Quote:
Originally Posted by CallMeVilla View Post
In case you did NOT read the very helpful article from The Family Handyman I provided, here is the pic for buried plastic pipe wiring ... Note also the more shallow undergrounded wiring is encased in metal conduit .... BUT BOTH are done without the ROMEX sheathing.
Actually both are done separate wires fed into the conduit. You can not strip NM cable and use it in conduit. The wires from inside a NM cable are NOT suitable for this use. You must use proper rated THHN/THWN wires.


JoeD is offline  
 
Reply With Quote
Old 03-10-2013, 09:31 PM  
CallMeVilla
Contractor
 
CallMeVilla's Avatar
Join Date: Feb 2010
Location: San Diego
Posts: 1,502
Liked 511 Times on 390 Posts
Likes Given: 208

Default

Good point, Joe ... For those who do not know, stand-alone THWN cables are coated in PVC, as opposed to vinyl, to assist in water resistance. THHN wire is typically two-conductor with ground, and found in the familiar ROMEX cabling that wires homes, e.g. 12-2. The coating also explains the slight price difference between the two ... and the noticeable price difference between ROMEX cabling (cheaper) and THWN stranded cabling. In harsh climates these are important differences to know!


CallMeVilla is offline  
 
Reply With Quote
Old 03-10-2013, 09:57 PM  
JoeD
Contractor
Join Date: Mar 2006
Location: Welland, Ontario
Posts: 1,093
Liked 136 Times on 111 Posts
Likes Given: 4

Default

THHN is NOT two conductor with ground. It is single wire, either stranded or solid. The wire inside NM cable is NOT suitable to be used in place of THHN. It is not labelled as THHN and can not be legally used in conduit.
JoeD is offline  
 
Reply With Quote
Old 03-10-2013, 09:58 PM  
nealtw
Contractor
Join Date: Nov 2010
Location: Upper Fraser Valley, British Columbia
Posts: 13,522
Liked 1354 Times on 1195 Posts
Likes Given: 2329

Default

PVC, as opposed to vinyl, as in poly vinyl chloride?
nealtw is offline  
 
Reply With Quote
Old 03-11-2013, 10:17 AM  
CallMeVilla
Contractor
 
CallMeVilla's Avatar
Join Date: Feb 2010
Location: San Diego
Posts: 1,502
Liked 511 Times on 390 Posts
Likes Given: 208

Default

Rather than get caught up in the chemistry of coatings, how about this:
1.The "T" stands for thermoplastic insulated cable.
2.A single "H" means the wire is heat resistant.
3."HH" means that the wire is heat resistant and can withstand a higher temperature. This wire can withstand heat up to 194 degrees Fahrenheit.
4.A "W" means that the wire is approved for damp and wet locations. This wire is also suitable for dry locations.
5.The "X" means the cable is made of a synthetic polymer that is flame-retardant.
6.The "N" is for the nylon coating that covers the wire insulation.

Go here for more: http://electrical.about.com/od/wirin...elettering.htm



CallMeVilla is offline  
nealtw Likes This 
Reply With Quote
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Conduit outdoors doechsli Electrical and Wiring 0 11-20-2012 01:33 PM
GFCI Outlets Outdoors/Garage SavvyCat Electrical and Wiring 9 05-04-2009 09:29 PM
2 questions - vanity light and romex with no power rando Electrical and Wiring 5 05-27-2008 06:27 AM
Romex Routing in Attic 69-er Electrical and Wiring 3 02-19-2007 03:40 PM
Installing Slate tiles outdoors VictorC General Home Improvement Discussion 0 10-30-2006 07:30 AM

Newest Threads

LATEST SPONSOR DEALS