Default Double glazed door leaking at damp-course / sill interface.

Hello,

I have tried looking for my issue on the forum and can't find it, so I wonder if anybody can help. To begin, an image:
Click image for larger version

Name:	Slide1.jpg
Views:	294
Size:	28.8 KB
ID:	3808

I have had to remove a large section of chip board flooring affected by the leak. Water is coming in immediately ABOVE the damp-course layer, i.e. just below the bottom white part (the sill?) and the water tracks along the damp course, where the water absorbs into wooden floor.

Our builder looked at it an said that it could be water being driven in from outside, under the sill, at the sill/brick interface. As such, he has comprehensively made a framing silicone bead, so stop water been driven through. But after a hard rainfall, with rain driven at the window, the leak is back!

Important to note here, is that water IS NOT seeping in at the line between the window frame and the top of the sill (as we look at picture in the inside) this joint is dry. The water is coming in above damp course layer, immediately below the bottom of the sill.. . . What could it be? I asked my builder if we should remove the glass pane and he said he couldn't see the benefit as leak is much lower down in door unit (somewhere).

The only clue I can see on forum is something to do with drain-away's, maybe the sill is full of water? Any guidance would be appreciated.

Thank you,

Paul.


magpie77 is offline  
 
Reply With Quote
Old 04-12-2012, 01:30 PM  
magpie77
Junior Member
registry_dropdown_27101_71363
 
Join Date: Apr 2012
Posts: 3
Default

To be clear, the leak is on the red line. I added the amateur silicone beading here, which has done no good and is really not a solution to problem. I will remove that as soon as I can understand cause.


magpie77 is offline  
 
Reply With Quote
Old 04-12-2012, 02:06 PM  
nealtw
Contractor
registry_dropdown_20526_71364
 
Join Date: Nov 2010
Location: Upper Fraser Valley, British Columbia
Posts: 12,851
Liked 1267 Times on 1117 Posts
Likes Given: 2123

Default

There are many systems for deverting water from below the door and I think they all will require pulling it out. I find it hard to beleive that water would enter below the door everytime it rains unless the deck outside is level to the floor inside and the water pools outside. Water could be entering in a multitude of location and show up at the door.
Photos of the outside sill area and everything above the door will be helpfull.
nealtw is offline  
 
Reply With Quote
Old 04-14-2012, 08:40 AM  
magpie77
Junior Member
registry_dropdown_27101_71418
 
Join Date: Apr 2012
Posts: 3
Default

Here's another couple of pics:
-There is no decking outside. The other picture shows that I have sealed around edge of window and under the window at frame/brick interface. I agree its a very odd place to leak, though any thoughts appreciated.
IMG_0373.jpg   IMG_0375.jpg  
magpie77 is offline  
 
Reply With Quote
Old 04-14-2012, 05:13 PM  
oldognewtrick
Moderator
HRT_ADMIN.png
 
oldognewtrick's Avatar
registry_dropdown_15773_71430
 
Join Date: Jul 2009
Location: Nashville, TN
Posts: 6,783
Liked 651 Times on 534 Posts
Likes Given: 205

Default

Can you show us a pic of the top of the window?
oldognewtrick is offline  
 
Reply With Quote
Old 04-14-2012, 08:58 PM  
mudmixer
Contractor
 
mudmixer's Avatar
registry_dropdown_2039_71433
 
Join Date: Sep 2006
Posts: 619
Liked 55 Times on 45 Posts
Likes Given: 45

Default

magpie -

You seem to be confusing the point of leakage with where it shows up on interior. Water runs vertically, horizontally and can also be controlled by capillary action where water is drawn for moist areas to drier areas an d shows up in various ways wherever there is little air circulation.

Since you have a brick exterior, is there a primary moisture barrier and proper flashing. It is estimated that about 60% of all windows and doors are installed improperly and cannot be analyzed easily from mere external observations.

Dick
mudmixer is offline  
 
Reply With Quote
Old 04-21-2012, 08:25 AM  
joecaption
Senior Member
registry_dropdown_21184_71696
 
Join Date: Jan 2011
Location: Hartfield VA, VA
Posts: 1,467
Liked 72 Times on 59 Posts
Likes Given: 2

Default

Those look like vinyl or aluminum clad windows not welded seam soild vinyl.
More then once I've seem them leak in the outside corners and down behind the vinyl to window area.
Vinyl expands and contracts a lot, brick does not, so the seams like to open up.
A simple cheap test I had to do to prove a window was leaking there and not my siding I had just installed was mixing some red food coloring with water and applying it with a Turkey baster to the corner, red coloring came running out on the inside.
joecaption is offline  
 
Reply With Quote
Old 04-21-2012, 12:21 PM  
oldognewtrick
Moderator
HRT_ADMIN.png
 
oldognewtrick's Avatar
registry_dropdown_15773_71705
 
Join Date: Jul 2009
Location: Nashville, TN
Posts: 6,783
Liked 651 Times on 534 Posts
Likes Given: 205

Default

Joe, you may be correct, but I'd still like to see the top of the window and the area above that.
oldognewtrick is offline  
 
Reply With Quote
Old 04-22-2012, 08:27 AM  
joecaption
Senior Member
registry_dropdown_21184_71736
 
Join Date: Jan 2011
Location: Hartfield VA, VA
Posts: 1,467
Liked 72 Times on 59 Posts
Likes Given: 2

Default

Got ya, what made me think that is look where the blue lines are in the picture, exactly where the seam is.

I've seen this happen many times in Pella and Anderson windows.
joecaption is offline  
 
Reply With Quote
Old 04-22-2012, 11:39 AM  
oldognewtrick
Moderator
HRT_ADMIN.png
 
oldognewtrick's Avatar
registry_dropdown_15773_71746
 
Join Date: Jul 2009
Location: Nashville, TN
Posts: 6,783
Liked 651 Times on 534 Posts
Likes Given: 205

Default

For the life of me I don't understand why window mfg's don't make a window with a built in sill pan.


oldognewtrick is offline  
 
Reply With Quote
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Hardwood doors or double glazed doors? gesmarty Windows and Doors 5 06-08-2011 08:12 AM
Leaking double wide mobile home roof jenialvr Roofing and Siding 5 03-29-2011 05:08 AM
door sill pan vanamber Windows and Doors 0 06-26-2010 02:32 AM
Cement door sill goser Windows and Doors 3 01-20-2010 05:29 AM
2x4 or 2x6 underneath door sill llckll Windows and Doors 1 08-24-2009 03:37 PM

Newest Threads

LATEST SPONSOR DEALS