I live in "one of those" subdivisions where everyone has a pole light mounted to their brick or stone mailbox at the end of the drive on the street. The light is supposed to be on all the time in darkness, hence my problem.

Last year mine stopped working in the middle of the winter. This happened during a major cold snap where there was a lot of rain, then major cold and snow on top of it all. I live in Georgia, this is a very rare weather event.

Anyway the circuit tripped.

Also on this circuit is the front entry way to my home, some light switches and a few outlets. In the crawl space of my home there is a grey power cable which drops down out of the front foyer of the house and connects in a box to another grey power cable that then goes through the foundation and down the lawn to the mailbox.

I simply disconnected the circuit in the crawl space so at least I have power to the front of my home, however the mailbox light of course doesnt work. I am now trying to fix this. There is a box at the mailbox and I seem to have continuity between this box and the crawlspace of my home. I also have continuity between the mailbox box and the wires where they connect to the fixture. I have replaced the fixture, that wasnt it.

Before I go and dig up 80 feet of buried wire, are there any suggestions? If an animal chewed through the buried wire, would I still have continuity? Cause I seem to have just that.



__________________
AU_Prospector is offline  
 
Reply With Quote Quick reply to this message
Old 11-13-2011, 03:43 PM  
AU_Prospector
Senior Member
 
Join Date: Jan 2008
Posts: 106
Default

I think I have some digging to do. I simply disconnected everything at the mail box and put wire nuts on all the wires. breaker still trips even though there is nothing attached.
I assume this means there is a break in the wire underground between the crawlspace and the mailbox, agreed?

So what do I rewire this with and what can I use for conduit? PVC okay? ABS?



__________________
AU_Prospector is offline  
 
Reply With Quote Quick reply to this message
Old 11-13-2011, 03:59 PM  
joecaption
Senior Member
 
Join Date: Jan 2011
Location: Hartfield VA, VA
Posts: 1,397
Liked 51 Times on 42 Posts
Likes Given: 2

Default

Not likly an animal has eaten the wires, more likly someone has hit the wire while digging, wrong wire used (it should be gray wire feeding the box and say UF on the insulation) corroded connections, someone spliced the wires instead of one continuous wire and did not use below grade connectors, loose connections. To name a few that come to mind.
Yes it's possible to get an ohm reading showing continunuty, say from black to black and white to white, but if another color is also touching another color
it will not show up with an ohm test in most cases. But if you did the same test and touched the black and the white wire at the same time on the opposite ends it may show the same result as black to black and white to white.
Wire needs to be buried at least 18" below ground. In most cases just using UF wire is fine. As an added precaution you can use gray underground rated PVC but it's not required and a real pain to do this way.
If you go with UF with not PVC you need to use Gray Pvc where ever it's above ground and water tite connection boxes called LB's.

__________________

Last edited by joecaption; 11-13-2011 at 04:07 PM.
joecaption is offline  
 
Reply With Quote Quick reply to this message
Old 11-13-2011, 04:16 PM  
AU_Prospector
Senior Member
 
Join Date: Jan 2008
Posts: 106
Default

With the power disconnected I did the following test. Wire nut black to white in the crawlspace. Touch black and white at the same time at the mailbox and got continuity.

The box in my crawl is basically a splice between the wire coming from my living space and the wire going to the mailbox. This is grey wire, it is labeled UF/B, the wire coming from the living space is also grey but it is different and not labeled UF. Most all the other wires in my home are yellow.

At the initial time of my problems, there was no one digging. Is it possible the problem would be delayed after the digging event by months? Come to think of it, I have lived in the home 4 years and have not used a shovel anywhere close to this area.

So you agree, I need to excavate the power cable right? This is not something I take lightly. Kind of like one of those chores I dont really want to do.

__________________

Last edited by AU_Prospector; 11-13-2011 at 04:33 PM.
AU_Prospector is offline  
 
Reply With Quote Quick reply to this message
Old 11-13-2011, 04:54 PM  
kok328
Supporting Member
HRT_SUPPORTER.png
 
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,229
Liked 116 Times on 101 Posts
Likes Given: 65

Default

check for shorts in the wire leaving the crawlspace and again where it surfaces at the mailbox. If your lucky, you'll find a nick in the wire that is causing the short.
Otherwise, check for continiuty between (earth & hot) and (earth & neutral). If you find continuity there, you will need your shovel.
I wouldn't waste time trying to locate the short and just bury a new wire if nothing pans out for you.

__________________
kok328 is offline  
 
Reply With Quote Quick reply to this message
Old 11-13-2011, 05:03 PM  
joecaption
Senior Member
 
Join Date: Jan 2011
Location: Hartfield VA, VA
Posts: 1,397
Liked 51 Times on 42 Posts
Likes Given: 2

Default

Disconnect the wires on both ends of the circut.
Then check for continuity from point to point, white to white, black to black.
Then check black to white. White to black. If there's still continuity there's a short.

__________________
joecaption is offline  
 
Reply With Quote Quick reply to this message
Old 11-13-2011, 07:18 PM  
AU_Prospector
Senior Member
 
Join Date: Jan 2008
Posts: 106
Default

Hey really? 18" deep? The frost line around here is only about 5" maybe less.
18" means I have to go rent a trencher I guess. What is the purpose of 18"? I cant get that deep with a spade. Heavy clay, rock hard stuff where I live.

__________________
AU_Prospector is offline  
 
Reply With Quote Quick reply to this message
Old 11-13-2011, 10:16 PM  
nealtw
Contractor
 
Join Date: Nov 2010
Location: vancouver, b.c.
Posts: 10,976
Liked 963 Times on 856 Posts
Likes Given: 1648

Default

You want 18" for safety and code not frost protection.

__________________
nealtw is offline  
 
Reply With Quote Quick reply to this message
Old 11-14-2011, 12:25 AM  
BridgeMan
Senior Member
 
BridgeMan's Avatar
 
Join Date: Aug 2011
Location: Cottage Grove, Oregon
Posts: 738
Liked 75 Times on 67 Posts

Default

It does sound like you have a short circuit somewhere underground, as if someone did a "mickey mouse" splice in midstream to save a few nickels. Now you get to pay for it. Have you checked to see if, by chance, your mailbox feed is enclosed in conduit? If so, you lucked out (no digging required)--just pull your new wire through, attached to one end of the existing line. Blow some conduit lube in from both ends with compressed air to make the pull easier, as 80 ft. could prove stubborn.

I built a brick, lighted mailbox at a former house in NM, simply because the going thing for bored teenagers was to drive through neighborhoods and smash mailboxes with baseball bats. Worked like a charm, and even survived a direct hit from a BMW who's driver smacked it during an ice storm (driving way too fast for conditions--I was standing there when it happened). His precious BMW had to be towed, but my mailbox (and light) came through unscathed.

__________________
BridgeMan is offline  
 
Reply With Quote Quick reply to this message
Old 08-22-2012, 07:21 AM  
bobsmith12
Junior Member
 
Join Date: Aug 2012
Posts: 1
Default

Hey it has been such a long time since you have posted about your mailbox issues. Your problem has been solved or not?
__________________________
mailboxes



__________________
bobsmith12 is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Did I mount outdoor light fixture correctly? Devg Electrical and Wiring 1 08-16-2009 07:20 AM
Was it a coincidence or did... (Outdoor flood light question) TenTwelve Electrical and Wiring 3 07-19-2008 01:19 PM
stolen mailbox haha GBjay General Home Improvement Discussion 2 08-13-2007 07:43 PM
Outdoor lantern or light pole gulab jamun Electrical and Wiring 3 03-30-2007 08:09 PM
solar powered motion-sensor outdoor light todd_k Electrical and Wiring 3 01-19-2007 04:13 PM

Newest Threads

LATEST SPONSOR DEALS