Default Unit quit working

Trane XL 1200 - Model YCY030F1MOA not working. Main board is flasing indicating Pressure Switch not working.

If I close the contact on the Compressor Contactor Coil it turns on. When the back of the blower motor is touched it is hot but has not been on in several days.

Fuses are good, voltages are good.

Any thoughts would be appreciated.

Thanks


brampup is offline  
 
Reply With Quote
Old 01-05-2014, 03:48 PM  
Wuzzat?
Banned
registry_dropdown_17632_98077
 
Join Date: Jan 2010
Posts: 2,328
Liked 168 Times on 155 Posts
Likes Given: 94

Default

Check if the blower motor is seized. Is it getting full voltage?

The odds are apparently good that if you replace the pressure switch it will clear up at least one problem unless that signal may also mean the pressure is out of range.

Post a schematic.



Last edited by Wuzzat?; 01-05-2014 at 03:50 PM.
Wuzzat? is offline  
 
Reply With Quote
Old 01-05-2014, 05:09 PM  
brampup
Junior Member
registry_dropdown_32919_98086
 
Join Date: Jan 2014
Posts: 4
Default

Wuzzat, thanks for the reply.

The pressure switch is new as of this summer. I feel that is not the problem.

I leaning toward the fan motor due to the end being hot and it is not operating. I think that the fan has to be working for the pressure switch to function properly. Since the fan is not running it shouldn't be hot, I'm thinking. This last point I'm not 100% sure about.

I did measure voltage to the main wires is that area.
brampup is offline  
 
Reply With Quote
Old 01-06-2014, 04:52 PM  
kok328
Supporting Member
HRT_SUPPORTER.png
registry_dropdown_4883_98154
 
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,315
Liked 144 Times on 122 Posts
Likes Given: 71

Default

blower motor, fan motor, inducer motor, draft motor.
I picture the first two being the same and the last two being the same.
If your inducer/draft motor is hot but, not turning, it could be bad assuming no physical blockage.
This will cause the pressure switch to fault.
kok328 is offline  
 
Reply With Quote
Old 01-06-2014, 05:37 PM  
brampup
Junior Member
registry_dropdown_32919_98155
 
Join Date: Jan 2014
Posts: 4
Default

Gentlemen, it was the Blower, Combustion motor. Working like a champ. The fan blades of the old motor moved but grudgingly. But with power on did not turn at all.

Thanks for the help and keep smilen!!

Off to watch FSU teach Auburn a little about ACC football.

Thanks again.
brampup is offline  
 
Reply With Quote
Old 01-06-2014, 07:06 PM  
Wuzzat?
Banned
registry_dropdown_17632_98166
 
Join Date: Jan 2010
Posts: 2,328
Liked 168 Times on 155 Posts
Likes Given: 94

Default

Quote:
Originally Posted by brampup View Post
Gentlemen, it was the Blower, Combustion motor. Working like a champ. The fan blades of the old motor moved but grudgingly. But with power on did not turn at all.

Thanks for the help and keep smilen!!

Off to watch FSU teach Auburn a little about ACC football.

Thanks again.
You probably paid yourself $100/hour of tax-free income on this job. Plus the knowledge you gained.

Now that everything is working, take voltage and current measurements everywhere; you may someday need them.
Wuzzat? is offline  
nealtw Likes This 
Reply With Quote
Old 01-07-2014, 10:08 AM  
brampup
Junior Member
registry_dropdown_32919_98203
 
Join Date: Jan 2014
Posts: 4
Default

Good point Wasset! I have some of the basic voltages traciking this issue but did no take the time to log as many as I should.
brampup is offline  
 
Reply With Quote
Old 01-16-2014, 08:52 PM  
mahitas1111
Junior Member
registry_dropdown_33006_98703
 
Join Date: Jan 2014
Location: Fremont
Posts: 1
Default

I assume it is control board fault..It happens often on tranes units


mahitas1111 is offline  
 
Reply With Quote
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
What is the best way to quit smoking? SteveMarker General Chit-Chat 27 09-30-2012 11:24 AM
York AC unit not working.. jcherryj HVAC 5 07-08-2012 07:13 AM
Inside Unit Not Working - Please Help! ThatDudeMike HVAC 7 02-26-2010 08:44 PM
Outside unit stopped working, no heat? rrange HVAC 4 11-26-2008 11:11 AM
evaporator fan quit today paul s HVAC 3 08-05-2008 02:48 PM

Newest Threads

LATEST SPONSOR DEALS