Default Lennox 10ACC Condenser Fan Motor Overheating

Hi Everyone,
I have found all of your advice on this subject very helpful, but I am still not sure of the solution.

We have a Lennox 10ACC-036-230-02 condenser unit about 7 years old. After about 20 minutes of the unit starting the fan motor (original unit) overheats and shuts off while the condenser still runs. The original unit had a Dual run capacitor but 2 years ago a local tech replaced it with 2 single capacitors. I have visually checked all of the contacts and have cleaned off the fan motor shaft and even oiled it a little. The capacitors are cool to the touch just the fan motor is hot. Oh, and just a side note, we also have a slow freon leak in the evaporator coil.

I am trying to avoid purchasing a new fan motor, so my question is:

Can a bad capacitor cause the fan motor to overheat?

Thanks you in advance for your help. I have seen you give great advice to others and would really appreciate your assistance.

Trevor



__________________
TGrayson is offline  
 
Reply With Quote Quick reply to this message
Old 04-21-2011, 07:36 PM  
kok328
Supporting Member
HRT_SUPPORTER.png
 
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,213
Liked 115 Times on 100 Posts
Likes Given: 65

Default

I doubt that the capacitor is the problem however, it is your cheapest "replace & see" option. A new cap should be under $10.

I suspect that the replacement cap may not have been of identical rating as the old cap.



__________________
kok328 is offline  
 
Reply With Quote Quick reply to this message
Old 04-21-2011, 08:33 PM  
TGrayson
Junior Member
 
Join Date: Apr 2011
Location: Charlotte, NC
Posts: 24
Liked 1 Times on 1 Posts

Default

Hi kok328, thanks for the quick response. I thought that would be a good way to go, but should I just replace the one single run capacitor to the fan or go ahead and replace both now with a dual run capacitor?

Thanks again.

__________________
TGrayson is offline  
 
Reply With Quote Quick reply to this message
Old 04-22-2011, 08:35 AM  
kok328
Supporting Member
HRT_SUPPORTER.png
 
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,213
Liked 115 Times on 100 Posts
Likes Given: 65

Default

I would at least replace the one for the fan motor but, first check the specs for the cap on both the compressor and the motor. Make sure the correct rated cap is installed for both. If not replace as necessary. Also check all your electrical connections. A loose connection will make for a hot condition.

__________________
kok328 is offline  
 
Reply With Quote Quick reply to this message
Old 05-26-2011, 02:56 PM  
TGrayson
Junior Member
 
Join Date: Apr 2011
Location: Charlotte, NC
Posts: 24
Liked 1 Times on 1 Posts

Default

Hi kok328,
I am sorry I did not get back to you sooner. I just replaced the fan motor capacitor the other day (7.5 MFD, 440 VAC) that I purchased from Grainger for $9. After a very easy installation the old fan started right up and has been running fine ever since. Now all I need is to fill the system with freon that has been leaking from the evaporating coil. Too bad I can't do that on my own. Thanks again for your help.

__________________
TGrayson is offline  
 
Reply With Quote Quick reply to this message
Old 05-26-2011, 03:20 PM  
kok328
Supporting Member
HRT_SUPPORTER.png
 
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,213
Liked 115 Times on 100 Posts
Likes Given: 65

Default

Good job. Sorry I can't help with the recharge. You may want to consider fixing the leak because a newer type of freon is coming out thus making the older freon types more expensive.

__________________
kok328 is offline  
 
Reply With Quote Quick reply to this message
Old 05-27-2011, 05:16 PM  
xmlaroux
Junior Member
 
Join Date: May 2011
Location: San Antonio, Tx
Posts: 3
Default Kok328

Kok328,

I have the exact same problem. The fan motor over heats after 15 minutes. I have replaced both the fan motor and the capacitor now twice. Both were matched with the original. The first time I did this 2 months ago I had no issues, but now I just replaced the motor (.25 HP 1.8A 60hz) with a 5 370 capacitor. I just replaced them again with new ones and it started up fine, then failed within 20 minutes.

Any ideas?

Thanks.
XM



__________________
xmlaroux is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Lennox A/C condensor fan motor GWS HVAC 23 07-18-2012 12:33 PM
Lennox Fan Motor needs replaced? gogoguy HVAC 2 05-24-2009 08:40 AM
GE profile refrigerator condenser fan motor trouble David B General Appliance Discussion 2 11-04-2008 06:56 PM
"Overheating" circulator motor romeyn HVAC 6 04-13-2008 06:39 AM
Condenser fan motor Tonnyray HVAC 1 09-10-2007 11:06 AM

Newest Threads

LATEST SPONSOR DEALS