I have a problem that is intriguing me, and would appreciate any help with this problem. Thanks in advance

I have a GFCI that is in a sunroom. It tripped. Tried resetting it, but it will not reset.

I diconnected all the downstream receptacles by disconnecting the load wire, and still will not reset. I bought a new GFCI receptacle, and connected the line side to the wire, with nothing attached to the load end, and it too will not reset.

I connected the new GFCI to another wire, and it did reset OK, even the old one did. I left the GFCI reset, and wired it to the wire in the sunroom, and it worked. I then attached the load side, and all the downstream receptacles worked OK. It did not trip, even after attaching all the appliances to it.

I then Pushed the test button, and was unable to reset it again, and all receptacles went dead. I got a third GFCI, same result. I kept the GFCI tripped as I need to figure out what is wrong, before leaving it on.

Could this be a problem upstream. What can be done to trooblshoot the problem. Help please.

Thanks


imadns is offline  
 
Reply With Quote
Old 12-20-2011, 07:29 AM  
JoeD
Senior Member
Join Date: Mar 2006
Location: Welland, Ontario
Posts: 1,503
Liked 266 Times on 227 Posts
Likes Given: 19

Default

Check the breaker. Some GFCIs won't reset if there is no power. Turn off then back on. Some breakers will look on when they are tripped.
If breaker is good then look another GFCI or a loose connection upstream.


JoeD is online now  
 
Reply With Quote
Old 12-20-2011, 04:37 PM  
nealtw
Contractor retired
 
nealtw's Avatar
Join Date: Nov 2010
Location: Upper Fraser Valley, British Columbia
Posts: 23,718
Liked 3054 Times on 2673 Posts
Likes Given: 5050

Default

You are looking for white touching ground in that box or the main breaker box or some box in between. If not then you may have a damaged wire.
nealtw is offline  
 
Reply With Quote
Old 12-23-2011, 03:09 PM  
imadns
Junior Member
Join Date: Dec 2011
Posts: 2
Default

Thanks for your help.
I traced the wire to a junction box, the white wire was loose. I disconnected the wire, ran a new wire to the panel and connected both ends in a new junction box. The GFCI now works perfectly.
Again thanks for all your help.
imadns is offline  
 
Reply With Quote
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
GFCI outlets vs GFCI breakers Dzarate29 Electrical and Wiring 6 11-01-2013 11:32 AM
GFCI Breaker Won't Reset LSUCoonie Electrical and Wiring 4 06-17-2011 10:06 AM
Newly installed GFCI will not reset banterer Electrical and Wiring 6 06-03-2008 12:18 AM
GFI Won't Reset Goose Electrical and Wiring 5 02-17-2008 06:41 PM
GFCI at Control Panel won't reset jim2468 Electrical and Wiring 6 12-12-2007 06:13 PM



Newest Threads