Old 01-23-2014, 02:19 PM  
Louuuuu
Junior Member
 
Join Date: Jan 2014
Posts: 6
Default Kinda electrical. Kinda plumbing.

I recently replaced my 1/2 HP well pump with a 1 HP well pump. Why? Because it's what was readily available at the time...

Now, when the pump kicks on, I get a loud bang . I'm thinking I can either 1.) install some type of "start-up pressure absorber" device on the water line, or 2.) install some type of electrical rheostat that eases the amperage into the pump. (# 3 - "put the right pump in" ain't happening. It's 10 degrees outside.)

Any thoughts?



__________________
Louuuuu is offline  
 
Reply With Quote Quick reply to this message
Old 01-23-2014, 06:50 PM  
JoeD
Contractor
 
Join Date: Mar 2006
Location: Welland, Ontario
Posts: 984
Liked 107 Times on 87 Posts
Likes Given: 4

Default

When it kicks on or kicks off you get the bang?
Sounds like water hammer. Perhaps a larger pressure tank or the tank closer to the point of entry into the house would help.



__________________
JoeD is offline  
 
Reply With Quote Quick reply to this message
Old 01-24-2014, 05:49 AM  
Louuuuu
Junior Member
 
Join Date: Jan 2014
Posts: 6
Default

Only when it kicks on.

I wouldn't think it would be water hammer. Because it only started after I replaced the pump.

Logical?

(And the pressure tank is three feet from where the line enters the house.)

__________________
Louuuuu is offline  
 
Reply With Quote Quick reply to this message
Old 01-24-2014, 09:14 AM  
Speedbump
Water well etc.
 
Speedbump's Avatar
 
Join Date: Apr 2009
Location: Riverview, Fl.
Posts: 439
Liked 23 Times on 22 Posts
Likes Given: 4

Default

Where does the noise appear to be coming from? Did you install a new check valve?

__________________
FAQ's
Speedbump is offline  
 
Reply With Quote Quick reply to this message
Old 01-24-2014, 10:42 AM  
Louuuuu
Junior Member
 
Join Date: Jan 2014
Posts: 6
Default

The corner of the basement where the pressure tank is located.

It's a one-time klunk every time the switch comes on.

It's still the original check-valve.

__________________
Louuuuu is offline  
 
Reply With Quote Quick reply to this message
Old 01-24-2014, 11:05 AM  
Speedbump
Water well etc.
 
Speedbump's Avatar
 
Join Date: Apr 2009
Location: Riverview, Fl.
Posts: 439
Liked 23 Times on 22 Posts
Likes Given: 4

Default

My guess is the switch. What brand pump and switch did you buy?

__________________
FAQ's
Speedbump is offline  
 
Reply With Quote Quick reply to this message
Old 01-24-2014, 11:44 AM  
bud16415
Fixer Upper
 
bud16415's Avatar
 
Join Date: Feb 2013
Location: Erie Pa, Pa
Posts: 1,338
Liked 398 Times on 311 Posts
Likes Given: 130

Default

Your tank is the shock absorber in the system you first asked about. Do you have a bladder tank or a free air control tank. Any way you could have lost air in your tank? Are you still getting fairly long cycles between motor kicking on and off? Is the noise less on startup if you have some heavy usage of water going on like a hose coming directly off the tank. Is the noise the same?

You mentioned you were not interested in replacing it with the “right” pump because of the weather. Is the pump down in the well as a submergible? I don’t see where a larger than needed pump should be causing problems. What you basically will have is a higher flow rate. When you hooked this up was there a large size reduction between the new pump and the old pipe?

__________________
bud16415 is offline  
 
Reply With Quote Quick reply to this message
Old 01-25-2014, 08:15 AM  
kok328
Supporting Member
HRT_SUPPORTER.png
 
Join Date: Nov 2007
Location: Grand Blanc, MI
Posts: 2,215
Liked 115 Times on 100 Posts
Likes Given: 65

Default

Unfortunately, the cost of a VFD controller to slowly ramp up the pump speed would be cost prohibitive especially if the pump will be changed out when warmer weather gets here.
Any loose piping anywhere that could be tightly secured to minimize the kick?

__________________
kok328 is offline  
 
Reply With Quote Quick reply to this message
Old 01-26-2014, 09:38 AM  
Louuuuu
Junior Member
 
Join Date: Jan 2014
Posts: 6
Default

It's a FloTec. Switch is Parts2o (30-50)

Submersible. 130' down.

Tank pressure should be about right. I "topped it off" last fall after 14 years of maintenance free use. Cycle time seems to be about the same.

No additional reducer needed on replacement. 1 1/2" schedule 80 PVC

__________________
Louuuuu is offline  
 
Reply With Quote Quick reply to this message
Old 01-27-2014, 07:17 AM  
bud16415
Fixer Upper
 
bud16415's Avatar
 
Join Date: Feb 2013
Location: Erie Pa, Pa
Posts: 1,338
Liked 398 Times on 311 Posts
Likes Given: 130

Default

My guess is the new pump just has a higher flow rate and maybe that’s where the line goes into the tank is stepped down causing a partial restriction to the inrush water so as it’s trying to compress the air in the tank it’s now also able to water hammer some. As kok328 pointed out there is a loose pipe that’s smacking against another or something like that. The 1 ½ line coming into the tank goes into what size fitting there?



__________________
bud16415 is offline  
 
Reply With Quote Quick reply to this message
Reply


Quick Reply
Message:
Options

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter DIY Home Repair Forum Replies Last Post
Electrical Questions here or in Electrical Forum toofast Pools and Spas 11 10-19-2012 09:31 AM
the big dead tree next door (kinda long) Philphine General Home Improvement Discussion 11 06-30-2010 02:18 PM
Kinda bummed out-cannot get a Heat Pump Outbacker HVAC 4 05-25-2009 07:05 PM
Help plz...kinda stuck here flchoirboy General Home Improvement Discussion 1 12-30-2006 02:03 PM