Old 04-24-2013, 01:15 PM  
drewdin
Junior Member
Join Date: Aug 2012
Posts: 427
Liked 37 Times on 32 Posts
Likes Given: 107

Default Air Handler wiring question

Hi Guys,

I'm connecting the wires to the Air Handler in the Attic, i was told that I need a disconnect and there is only a 1/2" knockout on the top of the AHU. The disconnect i purchased will mount to the outside of the unit but what about the wire.

Do i need to run it in conduit between the disconnect and the AHU? do I need to run it in conduit to the disconnect and then to the AHU, can I just run the wire into the disconnect and then into the AHU without the conduit?

I just want to make sure I do it right, thanks!


drewdin is offline  
 
Reply With Quote
Old 04-24-2013, 03:39 PM  
kok328
Supporting Member
HRT_SUPPORTER.png
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,349
Liked 148 Times on 126 Posts
Likes Given: 71

Default

There are 2 approaches to this.
1. run the wire into the disconnect and then run out of the disconnect to the AHU. Using "sealtite" conduit will make the job much easier for a non-electrician.
2. mount the disconnect on the AHU and drill a hole in through the back of the disconnect & AHU. Install a "chase" nipple between the two and then run your wires into the disconnect and out the back of the disconnect into the AHU.
However, given the area where it is being installed, I do not believe conduit is a requirement.


kok328 is offline  
 
Reply With Quote
Old 04-24-2013, 05:33 PM  
CallMeVilla
Contractor
 
CallMeVilla's Avatar
Join Date: Feb 2010
Location: San Diego
Posts: 1,517
Liked 520 Times on 399 Posts
Likes Given: 211

Default

The "sealtite" is also called "Liquid-tight" ... it is flexible, so any vibration is not going to compromise the connection ... just remember to put connectors in the boxes to prevent wires from touching sharp edges.
CallMeVilla is offline  
 
Reply With Quote
Old 04-24-2013, 06:13 PM  
drewdin
Junior Member
Join Date: Aug 2012
Posts: 427
Liked 37 Times on 32 Posts
Likes Given: 107

Default

do they sell sealtite at the big box stores? I think i only need a right angle piece to connect the AHU to the disconnect.
drewdin is offline  
 
Reply With Quote
Old 04-24-2013, 09:45 PM  
nealtw
Contractor
Join Date: Nov 2010
Location: Upper Fraser Valley, British Columbia
Posts: 14,249
Liked 1457 Times on 1285 Posts
Likes Given: 2513

Default

http://www.homedepot.com/Electrical-...searchNav=true
nealtw is offline  
 
Reply With Quote
Old 04-25-2013, 10:20 AM  
CallMeVilla
Contractor
 
CallMeVilla's Avatar
Join Date: Feb 2010
Location: San Diego
Posts: 1,517
Liked 520 Times on 399 Posts
Likes Given: 211

Default

Actually, this is what you seem to want:
http://www.homedepot.com/Electrical-...wv=1z117wv&c=1
CallMeVilla is offline  
 
Reply With Quote
Old 04-25-2013, 03:56 PM  
drewdin
Junior Member
Join Date: Aug 2012
Posts: 427
Liked 37 Times on 32 Posts
Likes Given: 107

Default

Thanks for the links, i was looking in Lowes today and they didnt have much. I took some pictures so you can see what im working with.

I am trying to decide the best location for the disconnect, any suggestions? Thanks
2013-04-25 14.33.30.jpg   2013-04-25 14.32.18.jpg   2013-04-25 14.32.08.jpg  
drewdin is offline  
 
Reply With Quote
Old 04-25-2013, 03:57 PM  
drewdin
Junior Member
Join Date: Aug 2012
Posts: 427
Liked 37 Times on 32 Posts
Likes Given: 107

Default

Quote:
Originally Posted by CallMeVilla View Post
Actually, this is what you seem to want:
http://www.homedepot.com/Electrical-...wv=1z117wv&c=1

How does the liquidetight connect? which fittings should i use? Thanks
drewdin is offline  
 
Reply With Quote
Old 04-26-2013, 09:39 AM  
kok328
Supporting Member
HRT_SUPPORTER.png
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,349
Liked 148 Times on 126 Posts
Likes Given: 71

Default

You will want to install the disconnect within reach of the AHU and where it is easily accessible.
They make several types of sealtite connections and they are pretty much straightforward as to how they connect.
kok328 is offline  
 
Reply With Quote
Old 05-03-2013, 07:32 AM  
drewdin
Junior Member
Join Date: Aug 2012
Posts: 427
Liked 37 Times on 32 Posts
Likes Given: 107

Default

Here's the finished project, any suggestions or modifications I should make? Thanks


2013-05-01 20.52.19.jpg  
drewdin is offline  
 
Reply With Quote
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Air Handler in the attic Question drewdin HVAC 15 04-17-2013 06:20 PM
Wiring question JeremyB Electrical and Wiring 5 02-19-2013 11:11 AM
wiring question justin_dupuis Introductions 3 12-24-2007 04:18 PM
Electrical wiring question jamesm Electrical and Wiring 4 12-17-2006 08:21 AM

Newest Threads

LATEST SPONSOR DEALS