Default 2 breakers, 1 neutral, 14-3 wire coming from Load Center/panel

I'm not an electrician, but know some of the basics. But this is new to me so I want to see what some of you recommend.

Here's the situation (in Iowa by the way)...
Brand new 20x40 shed with brand new Load Center/panel installed inside by professional electrician. Currently has 1 basic light and 1 outlet wired by the electrician. Now I want to add some overhead lights. Using 2 15A breakers, I want to run a 14-3 wire out of the panel into 1 double gang box having 2 light switches where each light switch has it's own breaker and each controls 1 row of lights. So 2 circuits (1 on black and 1 on red), using the same ground and neutral. Each light has six 32W florescent bulbs for a total of 192W and each row has 3 lights so I'll just round up to 600W total per row. I know 15A using 14g wire can handle 1800 watts (1440 max) so the 600W is well under that, but I still want each row of lights to have it's own breaker.

Is this okay, meaning can the red & black hots share the neutral? I thought I read somewhere that this is okay IF the breakers are on opposite sides of the panel. Is it wrong/dangerous to have them on the same side? Does the electrical code speak to how this should be done and if so where specifically is this stated?

Anything else I'm missing? Many thanks in advance.


kmham is offline  
 
Reply With Quote
Old 05-29-2011, 02:46 PM  
Alphabet
Junior Member
registry_dropdown_22686_57459
 
Join Date: May 2011
Location: Kitchener, Ontario
Posts: 1
Default

You can do exactly like you and and but the breakers on the SAME side in the panel. If you want to put it on the other side then you have to make sure its on the other line. Either way you want one breaker on a black line and a breaker on the red line in the panel.Im assuming you ran 240v to your shed. If you only ran 120v there then it doesn't matter where your breakers go in the panel.


Alphabet is offline  
 
Reply With Quote
Old 05-29-2011, 03:11 PM  
kmham
Junior Member
registry_dropdown_22685_57460
 
Join Date: May 2011
Location: Cedar Rapids, IA
Posts: 2
Default

thanks alphabet - correct, it's a 240v panel. Okay, I think I was confused. I actually want the breakers on the same side next to each other - not on opposite sides - correct?

Is that because when you install a double pole breaker it's actually using 120v from each side? So if my 2 independent 15a breakers are on the same side and right next to each other, they are actually using the opposite sides anyway - right? Are the sides called "phases"? or something like that? Sorry I don't know the technical words for most of this stuff
kmham is offline  
 
Reply With Quote
Old 05-29-2011, 06:46 PM  
PeytonC2682
Junior Member
registry_dropdown_22688_57467
 
Join Date: May 2011
Location: Natchez, MS
Posts: 1
Default

The breakers should be on opposite legs (phases) in the panel. If you have a volt meter, you should be able to read 240v across the two breakers when installed correctly. The objective of this is that because they are opposites, the most that the neutral will ever take is the max on either one of the legs. For instance, if there were 12 amps on the black and 7 amps on the red, the neutral should be carrying 5 amps.
PeytonC2682 is offline  
 
Reply With Quote
Old 05-29-2011, 09:13 PM  
nealtw
Contractor
registry_dropdown_20526_57468
 
Join Date: Nov 2010
Location: Upper Fraser Valley, British Columbia
Posts: 13,044
Liked 1286 Times on 1130 Posts
Likes Given: 2171

Default

The two breakers should be tied together so you cannot turn just one off.


nealtw is offline  
 
Reply With Quote
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Load Bearing Wall Removal Advice (point load?) stringer9 Framing and Foundation 8 10-25-2010 02:48 PM
ITE Breakers dmccollim Electrical and Wiring 2 08-20-2010 11:44 AM
Neutral and Ground on a Sub-Panel wblandry Electrical and Wiring 6 06-26-2009 10:48 PM
Wire size for sub-panel deepstuff Electrical and Wiring 3 11-21-2008 12:58 PM
Load Center Location / Garage Door wannabebuilder Electrical and Wiring 2 01-13-2007 10:36 PM

Newest Threads

LATEST SPONSOR DEALS