Then the question is: "Can NMB be used in an unconditioned space?" If the cable sees more than 30C you might need to derate.
Wouldn't that be the same as an attic with a moisture problem.
Yes, unless the cable has some kind of cognition that we do not and can not know about (see Emergence).
Always a pleasure, nealtw. . .


Wuzzat? is offline  
 
Reply With Quote
Old 11-30-2012, 02:13 PM  
Wuzzat?
Banned
Join Date: Jan 2010
Location: , Western Hemisphere, N of the equator
Posts: 2,471
Liked 176 Times on 162 Posts
Likes Given: 108

Default

Quote:
Originally Posted by nealtw View Post
Then the question is: "Can NMB be used in an unconditioned space?" If the cable sees more than 30C you might need to derate.
Wouldn't that be the same as an attic with a moisture problem.
Seems damp to me.
http://www.paramount-lighting.com/wet_locations.pdf


Wuzzat? is offline  
 
Reply With Quote
Old 11-30-2012, 03:13 PM  
nealtw
Contractor retired
 
nealtw's Avatar
Join Date: Nov 2010
Location: Upper Fraser Valley, British Columbia
Posts: 23,705
Liked 3052 Times on 2671 Posts
Likes Given: 5040

Default

I think the smaller cables should be run thru holes in the joists too.
nealtw is online now  
 
Reply With Quote
Old 03-06-2013, 02:54 PM  
ROMEXCABLEFAN
Junior Member
Join Date: Mar 2013
Posts: 1
Default

Quote:
Originally Posted by alexb5647 View Post
My uncle has a log cabin that he gave to me and it was built back in the 40's. Since he's was an industrial electrician he redid the electrical in 1990 because of few plugs and knob and tube wiring. In order to avoid so many wires running along the wall he decided to drill through the floor and run the wire under the cabin to the next plug, switch, or if its a home run line. I looked under the cabin just recently and he just ran the romex loosely and it's laying on the ground. It doesn't look deteriorated or chewed. Some circuits close to the panel he just stapled the cable real nice and neat along the wall or ceiling. All junctions have covers and romex clamps on all boxes. All cables are stapled within 6" of fixture and stapled every 12". Also he put in some outdoor lighting on the porch and he just drilled through the logs from the inside and just ran romex out to the light. Is this acceptable by code? My uncle is not around anymore so I can't ask him. Any info would be appreciated.
If you ever replace this cable you would need to use the UF-B product Romex ®NM-B cable. It is permitted to be used “for both exposed and concealed work in normally dry locations” per NEC® 334.10(A)(1) and not permitted in “damp or wet” locations per NEC 334.12(B)(4). Any cable lying on the ground needs to be supported. - The cable needs to be supported and secured every 4’ and within 12” of each box, cabinet, conduit, or other termination. NEC 334.30(A)
This answer is intended to apply to Romex® Brand NM Cable. For other NM cables, please check with those respective brand suppliers or cable manufacturers. Romex® is a Registered Trademark of Southwire Company.
This communication is for general informational purposes only and is not intended to constitute advice. As all the facts and circumstances in any given situation may not be apparent, this communication is not intended to be, and should not be, relied upon by the reader in making decisions with respect to the issues discussed herein, and the reader assumes the risk if he or she chooses to do so. The reader is encouraged to consult an expert before making any decisions or taking any action concerning the matters in this communication. All warranties, express or implied, including warranties regarding accuracy, adequacy, completeness, legality, reliability, safety or usefulness of any information, ARE DISCLAIMED. Southwire Company is not liable for any damages however caused and on any theory of liability arising in any way out of the information provided or the reader's use of it.
ROMEXCABLEFAN is offline  
 
Reply With Quote
Old 03-06-2013, 03:24 PM  
nealtw
Contractor retired
 
nealtw's Avatar
Join Date: Nov 2010
Location: Upper Fraser Valley, British Columbia
Posts: 23,705
Liked 3052 Times on 2671 Posts
Likes Given: 5040

Default

Hey Romex: Welcome, great info until you dropped your lawyer on us. All that legal stuff is understud here
nealtw is online now  
 
Reply With Quote
Old 03-06-2013, 10:37 PM  
CallMeVilla
Senior Member
 
CallMeVilla's Avatar
Join Date: Feb 2010
Location: San Diego
Posts: 1,641
Liked 590 Times on 449 Posts
Likes Given: 246

Default

How nice to have you very own cabin!

If you are running conduit, you need stranded wiring, not UF or ROMEX sheathed. Heat builds up and so code requires strands. UF can be undergrounded but the aboveground stubs should be in conduit until you hit the required depth in the dirt (prevents critter gnawing on live wiring).

In California, we are required to bury UF or conduit a minimum of 14" below ground (which is exactly what I did today, BTW).

Here is a resource for you to consider: http://www.familyhandyman.com/DIY-Pr...cable/View-All

Last edited by CallMeVilla; 03-06-2013 at 10:40 PM.
CallMeVilla is offline  
 
Reply With Quote
Old 03-08-2013, 01:25 AM  
wireless
Junior Member
Join Date: Dec 2012
Posts: 3
Liked 1 Times on 1 Posts

Default

Quote:
Originally Posted by CallMeVilla
How nice to have you very own cabin!

If you are running conduit, you need stranded wiring, not UF or ROMEX sheathed. Heat builds up and so code requires strands. UF can be undergrounded but the aboveground stubs should be in conduit until you hit the required depth in the dirt (prevents critter gnawing on live wiring).

In California, we are required to bury UF or conduit a minimum of 14" below ground (which is exactly what I did today, BTW).

Here is a resource for you to consider: http://www.familyhandyman.com/DIY-Pr...cable/View-All
What code is that exactly?!
wireless is offline  
 
Reply With Quote
Old 03-09-2013, 07:25 PM  
CallMeVilla
Senior Member
 
CallMeVilla's Avatar
Join Date: Feb 2010
Location: San Diego
Posts: 1,641
Liked 590 Times on 449 Posts
Likes Given: 246

Default

Well, wireless, you can start here and follow the NEC ....
http://electrical.about.com/od/codes...iring_tips.htm

CallMeVilla is offline  
 
Reply With Quote
Old 03-10-2013, 01:44 AM  
wireless
Junior Member
Join Date: Dec 2012
Posts: 3
Liked 1 Times on 1 Posts

Default

Quote:
Originally Posted by CallMeVilla
Well, wireless, you can start here and follow the NEC ....
http://electrical.about.com/od/codes...iring_tips.htm

Really the NEC requires stranded wire in conduit?
wireless is offline  
 
Reply With Quote
Old 03-10-2013, 02:40 PM  
CallMeVilla
Senior Member
 
CallMeVilla's Avatar
Join Date: Feb 2010
Location: San Diego
Posts: 1,641
Liked 590 Times on 449 Posts
Likes Given: 246

Default

In case you did NOT read the very helpful article from The Family Handyman I provided, here is the pic for buried plastic pipe wiring ... Note also the more shallow undergrounded wiring is encased in metal conduit .... BUT BOTH are done without the ROMEX sheathing.


Click image for larger version

Name:	Underground.jpg
Views:	273
Size:	99.8 KB
ID:	4891  
CallMeVilla is offline  
 
Reply With Quote
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
How long will red tape last outdoors qmqmqm General Home Improvement Discussion 4 10-28-2014 09:00 PM
12/2 Romex or 14/2 Romex for Recessed Can Lighting? savatreatabvr Electrical and Wiring 24 01-18-2014 06:15 PM
Conduit outdoors doechsli Electrical and Wiring 0 11-20-2012 01:33 PM
GFCI Outlets Outdoors/Garage SavvyCat Electrical and Wiring 9 05-04-2009 09:29 PM
Installing Slate tiles outdoors VictorC General Home Improvement Discussion 0 10-30-2006 07:30 AM



Newest Threads