Old 11-03-2012, 04:16 AM  
speedy petey
Lic.Electrical Contractor
Join Date: Mar 2006
Posts: 470
Liked 44 Times on 31 Posts
Likes Given: 25

Default

Quote:
Originally Posted by Wuzzat? View Post
The cable strain relief has pulled out from your wall due to horizontal wind force deflecting your Service Entrance cable.
Apparently the strain relief bolt stripped and the nut and washer fell down inside your attic.
That is a lag insulator. There was no nut and washer. That was screwed into the corner post of the house. It's pretty easy to see.



Quote:
Originally Posted by Wuzzat? View Post
If this is not fixed your SE cable will have a short life. Copper cannot stand much tension
so the steel messenger cable that fastens to this anchor
carries the bulk of the tensile force.
The drop is super light fro what I can see and is not damaging the SE cable, but yes,this should be fixed as soon as possible.




Quote:
Originally Posted by Wuzzat? View Post
Now it kind of looks like the messenger cable is also the neutral conductor.
The messenger is always the neutral.



Quote:
Originally Posted by Wuzzat? View Post
And look at the differences in cable ODs between what goes into the house and what comes from the utility pole. The pole wires must be 1/3rd the diameter of the larger cables on the left. I'd guess the nominal 240 volts must drop quite a bit when all the 240v house appliances are on.
The drop from the street is typically much smaller than the service entrance. POCO's fly by their own rules and run what they see fit. Many times after a service upgrade they simply leave the existing drop. Unless of course the actual load has increased substantially.
I'm not sure what the 240v appliances have to do with it.


speedy petey is offline  
 
Old 11-03-2012, 12:37 PM  
Wuzzat?
Banned
Join Date: Jan 2010
Location: , Western Hemisphere, N of the equator
Posts: 2,471
Liked 176 Times on 162 Posts
Likes Given: 108

Default

Quote:
Originally Posted by speedy petey View Post
That is a lag insulator. There was no nut and washer. That was screwed into the corner post of the house. It's pretty easy to see.
>the end looked square to me so I assumed it was a bolt. So now I guess I'd replace the lag screw with a bolt, then a coupler, then a threaded rod to be cut to length as needed, then a fender washer and nut

The drop is super light fro what I can see and is not damaging the SE cable, but yes,this should be fixed as soon as possible.
>Yet the wind force on this skinny cable was enough to pull out the lag screw.


The messenger is always the neutral.
>Is the neutral always the messenger? They don't use separate, steel messenger cables? So the (aluminum?) neutral is sized for both fault current ampacity and mechanical strength?

The drop from the street is typically much smaller than the service entrance. POCO's fly by their own rules and run what they see fit. Many times after a service upgrade they simply leave the existing drop. Unless of course the actual load has increased substantially.
I'm not sure what the 240v appliances have to do with it.
>Skinny drop = small CMs = high resistance = lower voltage available at the load center when all your appliances are on.
At my load center, a 20A, 240v load drops my voltage by 0.4v so a 200A, 240v load should drop my nominal 240v by ~4v, and then you've got the branch circuit drops.

Thanks for your info. This is not easily found on the Web.



Last edited by Wuzzat?; 11-03-2012 at 12:48 PM.
Wuzzat? is offline  
 
Old 11-03-2012, 12:49 PM  
Wuzzat?
Banned
Join Date: Jan 2010
Location: , Western Hemisphere, N of the equator
Posts: 2,471
Liked 176 Times on 162 Posts
Likes Given: 108

Default

xxxxxxxxxxxxxxxx
Wuzzat? is offline  
 
Old 11-03-2012, 05:26 PM  
speedy petey
Lic.Electrical Contractor
Join Date: Mar 2006
Posts: 470
Liked 44 Times on 31 Posts
Likes Given: 25

Default

Quote:
Originally Posted by Wuzzat? View Post
So now I guess I'd replace the lag screw with a bolt, then a coupler, then a threaded rod to be cut to length as needed, then a fender washer and nut
And since this is almost certainly on a finished interior wall HOW do you propose to do this??? Cut the wall open I assume?
A lag insulator is MORE than strong enough for this drop.


Quote:
Originally Posted by Wuzzat? View Post
Yet the wind force on this skinny cable was enough to pull out the lag screw.
HARDLY!
That happened because something either fell on the line, or fell on a line down the way, tensioning the wires, pulling the drop out. Or the pole itself broke.
Wind alone DID NOT do that. Never in a million years.


Quote:
Originally Posted by Wuzzat? View Post
Is the neutral always the messenger? They don't use separate, steel messenger cables? So the (aluminum?) neutral is sized for both fault current ampacity and mechanical strength?
Yes. No. Yes.
It's not just AL. It is an ACSR messenger. It is an AL conductor with a hardened steel single strand in the center. It is incredibly strong, and super hard to cut through.


Quote:
Originally Posted by Wuzzat? View Post
>Skinny drop = small CMs = high resistance = lower voltage available at the load center when all your appliances are on.
At my load center, a 20A, 240v load drops my voltage by 0.4v so a 200A, 240v load should drop my nominal 240v by ~4v, and then you've got the branch circuit drops.
240v loads cause MUCH less VD than 120V loads. 1/4 if I am not mistaken. That was my point.
Again, it is the POCO's prerogative to replace the drop. It is NOT mandatory.
speedy petey is offline  
 
Old 11-03-2012, 06:10 PM  
Wuzzat?
Banned
Join Date: Jan 2010
Location: , Western Hemisphere, N of the equator
Posts: 2,471
Liked 176 Times on 162 Posts
Likes Given: 108

Default

Cut the wall open I assume?
>If you have to, then use a drywall hot patch to fix the hole.

A lag insulator is MORE than strong enough for this drop.
>It wasn't this time.

HARDLY!
That happened because something either fell on the line, or fell on a line down the way, tensioning the wires, pulling the drop out. Or the pole itself broke.
Wind alone DID NOT do that. Never in a million years.
>I stand corrected, maybe. My first search for wind force on cables came up with one hit that I couldn't open. I'll be back on this one.

http://archive.ericsson.net/service/...101683&Lang=EN
Pg 18, 2000 newtons = 450 lbs. for a 90 meter span.
For a 9 meter span it's maybe 45 lbs.
I say you be right!

Yes. No. Yes.
It's not just AL. It is an ACSR messenger. It is an AL conductor with a hardened steel single strand in the center. It is incredibly strong, and super hard to cut through.
>Thanks, I've seen that conductor mentioned elsewhere.

240v loads cause MUCH less VD than 120V loads. 1/4 if I am not mistaken. That was my point.
>Only for equal wattage. Most 240v appliances are higher wattage.

Again, it is the POCO's prerogative to replace the drop. It is NOT mandatory.
>So if the HO asks for 200A service, he gets it, but PoCo is not compelled to provide that service to the house.
I guess the electrician could run a test and say what max service the homeowner could benefit from, if PoCo doesn't cooperate.

Last edited by Wuzzat?; 11-03-2012 at 06:23 PM.
Wuzzat? is offline  
 
Old 11-04-2012, 06:46 AM  
speedy petey
Lic.Electrical Contractor
Join Date: Mar 2006
Posts: 470
Liked 44 Times on 31 Posts
Likes Given: 25

Default

Quote:
Originally Posted by Wuzzat? View Post
>It wasn't this time.
Yeah, because a 20,000lb branch probably fell across the line.
I've seen it MANY times, and I'd much rather have the insulator pull out like that that have the whole corner of the house pulled down (which I have also seen).



Quote:
Originally Posted by Wuzzat? View Post
>Only for equal wattage. Most 240v appliances are higher wattage.
The wattage has NOTHING to do with it. 240V has 1/4 the voltage drop of 120V.



Quote:
Originally Posted by Wuzzat? View Post
>So if the HO asks for 200A service, he gets it, but PoCo is not compelled to provide that service to the house.
I guess the electrician could run a test and say what max service the homeowner could benefit from, if PoCo doesn't cooperate.
They ARE providing that service to the house. What is your limiting factor for this? Are you aware of the amperage ratings for conductors in free air? Are you aware that POCO's DO NOT have to follow the NEC?
What POSSIBLE test would/could an electrician run to see what a homeowner could benefit from?????? Connect up a 48,000 watt heater?

Last edited by speedy petey; 11-04-2012 at 06:51 AM. Reason: typo
speedy petey is offline  
 
Old 11-04-2012, 10:08 AM  
Wuzzat?
Banned
Join Date: Jan 2010
Location: , Western Hemisphere, N of the equator
Posts: 2,471
Liked 176 Times on 162 Posts
Likes Given: 108

Default

A 500 cu. ft. tree branch?

This thread is getting less productive!!!!!!!!!

Here's an idea that PoCo may not like if they are paying for it!!!!!!!!

At the pole, a pull-out connector for each hot lead and one high force pull-out connector for the messenger. The HO's strain relief pull-out force must be higher than PoCo's connectors but not so high that chunks of the house follow the cable down.

That way if a very heavy branch lands on the wire it will be unpowered as it falls to the ground.

With all due respect I have a book recommendation for you. . .
http://www.amazon.com/On-Being-Certa.../dp/B008SLU5Z8

". . .certainty is a mental sensation, rather than evidence of fact."

Yeah, you could rent & connect a constant current, constant power or constant resistance load. These first two would need electronics of some kind.

Last edited by Wuzzat?; 11-04-2012 at 10:19 AM.
Wuzzat? is offline  
 
Old 11-04-2012, 11:46 AM  
lleomon38
Junior Member
Join Date: Nov 2012
Posts: 5
Default

I am not the electrician. But here is the results

we call national grid few times and finally they came over. (Thanks for their hard work also, I talked to them and they work 16 hour per day).

So, first, they inspect the cable (meter). And they screw back the Lap insulator or neutral conductor (I am not sure but they screwed it back to the house).

And them inspect the cable from the Pole to my house. From few electrical sparks and they able to fixed it. Guess something from the Pole itself.

Since I don't know anything. But I would like at least provide what they did there and learn more.

Again, thanks for all the follow up and information you guys provided. I learn a lot there
lleomon38 is offline  
 
Old 11-04-2012, 04:45 PM  
Wuzzat?
Banned
Join Date: Jan 2010
Location: , Western Hemisphere, N of the equator
Posts: 2,471
Liked 176 Times on 162 Posts
Likes Given: 108

Default

You have to fix the hole in your house.
Wuzzat? is offline  
 
Old 11-04-2012, 05:45 PM  
speedy petey
Lic.Electrical Contractor
Join Date: Mar 2006
Posts: 470
Liked 44 Times on 31 Posts
Likes Given: 25

Default

Quote:
Originally Posted by Wuzzat? View Post
With all due respect I have a book recommendation for you. . .
http://www.amazon.com/On-Being-Certa.../dp/B008SLU5Z8

". . .certainty is a mental sensation, rather than evidence of fact."
So you are suggesting I am only correct in my head, but I believe I am right which is why I keep saying it??? You cannot be serious.

What is your area of expertise? Is it electrical contracting? Have you been at it for over 25 years?
When you can answer yes to the second two questions let me know. Until then I will stick to KNOWING I am right on this one. You can have your armchair contracting.

In fact, looking back on all the posts, there may be a book for you out there called "Continually Trying To Prove Folks Wrong: An Effort In Futility". Hell, you may even be the author.


And NO, no normal electrician, or any other kind of electrician, is going to rent a 50kW load to load test a 200A service. Not in the real world at least.


speedy petey is offline  
 
Closed Thread


Thread Tools Search this Thread
Search this Thread:

Advanced Search

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
What is this thing in the basement matts19 Framing and Foundation 5 04-26-2016 03:45 PM
What Do I Do With This Ugly Thing? MaryAguila Decorating and Design 10 05-19-2015 12:13 PM
Wet spot on wall I can't explain dorlow Walls and Ceilings 12 09-30-2014 05:06 PM
What is the Most Entertaining Thing? imported_frozenstar Garage & Workshop Forum 4 05-26-2011 10:06 AM
Can anyone identify this thing? Speedbump Plumbing Forum 21 05-25-2011 12:23 AM