly appreciated.

Thanks!!
Ok you say that post 5 has 98 volts, If you follow the main 115 volts Hot power through the wiring diagram, it goes through door switch or interlock switch, down to 6 on fan relay, bK over to transformer and then over to your 5 post on system relay This should be 115 to 120 volts all the way. so check and see where you are losing voltage, should not be down to 98 volts.
After you get this right then on a call for heat you should get 24 to 27 volts when testing across from 7 to 8 on system relay. Check all this out first.
Paul
paul52446m is offline  
 
Reply With Quote
Old 03-10-2011, 09:55 PM  
tndave
Junior Member
Join Date: Mar 2011
Location: Cleveland, TN
Posts: 23
Default

It's 98.3 coming out of transformer (black wire). 28 going into transformer (blue wire)
tndave is offline  
 
Reply With Quote
Old 03-10-2011, 10:23 PM  
paul52446m
Senior Member
Join Date: Oct 2010
Location: Houghton Lake, Mi.
Posts: 435
Liked 1 Times on 1 Posts

Default

Ok you say that post 5 has 98 volts, If you follow the main 115 volts Hot power through the wiring diagram, it goes through door switch or interlock switch, down to 6 on fan relay, bK over to transformer and then over to your 5 post on system relay This should be 115 to 120 volts all the way. so check and see where you are losing voltage, should not be down to 98 volts.
After you get this right then on a call for heat you should get 24 to 27 volts when testing across from 7 to 8 on system relay. Check all this out first.
This is the same message that i gave you in message 13. You have to check step by step the way a tell you or we are not going to find the problem. I said start with the incoming power Hot line and then follow in through the system like i said. I can't tell you where you are losing power, so read post 13 and go step by step. Paul
paul52446m is offline  
 
Reply With Quote
Old 03-11-2011, 07:56 PM  
tndave
Junior Member
Join Date: Mar 2011
Location: Cleveland, TN
Posts: 23
Default

The voltage drop is due to the ground. If you use the ground that comes out of the fan relay you get 98-99 Volts at post 5. If you use the main common you get 125. I connected a ground straight from main common to common on low volt board & that gave me 125 between post 5 & 7, but that didn’t help. I later took the jumper wire that I added off...

I found if I wiggled the wire from the limit to the relay (the one that was going down to 0 volts under load) that the inducer came on. So I got that connection (at the limit) cleaned and snugged up & the inducer works. Now the inducer comes on, the igniter glows and it flames up…for about 3 or 4 seconds & turns the gas off. It does the same again & shuts down. Cleaned up the flame sensor & now it works fine. I guess the connection at the limit was the original problem & the flame sensor was just an added bonus…

Thanks for your help!!!


tndave is offline  
 
Reply With Quote
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
propane line size Gregg Plumbing Forum 1 11-13-2009 04:27 PM
Attaching propane fireplace hose to a 20lb propane tank fionab General Home Improvement Discussion 1 09-18-2009 11:45 PM
How to find HEIL HVAC parts pamshoney2003 HVAC 2 05-28-2008 05:31 PM
Heil Furnace Backfire. mvannorman Introductions 2 12-05-2007 03:17 PM
Heil furance with Honeywell gas valve troubled furance HVAC 3 11-29-2007 01:39 AM